N4HMR
Feb 17, 2013, 01:09 AM
I am about to buy 75' of 10/4 stranded cable (Carol cable) to hook up two generators (to two different homes). Ain't screwing with two generators hooked to the same house - yet.
I will use 25' of cable to connect a 7,000 watt unit to my home, and the remaining 50' to connect a 9500 watter to the other home.
The manual on my 7,000W unit claims (note I wrote 'claims') that it will produce 57A at 120vac or 28.3A at 240vac. I will be using an L14-30P plug to pick up juice from my gen, and that connector has two 30A breakers on it.
I don't know what the amp ratings on the 9500W unit are, but they should be reasonably higher.
I just read an interesting post - "What is the amp rating for a 75' run of 10-3 romex wire?", and the conclusion was that the 10/3 (solid conductor) Romex was good for 30A max, period.
So, my questions are:
1. Will the 10/4 stranded cable support a higher amp load than the 10/3 Romex? One (me, for ex) might be inclined to think that the answer is 'Yes', mainly due to the multiple strands of wire per connector, and due to the 'skin effect'.
2. What is the max ampacity of 10/4 (or 10/3) stranded cable?
3. I think I will be OK with this cable for the 7,000W unit, but what about the 9500W unit? Maybe just a bit more voltage drop due to the longer length?
4. If both hot legs of this connection were each carrying 25A of 120vac load (no 240vac loading), wouldn't an Amp clamp read 50A on the neutral connector?
5. There will be a frame ground wire also, which will be bonded electrically with the neutral in the house panel, but in looking at the schematic for the gen I did not see any connection between gen frame ground and any neutral point in the A/C pathways.
The gen is supposed to have a frame ground wire added to either an earth ground rod or a metal water (not gas) pipe, etc.
If the neutral connection were to become open, then in spite of the frame ground connection, it would seem that no 120vac load would function at all. However, a 240vac load should work normally.
Is this correct?
Please advise asap.
Many thanks
Fred
N4HMR
I will use 25' of cable to connect a 7,000 watt unit to my home, and the remaining 50' to connect a 9500 watter to the other home.
The manual on my 7,000W unit claims (note I wrote 'claims') that it will produce 57A at 120vac or 28.3A at 240vac. I will be using an L14-30P plug to pick up juice from my gen, and that connector has two 30A breakers on it.
I don't know what the amp ratings on the 9500W unit are, but they should be reasonably higher.
I just read an interesting post - "What is the amp rating for a 75' run of 10-3 romex wire?", and the conclusion was that the 10/3 (solid conductor) Romex was good for 30A max, period.
So, my questions are:
1. Will the 10/4 stranded cable support a higher amp load than the 10/3 Romex? One (me, for ex) might be inclined to think that the answer is 'Yes', mainly due to the multiple strands of wire per connector, and due to the 'skin effect'.
2. What is the max ampacity of 10/4 (or 10/3) stranded cable?
3. I think I will be OK with this cable for the 7,000W unit, but what about the 9500W unit? Maybe just a bit more voltage drop due to the longer length?
4. If both hot legs of this connection were each carrying 25A of 120vac load (no 240vac loading), wouldn't an Amp clamp read 50A on the neutral connector?
5. There will be a frame ground wire also, which will be bonded electrically with the neutral in the house panel, but in looking at the schematic for the gen I did not see any connection between gen frame ground and any neutral point in the A/C pathways.
The gen is supposed to have a frame ground wire added to either an earth ground rod or a metal water (not gas) pipe, etc.
If the neutral connection were to become open, then in spite of the frame ground connection, it would seem that no 120vac load would function at all. However, a 240vac load should work normally.
Is this correct?
Please advise asap.
Many thanks
Fred
N4HMR