PDA

View Full Version : Propane gas generator


Joe Nardini
Jul 3, 2007, 06:56 PM
I have a customer who recently had a new 16 kW propane gas Generac generator installed.
When and only when the generator is running, his APC/UPS keeps toggling back and forth indication a incoming power line problem. I checked the neutrals, grounds and phase connections and all seems OK. I heard in the past that a gas aspired generator is not conducive to a UPS or computer is this the problem?

Thank You,

[email protected]

tkrussell
Jul 3, 2007, 07:36 PM
The issue may be the frequency and/or voltage from the genset causing the UPS to think the power is not adequate.

The issue you mention with UPS on gensets is that a UPS is a highly capacitive load that the genset has a problem with.

Generally speaking the KVA of a genset should be at least 1.5 times the KVA rating of a UPS. Ideally there should be an equal amount of inductive load on a genset to help counteract the KVAR of a UPS.