View Full Version : Carrier 58gp blower will run then off then on for 2 seconds
sseager
Dec 1, 2009, 10:13 AM
Cycles through fine then blower powers off then back on for 2 seconds then back off?
sseager
Dec 1, 2009, 10:20 AM
Fan blower switch?
hvac1000
Dec 1, 2009, 01:04 PM
It is possible the blower fan control is the problem. The furnace residual heat is reactivating the blower more than likely.
sseager
Dec 4, 2009, 09:45 AM
Thank you hvac1000 - all seeing eye.
Question, if I replace the circuit board would that fix the problem. i.e. "blower fan control" located on the circuit board?
PS I have an a extra board on site.
hvac1000
Dec 4, 2009, 10:26 AM
Keep a copy for your use.
http://www.xpedio.carrier.com/idc/groups/public/documents/techlit/58gp,gs-2si.pdf
I see no specific fan temperature sensing control on this unit so it must be controlled off the board.
sseager
Dec 6, 2009, 02:27 PM
I have 2 of these Carrier units in my house one up and one down stairs.
I switched the limit switch located in the baffles that senses the temp of the baffles from the one that was working properly with the one that was not. Result same problem - blower on off on off on then finally off.
Replaced circuit board and it fixed the problem.
Thank you again hvac1000 for your time and interest in my problem.
You can do it we can help...
hvac1000
Dec 6, 2009, 04:01 PM
Glad you got it going.