Jul 17, 2011, 03:09 PM
Outside unit blowing cold air other then discharging hot air when a/c is on.
Not blowing inside the house.
Stratmando
Jul 17, 2011, 03:43 PM
Is the compressor kicking in? 24 Volts at contactor coil?
drtom4444
Jul 18, 2011, 04:16 AM
Sounds like the reversing valve is either stuck or not energizing like it should. It is energized through "O" or "B" (24-30 volts)depending on what part of US you are in. You will need a meter to see what the problem is. If you are lucky it will be a bad solenoid coil on reversing valve or bad t-stat. You have "O"(or B), "Y", and common going to outside unit. "Y" is contactor and "O" (or B)goes to reversing valve. Common is common to both, but you also have a defrost board which also has relays and can go bad, too. A stuck relay on it can keep it from cooling, but probably not the cause. Write back and let us know where you find 24 volts on the wires above.
DrTom4444