View Full Version : Lennox A/C HSXA15 outside unit not working


SLacy
Aug 21, 2013, 05:12 PM
Hello, I've checked the breakers, used a volt meter to confirm voltage to both the unit and the T-stat. Jumped the wires on the T-stat and still am having no luck. Any help would be greatly appreciated!

ma0641
Aug 21, 2013, 07:52 PM
You measured 240 on both sides of the contactor? Contactor closes?

SLacy
Aug 22, 2013, 03:49 PM
Is the contractor the first component that the house power runs to?

SLacy
Aug 22, 2013, 03:58 PM
If that is the contractor, then there is 240 going in and on the bottom where the leads come out, nothing..

mygirlsdad77
Aug 22, 2013, 05:15 PM
Okay, so you have 240 in, but not out. Do you have 24v to the contactor coil (terminals that the t-stat wires hook to?)

SLacy
Aug 22, 2013, 07:11 PM
Okay, so you have 240 in, but not out. Do you have 24v to the contactor coil (terminals that the t-stat wires hook to?)

I'm not sure what you mean. Am I checking on the same contactor as I did to test the incoming power but at a different location on the same contactor? I'm not sure where to check on that one, also, I'm definitely no volt meter expert. Once I find the T-stat connection, will I use both the ground and positive wands to pull a voltage reading?

SLacy
Aug 22, 2013, 07:30 PM
I'm not sure what you mean. Am I checking on the same contactor as I did to test the incoming power but at a different location on the same contactor? I'm not sure where to check on that one, also, I'm definitely no volt meter expert. Once I find the T-stat connection, will I use both the ground and positive wands to pull a voltage reading?

Also, I had shut off the furnace switch, would that prevent the voltage reading on the contactor?

mygirlsdad77
Aug 23, 2013, 05:13 PM
Yes, same contactor, different locations, usually on the sides. You will need the furnace power on with a call for cooling from the t-stat. This sends 24v to the coil on the contacter wich in turn pulls the contacts closed sending the incoming 240v through the contacter to the compressor and condenser fan motor.