Hi -
I am doing a Master Bath renovation and changing the plumbing locations. Also, in the future I will be redoing my kitchen and eliminating a wall where the main waste line runs so basically, I need to relocate everything.
I attached a layout of what I am looking to do and am looking for input.
1. The shower that I have circled...it is located 6' from the vent. Is this an acceptable distance?
2. Can the sink from the 1st floor be vented in the drain from the shower above?
massplumber2008
Jul 7, 2019, 11:21 AM
Hi.
Absolutely nothing you have drawn is even close to correct...sorry.
So, #1....no
#2.....No, you cannot tie a shower from the second floor into the vent for the kitchen sink from the first floor.
The lavatories are not piped properly...you cannot have sanitary tee fittings on the horizontal like shown in the picture or in the drawing. Further, you can't have 4 sinks on one drain line and only have the one vent. Someone that did the previous work didn't know anything about plumbing, for sure!
Final thought...why not connect the shower drain into the capped fitting off the vent stack? You would still need to vent the shower but this would allow you to keep the shower on the same floor. Even better, would be to connect the shower and sink drain(s) into the drain for the toilet and then vent the fixtures as required by code.
Thoughts?
Mark
adkhkr
Jul 9, 2019, 04:41 AM
Thanks for the input... Here is a revised sketch based on your comments.
Any better? https://uploads.tapatalk-cdn.com/20190709/9c62f7fdf2d662e0674091791331f25d.jpg
Sent from my SM-N960U1 using Tapatalk
massplumber2008
Jul 11, 2019, 04:03 AM
Getting closer here...
Codes vary by state, so hard to say exactly, but in most cases...
If you start 4" in the basement then you need to keep the drain 4" all the way up and through to the roof. You would take off branch drains using 4"x3" fittings (wyes on horizontal, sanitary tees if on vertical). Where you have the 4" branching left and right in 3"...exactly what fittings were you going to use to do this?
Most likely, again check local code, you may need to increase the toilet vent to 2".
Install cleanouts at the base of the 4" stack and at the base of the kitchen sink drain as well as under the kitchen sink cabinet.
Lavatory sinks still not right. Give me a day or two and I'll try to find you a picture of the proper way to pipe up 4 sinks.
adkhkr
Jul 11, 2019, 05:57 AM
This is what I had in mind where the 4 inch pipe splits.... And than cap the top of the pipehttps://uploads.tapatalk-cdn.com/20190711/66fa5d1d516b496199a96b6c4d255664.jpg
Sent from my SM-N960U1 using Tapatalk
adkhkr
Aug 19, 2019, 04:19 AM
Here is a revised layout... Any more suggestions? https://uploads.tapatalk-cdn.com/20190819/0ecbe46c11734951844e64820d5a2d2e.jpg
Sent from my SM-N960U1 using Tapatalk
massplumber2008
Aug 21, 2019, 03:05 PM
49212
Reduce the shower vent to 1.5"
Install Wye fitting on horizontal to pick up shower drain
Proper lavatory sink piping vent should be as I've drawn it. I didn't include the ptraps because it would crowd the drawing (in this case).
The wye and 90 I've indicated is better than the double sanitary tee fitting you posted...if drain gets snaked the snake could cross over this fitting. You are better off using a wye fitting on the vertical (lower) and install a long sweep 90 at the top to pick up the left drains.
Do not forget a cleanout at the base of the waste stacks.
Use long sweep 90s when going from horizontal to horizontal.
Mark
adkhkr
Nov 5, 2019, 09:49 AM
Finally getting back on the project.
In this photo...I have the following questions.
In red...are those Wye fittings?
In green...is 1.5" sufficient for the drain lines?
In Blue...is 1.5" sufficient for the vent for the combined shower and first floor sink?
In Yellow, is 1.5" sufficient?49243
Sent from my SM-N975U1 using Tapatalk
adkhkr
Nov 5, 2019, 10:57 AM
I had my sink layout wrong.. the attached picture is the correct layout.
1. Can the red drain line be 1.5"?
2. How to the vents go with this layout?https://uploads.tapatalk-cdn.com/20191105/c14dff95652eb9c764bd3bc39c59d317.jpg
Sent from my SM-N975U1 using Tapatalk
massplumber2008
Nov 6, 2019, 04:52 PM
Hi Adkhr
That picture above better not be correct....look at the last picture I posted. It is the only way to do back to back, in fact, double back to back lavatories....*wink*.
Now, In Green I would DEFINITELY run 2".
In Yellow, run 1.5" vent for the shower
Where the vent from the kitchen sink and the shower connect (Blue) increase vent size to 2" using a 2"x2"x 1.5" sanitary tee fitting...run 2" over to the vent stack.
The Red will depend on your local code requirements (see pictures). Some use double wye 1/8th combination (also called a double fixture tee) fittings, some use double sanitary tee fittings...it is STATE specific issue. The argument surrounds snaking the drains as well as air to water drain ratios, so it turns out to be up to each state. I'd suggest calling a local inspector and just ask him, "if I am installing back to back lavatories do I use a double sanitary tee or a double wye 1/8th combination fitting". This is the only way you can be guaranteed NOT to have to redo the work.
49245
49246
Are you clear on the way I drew this up otherwise?
Mark
adkhkr
Nov 7, 2019, 12:50 PM
See attached...doing the drains back to back isn't going to work. With that said, what option do I have given the separation between each sink? Would a 2" circuit vent like the one in the pic be acceptable?https://uploads.tapatalk-cdn.com/20191107/345b253faa2e5a032d4cbb9364332d65.jpghttps://uploads.tapatalk-cdn.com/20191107/05aa0ff1ed7567ced07883c83dcab137.jpg
Sent from my SM-N975U1 using Tapatalk
massplumber2008
Nov 8, 2019, 10:30 AM
That is used in commercial plumbing and is not used in residential setting, so I would not recommend it here.
You can pipe this as I presented...just turn the double sanitary fittings sideways (see image) and stub out to each sink with 90 degree elbows. Install ptraps to sink and all set.
49248
Mark
adkhkr
Nov 10, 2019, 04:29 AM
Got the vent for the sink and shower in coming around the corner. Does this look good? Where the 1.5/1.5 inch pipe transition to the 2 inch, is the fitting I used correct? And I used a vent elbow, not a sweep 90. Is that ok?
For the sink layout, can I use the sizes shown? Would a 1.5 inch Wye fitting and transition to a 2 in pipe be ok? Or should I use a 2 inch Wye? It's a little easier to fit the smaller Wye in the wall but if a 2inch is better I'll make it work.
Thanks.
Bradhttps://uploads.tapatalk-cdn.com/20191110/44c331b7b5e0bf3f33744f082c00bf21.jpghttps://uploads.tapatalk-cdn.com/20191110/2816c84d111b7edc52dd5fba4ebd4f58.jpg
Sent from my SM-N975U1 using Tapatalk
massplumber2008
Nov 10, 2019, 08:50 AM
Going down to the 1.5" DOUBLE FIXTURE TEE should be just fine...but not a double wye fitting.
Otherwise, looking great!
adkhkr
Nov 10, 2019, 09:20 AM
I can squeeze in the double wye 2inch and put in a 2 to 1.5 bushing for the stub outs. Here is the layout, does this look good? The blue is the 3 inch, the red from the side is the 2 inch vent. I have the 3x3x2 T with it sloped up. Is that the right way to do it?https://uploads.tapatalk-cdn.com/20191110/a232d114ac52e7211cb43fd803682d36.jpg
Sent from my SM-N975U1 using Tapatalk
massplumber2008
Nov 10, 2019, 08:31 PM
Why did you point the street 45 up in the double wye on the right...that won't work? Let me know why...
adkhkr
Nov 11, 2019, 10:42 AM
This should work, just have to turn it 90 into the wall from the wye. Have to hack the stud to get it in there but it should work. How does it look?https://uploads.tapatalk-cdn.com/20191111/d339e95fed8b26245797858de767b45a.jpg
Sent from my SM-N975U1 using Tapatalk
massplumber2008
Nov 11, 2019, 03:03 PM
I would really prefer to see you use double fixture tee fittings instead of the double wye fittings, but if you can't find them then the double wyes will have to do! In that case, looks great!
The work looks nice and clean...straight!
adkhkr
Nov 13, 2019, 05:12 AM
Managed to find the fittings online...had some issues getting the straight section in hence the 2 couplings. https://uploads.tapatalk-cdn.com/20191113/088808cc3d94def659e3edf57d842713.jpg
Sent from my SM-N975U1 using Tapatalk
massplumber2008
Nov 13, 2019, 11:39 AM
Nicely done!
Looking real good, EXCEPT...
Technically, Jim caps (the black rubber caps you have on the stack) are not allowed inside a finished wall or floor.... Please message me your telephone number if you want to chat about that more, or if not comfortable with that we can discuss through here.
Back to you...
Mark
adkhkr
Nov 24, 2019, 07:04 AM
Got sidetracked this week but here is the sinks completed less the venting...I'll message you, thanks!https://uploads.tapatalk-cdn.com/20191124/0c94d1628e360588f67bc55edc3e5fd5.jpg
Sent from my SM-N975U1 using Tapatalk
massplumber2008
Nov 24, 2019, 09:07 AM
Nice job...looks great!
adkhkr
Dec 1, 2019, 12:08 PM
Except for the rest of the pex supply lines, this wall is done. This was a tough one. https://uploads.tapatalk-cdn.com/20191201/972a85138f4edaf3b5315b72199c3fbd.jpg
Sent from my SM-N975U1 using Tapatalk
massplumber2008
Dec 2, 2019, 08:25 AM
It was a lot of work, no doubt...drilling large holes is a blast, huh??
You did a nice job here...very clean.
adkhkr
Dec 6, 2019, 01:21 AM
For the toilet plumbing, does this look right?
4x3 closet bend to 3x3x2, with the 2in vent going up the wallhttps://uploads.tapatalk-cdn.com/20191206/dc19111dd5e1f3f14415c4ea8feab60e.jpg
Sent from my SM-N975U1 using Tapatalk
massplumber2008
Dec 6, 2019, 05:30 PM
Tee goes in the other direction (flip it)...with the flow so water/condensation build up flows down the drain.
Otherwise, fine.
I like to use a 3" 90 and then install a 4"x3" stainless steel ringed closet flange but what you have there is fine as well.
adkhkr
Dec 7, 2019, 08:15 AM
Slow but steady lol
Working my way towards tackling the fernco fitting that needs to go.https://uploads.tapatalk-cdn.com/20191207/7b67e52d6ad2e133f59fc3fd885e7c0d.jpg
Sent from my SM-N975U1 using Tapatalk
massplumber2008
Dec 7, 2019, 12:36 PM
You follow directions well....nice job.