Should My Thermostats Panel Operate On The 2 Aa Backup Batteries Or Be Hardwired To Common And Have Batteries As Backup When Power Is Out?
Panel Lights Up With Batteries In, Does Not Without Batteries. Don't Know Where Common Wire Originates From. Can I Splice Into One Of The Other Wires, G, Y, W To Connect To C Terminal?

Thanks.

labman
Dec 4, 2005, 10:51 AM
Not without sacrificing its function.

Usually there is a 24 volt AC transformer in the furnace with the secondary winding connected to a red wire running to the thermostat and a blue wire, common, to the gas valve, A/C relay, and fan relay. From the thermostat there will be white wire to the gas valve, yellow to the A/C, and green to the fan. The thermostat is wired to switch the power from the red to the white, yellow, and green as needed with the blue completing the circuit. Most thermostats and furnaces have the contacts labeled R, B or C, W, Y, and G for the corresponding wire colors. It may be wired to have the A/C control wires return to the furnace and its controls and then a second wire goes to the A/C unit. Internal wiring may replace the green wire if the thermostat does not give you the option of fan only or continuous fan. Digital or programmable thermostats may need the blue wire connected to them.

If you don't connect the transformer to the common, you may be having to change batteries all the time and losing any program. If you don't have an unused blue or other wire, you could connect the green or yellow to B or C at both ends, losing the fan on or A/C options. If you have a crawl space or unfinished basement under the thermostat, it may not be too bad of a job to fish in another wire.

Paul6161
May 6, 2012, 07:28 AM
This is a 2 zone baseboard heat system. The old t87 honeywell has only 3 wires going to stat. Be for blue wire,R for red wire and W white.When calls for heat on that zone I get 24 volts between R and B. I am a south Florida contractor. Work very little with oil and zone valves. Does this mean I must use stat with common terminal for old B terminal?