macx351
Nov 20, 2010, 08:01 AM
Model PBNU-LD2DN100D, 86k BTU output, external air intake, with White Rogers ignition control model 5OE47.
Have had problems in the past with partly blocked combustion air intakes or exhaust outlets, with
Blocked pressure sensor tubes at inducer fan, with slow inducer fan, with water drain blocked,
With bad igniter, bad limit switch, and bad gas safety valve.
Have corrected all (new safety valve, new limit switch, new inducer fan, new control board, new igniter within last couple years, all seem to be working, also new blower motor) and checked all intake & exhaust & drains & sensor tubes which are not blocked at this time. Have 28v coming off last pressure sensor switch (3 wired in series) & going through fusible link & through limit switch to control board. Igniter glows, runs for the stated 45 sec's for igniter warmup, then safety valve clicks but apparently no gas being released so shuts down after the prescribed 4 second time limit with no ignition happening.
When power applied to system, control board LED gives off 1long flash - does this signal a problem or is
It just advising that it is getting power and functioning? No codes listed on wiring schematic on door.
I have 28v going to the gas safety valve from the control (black wire) but the other, yellow, wire between
The control & the valve never shows any voltage, even during the 4 second attempt at ignition.
Should this wire ever show voltage or is it just a "neutral"? Can't tell by the wiring schematic.
The schematic says 24v for all low voltage circuits but I show 28v on my digital multi meter.
Problem?
Being I have all the req'd voltages going to the control from all pressure & other switches, &
Voltage going to the safety valve after the igniter warmup period, is maybe the safety valve bad
Again? It has been several years since I replaced that. I have a used spare I will try next.
This seems to happen every winter early in the heating season. This year I've checked everything
And can't find a problem other than gas not being released by the safety valve. Tried tapping on it
During the 4 second time it is supposed to release gas to the burner, no effect.
Appreciate any help!
Have had problems in the past with partly blocked combustion air intakes or exhaust outlets, with
Blocked pressure sensor tubes at inducer fan, with slow inducer fan, with water drain blocked,
With bad igniter, bad limit switch, and bad gas safety valve.
Have corrected all (new safety valve, new limit switch, new inducer fan, new control board, new igniter within last couple years, all seem to be working, also new blower motor) and checked all intake & exhaust & drains & sensor tubes which are not blocked at this time. Have 28v coming off last pressure sensor switch (3 wired in series) & going through fusible link & through limit switch to control board. Igniter glows, runs for the stated 45 sec's for igniter warmup, then safety valve clicks but apparently no gas being released so shuts down after the prescribed 4 second time limit with no ignition happening.
When power applied to system, control board LED gives off 1long flash - does this signal a problem or is
It just advising that it is getting power and functioning? No codes listed on wiring schematic on door.
I have 28v going to the gas safety valve from the control (black wire) but the other, yellow, wire between
The control & the valve never shows any voltage, even during the 4 second attempt at ignition.
Should this wire ever show voltage or is it just a "neutral"? Can't tell by the wiring schematic.
The schematic says 24v for all low voltage circuits but I show 28v on my digital multi meter.
Problem?
Being I have all the req'd voltages going to the control from all pressure & other switches, &
Voltage going to the safety valve after the igniter warmup period, is maybe the safety valve bad
Again? It has been several years since I replaced that. I have a used spare I will try next.
This seems to happen every winter early in the heating season. This year I've checked everything
And can't find a problem other than gas not being released by the safety valve. Tried tapping on it
During the 4 second time it is supposed to release gas to the burner, no effect.
Appreciate any help!