Had a breaker problem. One circuit was out. Breaker would not reset.
In my case it was the two 20amp together 40Amp r, double pole breaker that was bad. Works fine now.
It operated about 10 outlets, lamps, TV, small stuff. I asked if I had a short instead of a bad breaker would it be more difficult. He said”
For a short in a circuit, turn each load off, before turning the next one on. If a certain one trips the breaker you have your bad boy. Is this true”?
Or do I have to buy an expensive tester?

creahands
Jul 28, 2012, 05:33 AM
It's true.

There are inexpensive testers out there. Depends on how much u will use it and how much u want to spend. They start at about $15.

Chuck

pastor1189
Jul 28, 2012, 06:15 AM
It's true.

There are inexpensive testers out there. Depends on how much u will use it and how much u want to spend. They start at about $15.

Chuck

Great

Stratmando
Jul 28, 2012, 06:48 AM
"In my case it was the two 20amp together 40Amp".
Sounds like a 2 pole 20 amp, Does it say 40?
A short on a circuit will trip the breaker. A short at a light fixture or fixture wiring would trip when the light switch is turned on.

pastor1189
Jul 28, 2012, 07:42 AM
It was only the breaker. Two 20amp. 40 Total.. Man just replaced the breaker and everything was fine. This particular breaker supplies ten outlets. Two of which have have switches.
Glad it was not a short this time. I have a tester for outlets, but the ones that work off a switch
I do not know how to test.

Stratmando
Jul 28, 2012, 10:26 AM
If you turn on a light switch and it trips, you would want to check/remove the wiring from fixture, and try again, if it doesn't trip now, problem is in that box, the fixture, or a wire got pinched.

pastor1189
Jul 28, 2012, 10:46 AM
Very good

ma0641
Jul 28, 2012, 11:05 AM
I'm still confused. A double 20 amp breaker is not 40 amps, it is 20 amps. Where did the 40 come from. You would never have a 40 Amp breaker supplying room outlets!

pastor1189
Jul 28, 2012, 11:39 AM
Yes it has two 20amps as one unit. With two switches. Type A 40Amps 120-240 vac
Everything is working fine

Stratmando
Jul 28, 2012, 03:35 PM
The 40 amps is confusing and is not 40 amps? Or is it? it is 2 20 amp circuits?
It could be 2 120 volt 20 amp circuits on same phase, or opposite phases. If they share a neutral, they need to be on opposite phases. If you have 240 volts from both breakers, they are on opposite phases.
Does it say 20 or 40 on the breaker? model Number of breaker? The 40 still has us confused? Thanks

pastor1189
Jul 29, 2012, 04:21 AM
40"c Type A 2 pole unit ctl 120/240 vac issue number KN-70
Each breaker button has a 20 on them.. One button was broken
And would not reset. Whole unit was replaced everything fine.now

ma0641
Jul 29, 2012, 06:49 AM
40"c Type A 2 pole unit ctl 120/240 vac issue number KN-70
each breaker button has a 20 on them..One button was broken
and would not reset. Whole unit was replaced everything fine.now

40 refers to the temp rating not the amperage. It is a 20 amp breaker as suspected.

Stratmando
Jul 29, 2012, 07:44 AM
Glad you got it, If it was a 40 amp breaker, I would have been worried.

pastor1189
Jul 29, 2012, 10:05 AM
Yes it a bit confusing because each of the switch has a 20 upon it.
And they are both entwine in a single unit.

ma0641
Jul 29, 2012, 01:46 PM
Yes it a bit confusing because each of the switch has a 20 upon it.
and they are both entwine in a single unit.

That is a standard duplex breaker -20 amp per pole. You would never have a 40 amp breaker for room outlets.

pastor1189
Jul 30, 2012, 04:33 AM
Boy I am learning a lot here. I wonder why they just don't have a single breaker.
If it is only 20 amps. It has two switches, do they trip in concert

Stratmando
Jul 30, 2012, 05:34 AM
When you run out of spaces and you need another circuit, that is what you have to do. They offer the protection for 2 circuits, If there is not a bar attached to both breakers, they will only trip that circuit, it is basically 2 circuit breakers in 1 space.

pastor1189
Jul 30, 2012, 05:44 AM
Great