Aug 20, 2010, 11:49 AM
Here's the deal, so before you tell me that it HAS to be a dedicated circuit, please read on...

We're changing the kitchen flooring from vinyl tiles to ceramic. We'd like to install some Warm Wire - to cover @ 100 square feet - here's the detail on the Warm Wire directly from the SunTouch website

100 sq ft area
470 total wire needed (@ 2.5" OC)
Amp draw = 10.0
Resistance = 9-12 ohms

I've got existing 20 Amp circuits in the kitchen - one with the refrigerator (6.5 Amps) and one other plug (2 outlets) - that's it on that circuit. A frig is not "continuous" power, and the Warm Wire wouldn't be continuous power either.

Can I make this work?

Ideas, thoughts, etc. - Thanks!

Kendal

KISS
Aug 20, 2010, 12:11 PM
OK, I won't. But I will tell you that space heating loads must be sized at 1.25 their rating. So the 10 A becomes 12.5A and 6.5+12.5 = 19A leaveing no wiggle room for even the motor on the fridge to start.

The heating load should be a 15 A circuit. 12.5A sized up to nearest breaker.

kcsmith1958
Aug 20, 2010, 12:28 PM
Oooo - oh bummer. I thought I might be able to get by with neither of them being a continuous power appliance.

I don't think I have any room to add a breaker. I can check to see if any of the wiring will support upgrading from 20 Amp to 30 Amp - requires 10 gauge wire correct?

Kendal

Stratmando
Aug 20, 2010, 12:59 PM
#12 is fine, you may be able to use one of these, do you have conduit or a way to get to the Panel?
piggyback breaker - Google Product Search (http://www.google.com/products?q=piggyback+breaker&rls=com.microsoft:en-us:IE-SearchBox&oe=&rlz=1I7ADFA_en&um=1&ie=UTF-8&ei=JN5uTO2BAsKC8gbqyOzxDg&sa=X&oi=product_result_group&ct=image&resnum=17&ved=0CIUBEMwDMBA)

kcsmith1958
Aug 20, 2010, 01:19 PM
I can get to the breaker panel no problem - no conduit, all the wires are in/thru the floor joists - so with one of these dudes, I can fit two breakers in the space of one?. running new wires, I assume?

Kendal

KISS
Aug 20, 2010, 01:49 PM
Yep. You can buy twins in 15/15, 15/20 and 20/20 Amp.

kcsmith1958
Aug 20, 2010, 01:55 PM
After a bit of research, I think I'll have to go into the sub-panel that's already installed. The main panel is all 1/2" breakers, it's a GE main panel - from what I've read, there are no such animals as piggyback 1/2" breakers in any amperage.

But, the sub panel does have a couple open 15 amp 1" breakers in it that I can get to.

With the Warm Wire install I've got coming up - 10 Amp draw - sized to 12.5 A from the previous post - I could tap one of those 15 A breakers with the piggyback breaker, run new 14 gauge wire to the Warm Wire thermostat and I'll be all set - Yes? Or do I have to go to one of the 20s and use the 12 gauge wire?

Kendal

KISS
Aug 20, 2010, 02:00 PM
15 A, 14 AWG is fine.

tkrussell
Aug 20, 2010, 02:02 PM
The heat circuit needs to be all #12 copper wire on a 20 amp breaker.

KISS
Aug 20, 2010, 02:13 PM
tk:

Why? The circuit draws 10 Amps?

100 sq ft area
470 total wire needed (@ 2.5" OC)
Amp draw = 10.0
Resistance = 9-12 ohms

kcsmith1958
Aug 20, 2010, 02:25 PM
There is one 20 Amp breaker in the sub panel that I can get to and install a 20/20 piggyback.

Sounds like as long as I can get the wire run from the wall upstairs in the kitchen to the basement and across the 40' run to get to the sub-panel / breaker box, I'm all set.

Got any tips on running that 12 gauge wire down through the floor and into the furnace area where it will come out? Oh yeah, the kitchen is completely wallpapered, I will have the baseboards off to install the tile floor. And I won't have much room in the basement where the wire will be - then it has to make a 90 degree turn and make the 35' run across the width of the basement to the panel.

I'm going to guess that I should have it make the really long run first and pull it over into the furnace area (unfinished) and go up into the kitchen that way - as the 12 gauge wire won't be easy to work with on that long run across... Yes?

BTW - thanks for all the help on this, you guys are awesome.

Kendal

Stratmando
Aug 20, 2010, 03:23 PM
Romex should not be too bad.
If the Kitchen has conduits to the panel, I would fish through there.
When I need additional wire ran in an existing conduit, I attach my new wires to one of the old wires, and attach another wire of the one I am removing.
Ground should already be run.

KISS
Aug 20, 2010, 04:16 PM
Yep, big steerable, 4' or longer, drill bits. Available at Home Depot. Steering wheel is separate. They also contain an eye for fishing a pull wire back.

tkrussell
Aug 21, 2010, 03:04 AM
Kiss, I had a dumb moment, and I doubled up. I realized it once I hit the send button.

Your right, and I was wrong.

#14 on a 15 amp CB is fine.