Compressor was bad got new outside unit now the inside won't shut off or shut off outside unit
Joshdta
Jul 29, 2013, 01:37 PM
If neither unit will shut off inless you turn of breakers then the probem is in the t-stat or t-stat wiring. Or do you mean the unit will not get to temp thus not shut down. In that case could be a number of things including freon problem or unit does not match or lines was not properly vacumed
Shann72
Jul 30, 2013, 07:11 AM
We removed the thermostat from the wall and they still both run I really think the outside unit is wired wrong and the guy says it isn't and wants to charge me to come c so for 3 ays I been pulling the breaker to let it stop for awhile before it blows
if neither unit will shut off inless you turn of breakers then the probem is in the t-stat or t-stat wiring. Or do you mean the unit will not get to temp thus not shut down. in that case could be a number of things including freon problem or unit does not match or lines was not properly vacumed
Joshdta
Jul 30, 2013, 01:48 PM
Are any wires touching each other at the t-stat. it your system a gas furnace and ac or a heatpump?
Shann72
Jul 30, 2013, 02:35 PM
No thermostat isn't hooked up at all right now and it is a ac/heatpump
are any wires touching each other at the t-stat. it your system a gas furnace and ac or a heatpump?
Joshdta
Jul 31, 2013, 01:44 AM
Yellow and red t-stat wires are touching somewhere. This is the only way both units would run
Stratmando
Jul 31, 2013, 06:00 AM
Identify thermostat wires at Air Handler, remove, and test for open between each of the wires, then twist all together at one end, go to the other and verify you have continuity, with all the wires disconnected at the Air Handler, It should not run, If it doesn't, it was a short in the wiring.
If it still keeps running with the wires disconnected, the Thermostat is not the problem, Problem is in Air Handler.
Shann72
Jul 31, 2013, 07:24 AM
A friend is coming today to check because the
Thermostat isn't even wired and either unit will shut off I really think he didn't wire outside correctly thanks will post results
if neither unit will shut off inless you turn of breakers then the probem is in the t-stat or t-stat wiring. Or do you mean the unit will not get to temp thus not shut down. in that case could be a number of things including freon problem or unit does not match or lines was not properly vacumed
Stratmando
Aug 1, 2013, 06:09 AM
I Understand thermostat is not hooked up, did you read the above post, especially the part about disconnecting the wires in air handler, to be sure a short on the thermostat wires is NOT the cause.
Shann72
Aug 1, 2013, 06:22 AM
Has to be outside I think cause that was the only wires he messed with my friend couldn't come last night so they both still on and I. Afraid to mess with it
yellow and red t-stat wires are touching somewhere. this is the only way both units would run
Shann72
Aug 1, 2013, 06:24 AM
I just saw you post I don't know what the air handler is lol
I Understand thermostat is not hooked up, did you read the above post, especially the part about disconnecting the wires in air handler, to be sure a short on the thermostat wires is NOT the cause.
Stratmando
Aug 2, 2013, 07:20 AM
The Inside Unit is commonly called an "Air Handler", and the unit outside, the "Compressor Unit",
The Air Handler has a 24 volt transformer, and supplies power to the thermostat, the thermostat will make connections to trigger relays in the Air Handler, to turn on the Fan and compressor for cooling, or the fan and heat strip for heating.
If thermostat wires are disconnected at the Air handler, and it still runs, problem is at the air handler with a relay stuck, or support electronics energizing relay.