:confused: I am attempting to replace our Weathertron thermostat with a Honeywell RTH3100C. We have a Trane heatpump system. I am having trouble with the wiring. My wires don't match the 'less common wire designations' in the manual.
I have the following wires on the Weathertron:

R-red
T-brown
O-orange
G-green
Y-yellow
X2-black
B-blue
W-white

I'm not sure where the T wire should go.

hvac1000
Feb 18, 2008, 11:22 PM
:confused: I am attempting to replace our Weathertron thermostat with a Honeywell RTH3100C. We have a Trane heatpump system. I am having trouble with the wiring. My wires don't match the 'less common wire designations' in the manual.
I have the following wires on the Weathertron:

R-red
T-brown
O-orange
G-green
Y-yellow
X2-black
B-blue
W-white

I'm not sure where the T wire should go.


Here you go

acetc
Feb 19, 2008, 06:57 PM
You will not use the brown wire, tape it off and stick it in the wall. This "T" connection is only used on the older Trane or GE heat pumps for the outdoor anticipator with the weathertron thermostats. Mike

booger3518
Jun 30, 2010, 05:58 AM
Ok I am trying to go from a trane weathertron baystat 240 to a honeywell RTH3100c. Baystat wiring was Red-r,Tan-t Orange-o, Green-g,Yellow-y,White-X2jumped to w,Blue-b. I wired the honeywell Green-g, Yellow-y, Orange-o,Red-r,Blue-b,White-ejumped to aux, taped tan off. Powered up system cooling flashed 5min. Then air came on just sounded queiter than normal. However it did cool off and turn off in auto. Did I wire everything correctly?