ceilingfanrepair
Sep 6, 2007, 11:04 AM
My church has acoustical tile ceilings, and therefore is lit in the majority of areas with 2x4' recessed fluorescent fixtures. These are the types with four bulbs and two ballasts.

When they moved into this location, one of the maintenance men unscrewed one bulb in each fixture, so only two of the four bulbs would light. They left the other bulb screwed in and both ballasts connected.

My understanding is, that the ballasts are still drawing current whether the bulbs are working, burt out, or missing. So this past week I went through and disconnected one ballast in each fixture.

Did I waste my time? Is the amount of current drawn by an unused ballast significant, or negligible? If I had to guess, there were probably about 50 fixtures.

tkrussell
Sep 6, 2007, 12:34 PM
Assuming each fixture is using the typical magnetic ballast for two 34 watt T 12 lamps, each ballast alone consumes 6 watts with no lamps.

So the savings is 50 units at 6 watts each totalling 300 watts, which running for one hour is .3 Kwh at $0.10/Kwh cost of power is a savings of 3 cents per hour the fixtures are in use.

While the cost savings may not allow you to open a Swiss bank account, there is still savings, plus you now have 50 ballasts out of service that cannot catch fire or contribute any heat to the space.

ceilingfanrepair
Sep 6, 2007, 12:47 PM
Hmmmm.. . We do need a significant decrease in our electric bill, it looks like this alone is not going to do it!

I will now be turning my attention to the fact that they run the air conditioner at less than 70 degrees, because when the building fills up with people it becomes 80-90 degrees regardless.

Other than HVAC, and lights, I don't think we use much current. Our PA and instruments are only in use during service. We have a barber shop and beauty shop as part of the church, but whatever appliances they use I'm pretty sure are minimal. I think the computers are turned off when not in use.

tkrussell
Sep 6, 2007, 01:26 PM
As far as the lighting, you should consider replacing all the ballasts to 4 lamp T8 electronic with T8 lamps. Check your area, there may be rebates available from the state, public utilities, or power company to retrofit over to energy savings lighting system.

ceilingfanrepair
Sep 6, 2007, 02:06 PM
I do NOT see our Pastor going for that! He's not one for spending money on things he can't tangibly see an improvement from. Besides, we don't own the building.

tkrussell
Sep 6, 2007, 05:50 PM
Many renters of commercial properties put money into the building if the lease is still has a reasonable amount of time left, and esp. if they plan to stay there.

The benefit would be better improved quality lighting plus the energy savings.
At least worth looking into the possibilities of rebates, some areas have generous paybacks.

ceilingfanrepair
Sep 6, 2007, 08:10 PM
Yes but I know how he thinks.

Our HVAC works in four zones of 1500 square feet each. Two of the zones are the sanctuary, two are offices. We get a bill for each. The sanctuary zones cost us around $250 each, the office zones $130. They keep the air on 68 except Saturday night they turn it to 60 so that it will be cooler for Sunday. It's always freezing cold when the building is in light use, and burning up hot when it's full of people.

Ideas? I suppose I should go post in the HVAC section but I've never ventured out of Electrical and Lighting.

Stratmando
Sep 7, 2007, 06:34 AM
If Changing lamps not an option. At least you have immediate back up should one fail.
I would disconnect hot to unused ballast as you have already done.

ceilingfanrepair
Sep 9, 2007, 11:04 PM
Pictures are worth many words.

http://www.bandwidthcrazy.com/mr_spiffy/church.jpg
http://www.bandwidthcrazy.com/mr_spiffy/church3.jpg
http://www.bandwidthcrazy.com/mr_spiffy/church4.jpg
http://www.bandwidthcrazy.com/mr_spiffy/church8.jpg

tkrussell
Sep 10, 2007, 02:42 AM
I don't see an EXIT sign at the door to outside.

Aren't paddle fans fun to install into a drop ceiling?

Oh and the clock is on the wrong time.

What the hell you doing there at a quarter to midnite?

labman
Sep 10, 2007, 04:28 AM
You might give Heating and Cooling a look. It is much like E&L and Plumbing with a very good professional as the forum expert.

It has been my experience many commercial spaces the HVAC is not sized to cope with large numbers of people. Maybe Northern Heat can help you get the most out of what you have.

ceilingfanrepair
Sep 10, 2007, 01:08 PM
TK, call me sometime and I will tell you some stories about the way this building is wired. If I took pictures above the drop ceiling, or behind the light switch panel, I'm sure you would commit suicide, kill yourself, and then jump off a building. The exit signs (lack thereof) and my fans are nothing. Another church used this facility before us, one of their members must have been an amateur electrician.