View Full Version : Furnace ignites but fan won't come on. Burner stays lit making furnace HOT.


eudaemonic
Oct 3, 2010, 01:18 AM

Baltar
Oct 3, 2010, 11:19 AM
Does the motor get hot? Try spinning it by hand, if it is seized up then you need a new one. Otherwise you have to check for power going to the motor. If none then you have to find out why.

eudaemonic
Oct 4, 2010, 04:27 AM
Thanks for your fast reply, Baltar!

I've had some time to learn and troubleshoot, so now my question has changed.

I've tested the fan, fan switch, upper & lower switches and they test good. (I tested with a lighter and a continuity meter)

My pilot lights and stays lit, when I turn up the thermostat the burner lights.

The fire coming from the burner is not as big as I remember - nor does it make as loud of a "whoosh" sound - and its yellow flame. Isn't it supposed to be a blue flame? I'm thinking that it's not getting hot enough to trip the fan & lower limit switch.

eudaemonic
Oct 4, 2010, 08:20 AM
Wow! I fixed it!

I figured the air/fuel mix was off, so I checked the air return, but it was free from obstruction. Then I finally got the nerve to take the regulator out to see if the burner tube was obstructed, but it was fine as well. I almost gave up and called a professional, but then on a whim I took a toothpick and stuck it in the regulators opening that the gas comes out of to flow through the burner. I fished out a spider nest! Now the flame is huge and blue and I'm already warm!

I have a fear of gas lines - when I was a child I was close by when a building exploded from a gas leak. This is a personal triumph, my wife can be proud!