If I add a 100 amp disconnect between my service entrance and my new 100 amp panel does the disconnect need to be fused?

tkrussell
Nov 12, 2010, 12:04 PM
Based on typical installations, and little details, I will say yes.

ma0641
Nov 12, 2010, 03:27 PM
All new installations, at least in Georgia, require a service disconnect outside the house, usually in the meter box. This way, emergency personnel can turn the power off without going inside i.e. fire. There should be a 100 Amp breaker in the disconnect.

Missouri Bound
Nov 12, 2010, 08:29 PM
May I ask why you are doing this? The main breaker serves as the disconnect. Are you moving the panel away from the service entrance?

donf
Nov 13, 2010, 04:22 PM
Not to waste any one's time, but if you install a main disconnect switch, the grounding system is affected and the panel would now require a four conductor feed and the removal of the main bonding jumper inside the panel.