View Full Version : Running a wire to an outside building with a 3 wires, #10


BGW
Jul 31, 2011, 12:21 PM
When I get to the outside building, I want to use one of the wires on 2 110 breakers for a ground. Will it work to use one ground for both breakers and get 110 out of each?
And also, I was wondering if I could run a hot wire to a building and ground the breaker
With a ground rod at the building and get 100 out of it.

hkstroud
Jul 31, 2011, 12:35 PM
Sounds like you are way off base. What are you trying to do?

BGW
Jul 31, 2011, 02:06 PM
Sounds like you are way off base. What are you trying to do?

For instance, If I run a 220 wire to a building, I would have 2 hot wires and 1 ground.
If I wanted to, could I split it up and have 2 110 receptacles with 1 ground, rather than
The 220.

FadedMaster
Jul 31, 2011, 02:32 PM
You need to hire an electrician is what you need to do. With limited knowledge of wiring you are only going to create problems. Don't attempt this yourself. Hire a professional.

ma0641
Jul 31, 2011, 05:56 PM
Your question does not make sense. If you have a straight 240, 2 wires and a ground, you can't make 120 since there is no neutral.

hkstroud
Aug 1, 2011, 04:41 AM
With a 2 conductor cable which is 3 wires (2 conductors and a ground) you can have either 120V service which requires a neutral or you can have 240V service, which does not require a neutral. The ground is not a neutral and cannot be used as such.

The cable must be approved for exterior use or approve for underground and must be sized (the #10 part) for the amperage draw.

Hire an electrician. You are out of your field of expertise.

FadedMaster
Aug 1, 2011, 07:38 AM
Factually true, right down to the part that the OP needs to hire an electrician.