I have a 2 pole double throw breaker. Each side reads 30. Is the breaker 30 amps or it the breaker 60 amps? Thanks.:confused:

KISS
Feb 9, 2008, 03:24 PM
That 30A of 240 V coming from two 120 VAC legs that are 180 deg out of phase, thus each leg must be fused at 30 A and they will both break at the same time due to the mechanical connection.

This out of phasing is because the primary is single phase and the secondary is center-tapped. This creates two out of phase voltages, but it is single phase power.

shortround3
Feb 10, 2008, 07:06 AM
That 30A of 240 V coming from two 120 VAC legs that are 180 deg out of phase, thus each leg must be fused at 30 A and they will both break at the same time due to the mechanical connection.

This out of phasing is because the primary is single phase and the secondary is center-tapped. This creates two out of phase voltages, but it is single phase power.

Thanks for the response. I understand that each side is 30 amps. Is the breaker referred to as a 30 amp breaker or a 60 amp breaker?

Stratmando
Feb 10, 2008, 08:06 AM
A 30 Amp/ 2 Pole Breaker @240 Volts

KISS
Feb 10, 2008, 12:30 PM
30 A. Sorry I wasn't as explicit as necessary.

shortround3
Feb 11, 2008, 03:38 AM
Thanks for the help.