View Full Version : Convert Table Saw from 110V to 220V
wbp
Sep 24, 2007, 09:47 AM
I have a table saw (Sears Craftsman Professional, 1-3/4hp) that can be converted from 110v to 220v. Can I just use the 110v plug it came with and plug it into a normal 110v receptacle that is wired with two hot wires and a ground? (I've run 12/2 NM on a 20AMP CB). Aside from the obvious risk of accidentally plugging in a 110v tool into the newly 220v receptacle I can't see any other issues. Also, the manual says that the start switch is "4 pole" and will need to be modified, but it does not say how. How could changing the voltage of the motor alter the on/off switch? Any advice will help greatly!
dherman1
Sep 24, 2007, 10:04 AM
DO NOT UNDER ANY CIRCUMSTANCE WIRE 220 to a 110V RECEPTACLE. THIS IS A DEATH WAITING TO HAPPEN. EITHER BY ELECTROCUTION OR FIRE!!
When I converted my table saw to run on 220, I went and bought a replacement cord at Depot. They had a 220v extension cord that had the correct plug on one end and I cut off the other end to attach it to the table saw.
I did need to change the switch to accept the load change,I just can't remember how. But, it was in the manual, if somewhat obscurely written.
Good Luck, Dan
biggsie
Sep 24, 2007, 10:12 AM
I have been in rental houses that wired 220 to a 110 outlet --- what a shock..
Can not believe this is up to code?? Any way you need to run a 220 volt
Outlet with 220 volt plug wired to a 220 volt rated switch ( BOTH LEGS SWITCHED )
And then you can change motor to 220 volt... keep AMPERAGE in mind, breakers
And wire need to be rated for load of motor, depending on distance from breaker box
KISS
Sep 24, 2007, 10:19 AM
The cord is fine, but buy a good quality 220V 20 A plug and a 220 20A receptacle. The motor MUST be rewired based on the nameplate instructions. The switch needs to have both hot legs switched. With 110 volts, only the blacks go to the switch. The other terminals on the switch need to switch the black wires.
Incidentally, the term poles seems to be used incorrectly. 4 terminals would make more sense.