200 amp service 450 feet underground will 250 urd cable be enough.

donf
Oct 3, 2014, 07:21 AM
If you truly need 200 amp, then you will need 350 kcmil conductors for 450 ft. That will give you just under 3% voltage drop leaving you an additional 2% end to end recommended max of 5% voltage drop.

Also, if this from a main service panelboard to a downstream panelboard, then you must use a four wire feed to the downstream panelboard and an independent grounding and bonding system must be set up at the secondary site.