I have a Goodman 4 ton HP CPJ60-1. Outside unit was coming on but the inside blower motor did not come on. Now the outside unit does not come on at all in either mode.
Where should I look?

NorthernHeat
Dec 5, 2006, 01:57 PM
Check breakers, check for 24 volts to the control board at Y and common

DaBears
Dec 5, 2006, 02:28 PM
I have a Goodman 4 ton HP CPJ60-1. Outside unit was coming on but the inside blower motor did not come on. Now the outside unit does not come on at all in either mode.
Where should I look?
Breakers are fine, I'll have to check for volts at the control board. Inside blower motor hums but doesn't start, cage spins freely.

DaBears
Dec 5, 2006, 02:29 PM
If the inside blower was not running is their something that would trip the outside unit because of this?

NorthernHeat
Dec 5, 2006, 02:47 PM
No there isn't. I'm curious why the indoor blower isn't running though, maybe a bad capacitor. Does the motor get really hot?

DaBears
Dec 5, 2006, 02:50 PM
Yes, motor gets very warm and stops humming, I will replace the capacitor. Still puzzled on why the outside stopped running

NorthernHeat
Dec 5, 2006, 02:54 PM
Yes it sounds like the motor or capacitor are bad, thermal protector finally opens and turns it off when it gets to hot.

seve tec
Feb 21, 2010, 11:22 AM
The out side stops because of the high limit pressure cut off switch, located on the high pressure side, if the indoor blower motor stops your high pressure will rise to the point the high limit switch switch cuts off the out sided unit. Be thankful for this or your compress will over heat and cost you big bucks!!