Ed_Coombs
Jan 8, 2008, 09:40 AM
Hi,
I am living in the South of France and the power supply to my house is 3 phase. The overall supply is 9kv giving a max of 3kv on each phase. I tried to fit a type AC 30ma breaker to each phase for safety reasons but have failed somewhere!
The supply is 3 lives (220v each) and 1 neutral. I connected each live to term 1 on the breaker and then out of term 2 and back to original position in the distribution unit. I took the neutral to a terminal strip and ran 3 wires from that strip though the ac breakers to a separate terminal strip and then a single wire back to the original neutral terminal in the distribution unit.
Each ac breaker will work until an ac breaker on the other phase is switched on. Switching on the second ac breaker seems to cause a dead short (I'm assuming because the neutral is a single wire common to all three ac breakers?). Each ac breaker will work fine on its own. Am I trying to do the impossible?
I really can't see where I've screwed up based on the wiring principles I work with normally - but this is the first time that I have tried anything like this with three phase.
As an aside, the main trip in the supply breaker didn't trip.
If you can give me an idea where I've gone wrong I would be very grateful! :p
Best regards,
Ed Coombs
St Antonin Noble Val, France.
I am living in the South of France and the power supply to my house is 3 phase. The overall supply is 9kv giving a max of 3kv on each phase. I tried to fit a type AC 30ma breaker to each phase for safety reasons but have failed somewhere!
The supply is 3 lives (220v each) and 1 neutral. I connected each live to term 1 on the breaker and then out of term 2 and back to original position in the distribution unit. I took the neutral to a terminal strip and ran 3 wires from that strip though the ac breakers to a separate terminal strip and then a single wire back to the original neutral terminal in the distribution unit.
Each ac breaker will work until an ac breaker on the other phase is switched on. Switching on the second ac breaker seems to cause a dead short (I'm assuming because the neutral is a single wire common to all three ac breakers?). Each ac breaker will work fine on its own. Am I trying to do the impossible?
I really can't see where I've screwed up based on the wiring principles I work with normally - but this is the first time that I have tried anything like this with three phase.
As an aside, the main trip in the supply breaker didn't trip.
If you can give me an idea where I've gone wrong I would be very grateful! :p
Best regards,
Ed Coombs
St Antonin Noble Val, France.