View Full Version : Sizing parallel conductors


hurtz
Oct 18, 2007, 06:02 PM
On a 400 amp service for a commercial building. I'm trying to figure out the conductor size using parallel runs. I think 3/0 is sufficient but not sure. 3/0 is good for 225amps under the 90 degree column. Do you then multiply by 2 for 450 amps?

tkrussell
Oct 18, 2007, 06:15 PM
#3/0 is correct but not because of the 90 Deg C column, but it is rated 200 amps in the 75 Deg C column. Cannot use 90 D column unless the terminals are rated 90 D.

So parallel #3/0 will be rated 400 amps.

Washington1
Oct 18, 2007, 07:14 PM
Seeing that you said 225A in the begin, we can assume you are using copper:)