Log in

View Full Version : 230 volts compressor


Elkhunter
Sep 17, 2013, 02:26 AM
I just got for my walk In cooler an conpressor with condensing unit. The conpressor tag says 230 volts 60 hz 1hp single phase motor with max fuse 15 amp. I was figuring of running about maybe 20 ft of 12-3g from a double pole 15 amp breaker In the panel to hardwire to the compressor and condensing units wiring box. It's a older machine and I just wanted to make sure this was correct way to hardwire it in. Any suggestions? Thanks for your time

hfcarson
Sep 17, 2013, 04:18 AM
Unless you are less than 50 feet and within sight of the panel, you should install a disconnect at the equipment. What type of wiring are you using? Just a guess, but it sounds like MC cable or conduit would be appropriate. (If this is a business avoid using romex)
Otherwise, it sounds like you're OK...

stanfortyman
Sep 17, 2013, 04:55 AM
This is a walk-in? I assume it's a commercial setting?

Your best, and probably only, bet is to hire an electrician to do this. You should not be doing electrical work on a commercial place. Your own home is one thing if you don't really know what you are doing, but a commercial place where there will most likely be many people on site is not acceptable.

Elkhunter
Sep 17, 2013, 07:33 AM
Thanks for responses. This is not a commercial walk I'n cooler I'm a big time hunter I process my own meat. This is for personal use. What would be a adequate service disconnect. I have 12-3 romex and 12-3 wire for"wet" locations to be run I'n conduit. Thanks again

Elkhunter
Sep 17, 2013, 07:46 AM
Thanks for responses. This is not a commercial walk I'n cooler I'm a big time hunter i process my own meat. This is for personal use. What would be a adequate service disconnect. I have 12-3 romex and 12-3 wire for"wet" locations to be run I'n conduit. Thanks again

I am less then 50 feet max is 20 feet and the electrical panel is outside the cooler door like 8 feet. Cooler is 8 by 10 by 8 ft tall with a 5th by 8ft room with the electrical panel. This pretty much matched the existing length of shed and a place to hang gambels and scales and other things. The compressor and condensing unit is outside of the cooler itself I'n a little 4 ft by 4 ft room on back of cooler. A copper tube runs from the unit to a cooling fan inside the cooler. Thanks