Log in

View Full Version : Dynavent gas wall furnace lights and then goes out


mbmost
Jan 20, 2013, 11:13 AM
My Dynavent gas wall furnace glo-bar comes on and flame ignites and then goes out and then cycles back to the glow bar on again. Flame ignites and goes out after a few seconds. I replace the wiring harness and ignition control about two years ago. Could this be a problem with the flame sensing probe?

parttime
Jan 20, 2013, 01:12 PM
Hi mbmost and welcome, without a model number its only a guess, but I would try cleaning the flame sensor with steel wool or really fine sandpaper. Good luck

mbmost
Jan 21, 2013, 10:02 AM
parttime,

Thank you for your answer. The model is a Dynavent Vanguard DNV 40 PB. I am going to check out the flame sensor as you suggested. If you have any further suggestiopns based upon the model please let me know.

Thank you!

mbmost

parttime
Jan 21, 2013, 10:36 AM
Hi again, below is a trouble shooting guide from your manual for your problem, make sure the flame sensor is in the flame and clean. Good luck


Burner cycles off and glo bar comes on immediately, check the following:

REMEDY
5. A. Check flame sensing probe. Be sure
Probe is positioned in the burner
Flame and glowing cherry red. Check
Wire and wire connections at probe
And ignition control
B. If wire and wire connections okay,
Check for voltage across brown and
Orange wires at ignition control. If
No voltage, replace ignition control
C. If voltage present, check wiring and
Wire connections at valve
D. If wire and wire connections okay,
Replace valve

mbmost
Jan 21, 2013, 11:06 AM
parttime,

I just removed the flame sensor. It was not only cahed with burned residue but a lot of the sensor just crumbled in my fingers. I ordered a new sendor and door gasket and should be up and running again once the parts get here.

Thanks again!

mbmost

parttime
Jan 21, 2013, 11:17 AM
Your welcome, and keep us posted on the repairs.

That sensor is about the cheapest repair on that furnace, so looks like you lucked out.

mbmost
Jan 26, 2013, 02:46 PM
parttime,

I received the new flame sensor and door gasket. Unfortunately when I removed the door the glo-bar gasket fell apart. Had to wait a few days for that gasket but just put it back together and now my workshop has toasty heat!
Thanks for your help.

MM

parttime
Jan 26, 2013, 04:04 PM
Hi again, That's great news, you've done well. Thanks for the update