PDA

View Full Version : Wiring 3 sets of lights off one feed


jlh2001
Oct 10, 2007, 09:11 AM
I have 3 rooms in my basement that will contain 4 recessed lights per room. Each room will have one wall switch to control the lights per that room. The power will come from a new single 15amp feed from the sub panel. Could you provide an easy to follow wiring diagram/explanation on how to hook this up. Thanks, John

donf
Oct 10, 2007, 12:17 PM
To begin with, will a 15 Amp circuit be able to drive 12 individual lights? Have you correctly sized the load for this circuit?

To begin with, I would suggest that you pull 12/cable from the sup panel to the first outlet in the first room. Do not connect the new cable now. Make it the last thing you do.. At this outlet, again using 12/3 run a switch loop to where the first switch goes.

At the overhead outlet, the black from the sub panel connects to the white from the switch. Wrap a small amount to black tape to signify that this wire is now carrying voltage instead of being a neutral wire.

Black from the switch got to black from the first light from there on, black will go to black and white to white until all four lights are chained together.

Back at the overhead, do two pigtails, one for the power source (Black from the sup panel, white to the switch and black for the next room). The second pigtail is for the whites.

Continue your daisy chain until the three rooms are finished. Shut the sup panel down add the wire and breaker into the sup panel, turn the breaker on and test your rooms

labman
Oct 10, 2007, 01:25 PM
I would be just as happy to leave electrical questions to somebody that can give good answers. I still wouldn't questions like this, but I am afraid somebody would take the bad advice before somebody else corrects it. The answer above has some problems just as several of his have. Lights are frequently run on 15 amp circuits. As long as you are planning on using less than 120 watts per fixture, it will be OK although with little margin. I hope you aren't planning on using soon to be regulated out of existence incandescents. Besides the popular CFL's, there are halogens and even LED's. Little down side to going ahead with #12, but you will want 12-2 or 14-2 with ground. 12-3 suggests a third, insulated conductor, and Donf gives no instructions for what to do with the red wire it would have.

Donf and some others here seem to have an obsession with switch loops. Yes, they make sense in some cases. It might be easier in your case to just run the power to the closest switch, and then to the next and the next. Then run power from each switch up to each string of lights. How you do it might depend on whether the walls or ceiling are finished.

I may have missed something, so don't buy any wire until tkrussel checks in.
Maybe he understands why you would need 12-3.

donf
Oct 10, 2007, 03:38 PM
Labman,

I have an obsession with switch loops? He defines his room as 4 lights and one wall switch. If he doesn't use a loop to tie the switch into the circuit how is it going to connected?

12/3 is a typo. 12/2 is correct, thanks.

Stratmando
Oct 11, 2007, 06:24 AM
Like labman says, I would run from panel to first switch box, then 2 romex's out,(one to that string of lights,the other to next switch, from that second switch box, 2 more out(1 to that string of lights, the other to the next switch box. Personally I hate romex, I would use "Smurf" ENT(Electrical Non Metallic Tubing).
I would consider recepticles, and smoke detector(s).

labman
Oct 11, 2007, 06:51 AM
How much extra cost and work is smurf over NM? I think in most residential work it is a knee jerk reflex to use NM. The only time I can remember of venturing out of it, was the dog resistant feed to my A/C where I used rigid steel. So far, none of them have chewed it up. One thing about any conduit is you can pull what ever you need, black, white, red, green, purple, etc. and never need to remark a white wire that was paired with a black. Where a switch loop is what works best, just pull a couple of blacks or a red.

http://www.photolocker.net/images/Labman/KatetheAC.jpg

donf
Oct 11, 2007, 07:16 AM
If JLH is going to leave the wiring exposed on the walls and ceiling, then by code the wire must be run inside conduit. If he is going to frame the walls and dry wall over the frame, then NM Cable is the way to go, again by code. Or am I looking at a code book from Pluto?

JLH, please chime in with how the wiring is to be installed as soon as you can.

Stratmando
Oct 11, 2007, 07:27 AM
Hate Romex, Code does not say smurf is a violation. It allows future growth, ESPECIALLY
If wireing is covered with drywall. I think some people use romex so much, it is a habit.
I like conduit, it is a habit. Don't like destroying walls to add a?? a wall AC or something.

donf
Oct 11, 2007, 07:48 AM
I don't know why you hate NMB cable, it certainly has it's designed purpose. Nor did I say that "SMURF" is a code violation.

What I did say was that if the wiring is going to be exposed, it must be wired in conduit. Conduit in this usage means metal or PVC.

Also, if the wiring is going to be behind walls, then NMB wiring is allowed. It matters not to me if you want to place PVC behind the walls and pull wires. It just is not required by code to place PVC conduit behind walls in a residence. Commercial buildings are a different story.

Stratmando
Oct 11, 2007, 07:57 AM
I know its not required, just makes things easy in the future, to pull additional wiring.
Romex does have it's purpose, its fast, cheap, especially with copper prices.
It is more difficult to add even just 1 wire. I feel it is obsolete, the minute it is installed.
Poster can use what's allowed? Good Luck

donf
Oct 11, 2007, 08:18 AM
NMB is certainly not obsolete. Don't even think that, I just bought some stock in Romex :)

Seriously, I would appreciate your expanding your reasons and observations about the benefits of Smurf over NMB.

I want to learn, not squabble.

Stratmando
Oct 11, 2007, 01:40 PM
Future upgrading, some Automation stuff need neutral or a constant Hot, in box.
It is not Obsolete. I have ran a pair of wires through fan boxes, switch boxes, and through recepticles to get 3 wall unit AC's to 3 bedrooms. Romex would have been impossible.
Wall would have to be destroyed, patched, painted... and on.
I will try to say it clearer. Once romex is installed, I feel it is obsolete. Not easy to simply pull an extra wire. I also like stranded wire, as I feel it is less stressfull on devices(Physically).
If this is only 3 rooms, and only needs lights, and will never need a heater, recepticles for convience, maybe a wall AC, then romex is OK. Tnen it is obsolete?

shader
Oct 11, 2007, 02:31 PM
It appears a lot more info is being posted here than asked for. The original poster only asked for a wiring diagram/explanation on how to hook it up, not recommendations on what type of wiring materials to use-though some valid points are noted.

donf-there are simpler ways to wire this type of circuit. What's disconcerting is that in several of your posts you state that you're not a code expert or an electrician, and would defer your answers to electricians who post, yet you freely cite the code and give wiring advice. The code is very complex and many of the articles have exceptions. I know you're trying to be helpful, but posters come here for sound and correct advice, not what people "believe" or "suggest".

And a final thought on "code"- Just because a particular application is allowed by a "national code" doesn't mean it will comply with local codes-some are stricter. Notice tkrussell disclaimer? If it's a small project and with no permit pulled maybe OK. On a larger project problems could arise when selling the house, insurance claims, etc---just FYI

pelle
Oct 11, 2007, 04:57 PM
3 rooms with 4 can lights in each room that is a total of 12 lights even at 100 watts per light it would equal about 10 amps so the circuit breaker will be fine. 14/2 wire is fine this wire will contain 1-black, 1-white and a bare copper wire.
The power will have to run to the first room into a switch box. From this box 2 more wires will be needed... 1 will go to the first lite fixture in this room the other will go to the next rooms switch box.. The wire in the lite fixture box will connect to this fixture and another wire will run to the next fixture box.. Connect all the whites together all the blacks together and the bare coppers.. be sure to use the correct connectors..

Now for the switch box. There should be 3 of each color wire in this box.. the white get all connected together use a red wire nut and tuck these into the box.. the black from the panel and the black to the next switch box and a short piece of black (5" approx) get connected use a red wire nut .. now you should have 2 black wires and all the copper .. The 2 black wires should be 1 5" piece that is connected to the main panel and the next switch wires and the one black going to the light fixtures.. take these 2 blacks and connect them to a signal pull switch (ordinary lite switch).. take the copper and twist them together and connect 1 of the strands to the switch green screw

abcsalem
Oct 16, 2007, 10:01 AM
It was mentioned in the previous post that, if the original post member uses 100w light, then 12 of them on 15A breaker is fine.
Question: Considering the 80% design capacity rule,
When it comes to placing only lights on a breaker, what size light (MAX) can one
To assume, so that one can calculate what breaker size and wire size to use?

pelle
Oct 16, 2007, 05:35 PM
12 lights at 100w is 1200 watts divide this by 120v is equal to 10amps using ohms law
which is amps = watts divided by voltage.. so 10 amps is 66% capacity on a 15 amp circuit..

abcsalem
Oct 16, 2007, 06:55 PM
12 lights at 100w is 1200 watts divide this by 120v is equal to 10amps using ohms law
which is amps = watts divided by voltage .. so 10 amps is 66% capacity on a 15 amp circut ..
That's understood. The question was, what size, i.e. how much watts per light socket one needs to assume when figuring the total wattage for a breaker? Do electricians assume
People would go maximum of 100watts light bulb in a residential settings per light socket?

labman
Oct 16, 2007, 07:29 PM
Many fixtures specify 60watts max.

I do want to point out Pelle is just as wrong where he insists the feed must be to the switch as Donf is where he insists it must be to the light. As I said, either way is safe, workable and code compliant. Usually I would go with feeding the closer one to save time and wire.

Flying Blue Eagle
Oct 16, 2007, 08:09 PM
I go along with 9Donf ) answers he has it down pretty close .

labman
Oct 16, 2007, 08:36 PM
I am very disappointed in many of your answers as well as his. We have a top notch electrician here. I would like to see more questions left for him if people can't get things right.

donf
Oct 17, 2007, 09:25 AM
Interesting conversation albeit way off the original topic. First off, I'd like to take a position on labman comments. I agree that I am neither a electrician, nor an expert on the code book. That said, I have close to 50 years exp. Around electronics and electricity. When I was just out of diapers I ran parts back and forth to workers on the Major Deegan Expressway in the Bronx. Granted it was nothing more than take this over there. I was working under the table for Brown Electric Co.

However, I am reasonable competent around electricity and I do know when to call the power company or an electrician.

As to the code, my current code book dates back to the 1980s and I am waiting for the 2008 to appear at my door. I haven't had to use a code book since I left the field as an IBM tech and went to the R&D labs in Bocca, Dallas and Lexington.

I prefer to bring power to the overhead outlet and then switch loop to the wall switch. Labman prefers to bring power to the switch and then continue on to the load. It is six of one kind and a half dozen of the other as far as I am concerned. But remember on new construction, commercial or residential, the electrician doesn't get to decide. He has wiring plans that tell him which way he is going to install the wiring.

As to Mr. Russell, he corrects me when I make a blatant mistake and guides me on mediocre answers.

Oh, did I forget to tell you that I'm studying for the "Master's Electrician Test?

Don

donf
Oct 17, 2007, 09:29 AM
One other thought here, has anyone noticed that the sizes of the rooms is still unknown.

Code calls for the calculations to start with the outside size of the room to determine how many circuits must be run. Once you have that, then you know what is needed to light the room from there you can determine how many lamps are needed in order to purchase the end user equipment.

labman
Oct 17, 2007, 10:09 AM
Do you really think your blatant mistakes help anybody? I am sick of going through the plumbing, heating, and electrical correcting bad answers.

donf
Oct 17, 2007, 10:26 AM
Then don't go through them! Stick to what you appear to know best, rearing dogs!

labman
Oct 17, 2007, 11:31 AM
And let people follow bad advice from those that aren't giving good answers?

donf
Oct 17, 2007, 12:08 PM
Labman,

Again, I'm perfectly willing to take up this discussion with you off-line of this forum, via e-mail. You and I squabbling back and forth is pointless to any useful forum item as well useless to you and I ever finding any common ground.

If taking our topical battles out of the forums ia acceptable to you, please send me a PM.

tkrussell
Oct 17, 2007, 03:44 PM
Can someone please show me a mistake?

Let's us all step back and relax.

Labman, please quote what don is in error of?

MOWERMAN2468
Oct 17, 2007, 05:32 PM
I am very disappointed in many of your answers as well as his. We have a top notch electrician here. I would like to see more questions left for him if people can't get things right.
Well, perhaps you need to know someone's qualifications before indicating they do not know what they are talking about. I am absolutely sure that one of them happens to have held many, many electrical certifications, and license. So just because you do not agree does not make you right.
Perhaps they do not agree with you if they were to step in on your area of "expertise" on dogs. But that would not mean that you were specifically incorrect does it. And it also does not mean that they would be disappointed in your opinions or views.
Take two aspirins and call me in the morning. Ha ha

MOWERMAN2468
Oct 17, 2007, 05:33 PM
Can someone please show me a mistake?

Let's us all step back and relax.

Labman, please quote what don is in error of?
Hey and while your at it labman, lets see where you could say flying blue eagle is wrong. Well??

labman
Oct 17, 2007, 05:40 PM
Labman,

I have an obsession with switch loops? He defines his room as 4 lights and one wall switch. If he doesnt use a loop to tie the switch into the circuit how is it going to connected?

12/3 is a typo. 12/2 is correct, thanks.

The big objection I have in this thread is his insistence on using switch loops. He doesn't even seen to understand you can feed the switch. In this, or any circuit, a switch loop may or may not be the most efficient way of doing it. There was also the careless reference to 12-3.

MOWERMAN2468
Oct 17, 2007, 05:40 PM
And let people follow bad advice from those that aren't giving good answers?
Well labman, got to spread some around, but if you took your own advice and stayed out of electrical, plumbing, etc... you would not have to worry about it and have a stroke.

MOWERMAN2468
Oct 17, 2007, 05:43 PM
Labman,

Again, I'm perfectly willing to take up this discussion with you off-line of this forum, via e-mail. You and I squabbling back and forth is pointless to any usefull forum item as well useless to you and I ever finding any common ground.

If taking our topical battles out of the forums ia acceptable to you, please send me a PM.
Man ain't it so. To bad. Ohh well, I guess I would just trust the "real" electricians here. But perhaps you should check with a local electrician for your local codes. And then go from there.

Flying Blue Eagle
Oct 17, 2007, 05:56 PM
The big objection I have in this thread is his insistence on using switch loops. He doesn't even seen to understand you can feed the switch. In this, or any circuit, a switch loop may or may not be the most efficient way of doing it. There was also the careless reference to 12-3.
Then heed to donf's advice and stay outa these areas, and you will not be so upset. And 12/3 could be used to have more than one switch.

ceilingfanrepair
Oct 17, 2007, 10:33 PM
I missed this whole dilemma. I will say, I have never seen LabMan give a bad electrical answer (that I recall) and I have seen plenty of others in this thread give incorrect answers. It's not always about how much you know, sometimes it's about knowing your limits. Too many people overreach and try to answer a question when they really don't know what they're talking about.

tkrussell
Oct 18, 2007, 03:37 AM
Bringing a feed to a switch, then onto the light is fine, as is bringing a feed to a light and then having another cable going to a switch, a "switch loop", is fine also.

This is not a matter of right or wrong, but preference, depending on the size of boxes and how many wires can fit, and economizing on lengths of cable.

So what is the problem? I do not see anyone "insisting". What am I missing?

I appreciate anyone not being in the trade to inform the person asking a question that the answer is from a layperson. This allows the person receiving the answer to qualify the answer, and realize to take the advice with a grain of salt.

If someone has a different answer, then give it.

If a typo is found, note it.

If a piece of advice does not make sense, then mention it and ask why? It may be a typo or brain cramp.

Noting a few other items I found that have collected in this post:

A discussion on the max size of a fixture being 60 watts. Each SOCKET has a max rating of 60 watts. What about a 10 lamp chandelier, each socket rated at 60 watts? The fixture will have a total load of 600 watts, which is fine, but needs to be considered when calculating the total circuit load.

Most recess lights are rated more than 60 watts.

Found a comment that #14-2 cannot be used to "hardwire" to a fixture. Where is that stated in Code?

There is no problem using #14-2 cable to hardwire to a recess fixture.

Regarding different wiring methods. We all must keep in mind that this is a forum that each section of the country will have it's own unique methods, either due to local Codes, local weather, local construction methods.

While Romex is widely used, there may be areas that it is just not used at all. In Chicago, no matter what is being wired, conduit is the only method allowed. Remember the little fire they had once?

In Key West, being surrounded by ocean, most construction is masonry, and Romex is not preferred. Neither is any aluminum wire, due to the corrosion caused by the salt air.


My point is, while one may work in your town, another may not be typical in another, for different reasons. Hence the reason to always recommend that local codes be checked.

So while there is varying methods of wiring due to local conditions, there are also varying methods to circuitry. Pros and cons to either.


If there are any answers given that someone thinks it is "bad advice", use the Report Inappropriate Post button, and point out the information in question, and let me take it from there. When there are discussions in one post, I may miss something.

I wonder what the original poster, JLH2001, (anyone remember him?), thinks of this discussion.

donf
Oct 18, 2007, 05:46 AM
The big objection I have in this thread is his insistence on using switch loops. He doesn't even seen to understand you can feed the switch. In this, or any circuit, a switch loop may or may not be the most efficient way of doing it. There was also the careless reference to 12-3.

Labman,

For the last time, I will even try using English this time.

I am not obsessed with switch loops, I have stated that on multiple occasions. However, I do prefer to install overheads that way. You are obsessed with power to switch then to overhead, That's Fine with me!

Also as previously stated, "12/3" was/is a typo. You corrected me on that and I acknowledged your correction as being my mistake. Guess what, the world didn't end because I made a typing mistake!

You know, I like what I read from you and more often than not I will echo your response, again I ask, why the ferocity? I'm not your enemy here. If you tell me I'm wrong, I'm adult enough to accept your response and go back to the book and see why I'm wrong. It does not hurt my ego one little bit.

For goodness sakes, I referee High School Basketball and Baseball along with all manner of independent leagues. I understand criticism is just one way of helping the poor guy. Just ask any spectator on a safe/out judgement call. They will tell you what the umpire did wrong.

MOWERMAN2468
Oct 18, 2007, 10:10 AM
Hey some good responses here as of late. And as far as me saying that 14/2 was not allowed in code, I thought that I had mentioned in MY locality it did not meet code. With that said, good day.

tkrussell
Oct 18, 2007, 01:13 PM
This thread is closed.