Log in

View Full Version : Furnace takes 4 hours to increase heat 10 degrees. Is this normal?


bradpeterson
Nov 28, 2009, 07:24 PM
This September, we had a furnace installed to heat the basement. It's an Armstrong, two-speed, 95% efficiency unit. The specs say it can do 57,000 BTU/hr, and my basement is 1350 sq ft.

Yesterday was a cold day, so I had my first chance to try it out. The temp in the basement was 61 degrees. It took 4 hours for the furnace to heat it up to 71 degrees.

This doesn't seem right to me. I've never seen a furnace take this long. I called the furnace company, and they said the time doesn't matter, just so long as it can eventually get there and *hold* the 71 degrees. But that doesn't seem right either, because my furnace must be creating 57000 BTUs an hour as it's going full speed, which means I'm not efficiently heating my basement.

What do you guys think on this?

KISS
Nov 28, 2009, 08:18 PM
How about a link to the manual and model #.

Ok, so it's two speed or two stage?

It could be stuck in low fire mode or it may not have a two stage thermostat installed. Sometimes a furnace control bump things to two stage with a single stage stat.

In any event, I would probably expect it to either start in high speed because of the temperature difference if the thermostat was doing the controlling.

If the furnace board was staging, then I might expect around 30 min of low speed/low fire and switch to high fire.

How many W terminals are connected to the furnace? W, W,W1 or W/W2

bradpeterson
Nov 28, 2009, 09:14 PM
Thanks for the reply. Sorry for not having the full details, I'm just a lowly homeowner learning about this stuff for the first time. :)

It's an Armstrong G2D95CC060V14B. Info on it here: http://www.armstrongair.com/pdfs/ag2d95-100.pdf and http://www.armstrongair.com/pdfs/506244-01.pdf. It's a two stage furnace (not speed).

Based on what I've seen, it starts at the first stage for a few minutes with slow airflow. Then it kicks into the second stage and really blows out air and stays there for hours until it gets to the target temp. Only other info I know is that the thermostat is connected to the furnace with a 2 strand wire, not a 5 strand wire.

I'll research and figure out how many W terminals are connected to the furnace if it's needed.

bradpeterson
Nov 28, 2009, 09:31 PM
Yep, two strand wire. Only W1 is connected.

KISS
Nov 28, 2009, 09:45 PM
I'll try to look at the manual, but hopefully there is an observation window. The flame should get bigger when the blower goes to high speed. The air temp should be hotter too.

KISS
Nov 28, 2009, 10:08 PM
Can't seem to find an install guide. Usually the contractor should leave you one.

hvac1000
Nov 29, 2009, 02:25 AM
Since you just purchased that unit and it is still under warranty I suggest you call the company back and tell them you want someone to wire it correctly so both stages kick in. There are many different ways that furnace companys have to activate the second stage. Some need an additional wire from the thermostat for the second stage and some brands have a circuit board setup that works on a timed/temperature function so when the first stage is running if it will not bring the temperature up quick enough it will automatically kick in the second stage. Goodman brand has this feature on some of there units. This way if you do not mess with it they cannot say you violated the warranty since some HVAC companys will violate the warranty if they can tell you changed something or tried to make an adjustment.

A basement which is not hard to heat to start with at 1350 sq ft should have no problem with a 57,000 BTU unit.

Joshdta
Nov 29, 2009, 08:45 AM
Seems to me it is working. If the fan kicks from low to high then it must be controlled from the 2 stage switch on the control board. Is this basement fully finished? Or is it all block and concrete? If it is not finished it will take a long time to heat up. If it is a finished space why was the stat set so low to begin with?

KISS
Nov 29, 2009, 09:54 AM
What you might want to do, is take a reading of the gas meter at full fire and one 30 min to an hour later with the furnace in high fire mode.

Use the conversion of 1028 BTU/cubic ft and see if the BTU/hr is not way off.

hvac1000
Nov 29, 2009, 10:16 AM
A four hour burn at 57,000 btu's per hour gives a total gross available heat gain of 228,000 btu's during the four hours. With a 10 degree temp gain on 1,350 sq ft in a basement setting it should do that gain in a lot less time. I cannot believe the second stage is working or it is being delayed for way to long of a time. Divide the total btu's by the square feet and see what you get. It is a big number per sq ft.

Joshdta
Nov 29, 2009, 10:39 AM
This may not be a furnace problem at all? Was all new duct installed when this unit was put in? It may be a airflow, or registar problem! Or lack there of.

bradpeterson
Nov 29, 2009, 10:41 AM
Thanks all. I'll be doing some meter tests later today, grabbing lots of data along the way. Luckily I have an upstairs floor furnace of very similar characteristics (and the floor layout is almost exactly the same too). I'll run the same test against the upstairs furnace, so I can compare how much gas it uses to heat t Just to answer some quick questions:

1) The basement is finished. However, it's an older block house. Half the walls have great insulation (I just put that in), the other half has poor insulation, using R-7 (I didn't even know they made that!)

2) I looked at the manual, and it seemed to indicate for it to get to a second stage, it needs the W2 wire, and the thermostat controls it. A picture also seems to show that several speeds will be reached as it climbs to the second stage.

3) The reason we let the basement get so cold is that we don't live down there. I'm currently renovating it. It was recently that I was down there working that I got cold and decided to try out the new furnace.

Joshdta
Nov 29, 2009, 10:43 AM
How many supplys and how many returns do you have down there?

bradpeterson
Nov 29, 2009, 10:45 AM
This may not be a furnace problem at all? Was all new duct installed when this unit was put in? It may be a airflow, or registar problem! Or lack there of.

You know, this may be the issue.

The device is counterflow, so the ducts run under the slab. I know some vents seem to blow out slightly warm air, but a few don't seem to be of normal warmth. (One vent even blows cold air, so I blocked that off). I do know though that there is plenty of room through those ducts, and all vents really kick out air fast.

bradpeterson
Nov 29, 2009, 10:47 AM
How many supplys and how many returns do you have down there?

6 supplies (there are 4 rooms, the two larger rooms get two supplies). There is one return, it's on a wall adjacent to the furnace. (It's a very large return, and it's positioned about 10 feet from the thermostat.)

Joshdta
Nov 29, 2009, 10:53 AM
Your ducts are under the concrete? Were the insulated? I would think for 1300 sf you would need at least 8 to 10 6'' supplys, inless the supplys you have are large.

KISS
Nov 29, 2009, 10:54 AM
There is also the possibility as not enough gas flow. i.e. pipes not sized properly

The heaters are the most energy consumables in the house and you have to plan for two in the piping design.

So, consumption verification would indicate that there is a problem. It doesn't say where.

bradpeterson
Nov 29, 2009, 11:17 AM
your ducts are under the concrete? were the insulated? I would think for 1300 sf you would need at least 8 to 10 6'' supplys, inless the supplys you have are large.

I know that right before we put the furnace in, I saw a pit with three 4 inch metal pipes heading out towards the rooms.

At the supply ends, it almost looks like the ducts are a trough, a foot deep and about 4 inches wide. The ducts appear to just traverse the perimeter of the foundation. There is no insulation in the duct work. In fact, the walls of these ducts are just pure concrete. (Again, it's an older home).

KISS
Nov 29, 2009, 11:52 AM
So, you could be heating the slab. Nonetheless, the contractor probably goofed.

Joshdta
Nov 29, 2009, 02:57 PM
Given the fact that your ductwork is concrete, I would jumper your furnace so it runs on high fire all the time. As you are heating the concrete thus not getting the temp out of the registars, expecally on low heat.

bradpeterson
Nov 29, 2009, 10:05 PM
Ok, I just ran a bunch of tests. Because I'll need to explain what I found to the furnace people as well, I put it all in chart form. (Plus, my job has me analyzing stuff all the time, so this is a bit normal for me to do.)

http://img163.imageshack.us/img163/290/furnance.png

To measure gas flow rates, I went outside and watched my meter. The quarter foot needle spun fast, so I watched it spin and timed it for 1 minute. On my power bill, it gives a direct ratio for BTU per cubit feet. Here in Utah, we have high quality natural gas, so it's 909 BTU per ft^3.

For what I saw, the downstairs furnace appears to be stuck in the first stage. But it is definitely consuming natural gas at a decent rate. The upstairs furnace seemed to go a bit beyond what it says it should burn in BTUs for stage two.

I'll have to try forcing the downstairs furnace to run on high fire. But I'll need the furnace people to work with me on that (I can't void any warranties.) Overall though, it seems that I'm losing a lot of heat into the slab.

The upstairs furnace heated quickly. So quickly, it didn't appear to radiate into the walls and furniture. I just had hot air.

I turned off the thermostat, and let the room stabilize back down to around 74. Comparing the BTUs used, it seems the downstairs furnace needed to use about twice as much gas as the upstairs furnace to heat a floor. Ugh.

KISS
Nov 29, 2009, 11:07 PM
Based oon your spec, the first stage is 42 K BTU/hr and it looks like your right on the money.

Which means, the second stage isn't kicking in. Because you should have measured 60K BTU/hr.

Not sure what you mean by vent temperature range. Does this mean discharge temp measured at about the same time? If it does mean that, then your heating the slab.

20/20 Hindsight says the ducts should have been insulated.

Job well done: Furnace is NOT running in the second stage (or it doesn't have enough gas supply. Doubt the latter.)

I'm not too happy with the contractor who doesn't know how to hook up a second stage.

The R value of concrete is not good at all: R-value (insulation) - Wikipedia, the free encyclopedia (http://en.wikipedia.org/wiki/R-value_%28insulation%29)

It's interesting what these guys recommend for ducts in concrete. 1/4" thick. http://www.bart.gov/docs/STD_SPEC/BFS/BFS_2_0_Spec/STDSPEC/23%2031%2000.pdf

Section 4.5.2 Guide for Concrete Floor and Slab ... - Google Books (http://books.google.com/books?id=HdL2h0vBMUkC&pg=PT20&lpg=PT20&dq=embedding+hvac+ducts+in+concrete+insulation&source=bl&ots=JHoIr9rhrJ&sig=yOwHJ2uxHUNsITiph0D0t9HBrXU&hl=en&ei=El8TS9icGI_hlAfm67ybBA&sa=X&oi=book_result&ct=result&resnum=6&ved=0CCAQ6AEwBQ#v=onepage&q=&f=false)

reccomends watertight joints and sand.

Not a whole lot of difference in thermal conductivity. Thermal Conductivity of some common Materials (http://www.engineeringtoolbox.com/thermal-conductivity-d_429.html)

bradpeterson
Nov 29, 2009, 11:37 PM
Thanks for the comments.

When I talked about temperature range of the vents, I was summarizing the temperatures I was seeing coming out of the 6 vents in the basement.

When temperatures peaked, one vent was giving out 113 degree air, the next as 107 degree air, the next vent was at 67 degrees, then 83, then 99, and the last vent was 95 degrees. So the range was from 113 to 67 degrees.

What I'm gathering is that air is leaving the furnace at least at 113 degrees (the hottest vent had that temp). By the time it travels to the vents, it cools significantly. One vent cools all the way down to 67 degrees! My guess on the path is that the cement duct is perhaps only 30-40 feet from source to destination. Wow, valuable lesson why ducts should be insulated.

I just realized a better test I could have ran. I'm worried about the variables of heat loss, and variable of the entire floor capturing and holding heat (solid objects and air). For example, the basement has lost about 7 degrees in 5 hours time. It may just be that the basement furnace very slowly heats the downstairs, and during this time, heat is radiated outside while the furnace kicks new heat into the floor. But overall, it uses BTUs efficiently.

So to factor in heat loss, I should give the experiment a total time to run, say, 8 hours. I should increase the temperature of a floor 10 degrees and maintain that temperature until the 8 hours is up. Then do the same for the upper floor, maintaining the temp increase for the same total amount of time. I might just find out that the downstairs furnace is up to the task. My only problem is that the gas meter doesn't have a good way of measuring cubic foot usage for a several hour time span. It tends to only work well for a month. Maybe my furnace company has some gauge that would help me figure this out...

KISS
Nov 30, 2009, 07:35 AM
Remember, that the furnace typically has a heat rise, somewhat modified by relative humidity. It will raise the temp of the air coming in by x degrees.

I have my doubts that insulating ducts in cement would really help. The themal conductivity isn't that great for cement . The long run probably has more of an influence.

For temperature uiformity, you may have to resort to zoning with register or duct dampers. For fun, you could get thermostats that can be adjusted everywhere.

The 30% difference between high and low fire will knock off 30% of the time to raise it 10 degrees.

7 degrees in 5 hours probably means the furnace is going to be running more. If it's running more with the duct variation, then temperature uniformity may be really bad.

A 67 degree discharge temp isn't going to heat air very well.

The furnaces ability to maintain the space, is going to depend largely on the surrounding temperatures, BUT the ground is fairly uniform. You might have some direct exposure to the outside.

You have a lot of area in the ductwort, but the thermal conductivity isn't great, but 3 ducts in parallel is probably worse than a single duct. Heat Loss Through Enclosure Walls Equations and Calculations - Engineers Edge (http://www.engineersedge.com/heat_transfer/heat-loss-container-calcs.htm)

Calculating Heat Loss - Features - Process Heating (http://www.process-heating.com/Articles/Feature_Article/f8fa6b7710d19010VgnVCM100000f932a8c0____)

Do you know what the ducts are surrounded in and how thick they are?

You need to look at steady state performance once you get the high fire thing to work. i.e room temperature variation after say 24 hours.

bradpeterson
Dec 16, 2009, 03:28 PM
Just an update (in case people run into this thread months down the road and wanted to see the result). We've had the furnace folks over a few times. Here's what we've found:

* All tests showed the furnace is working as it should, our vents beneath the slab are just dumb.
* Forcing the furnace into the second stage helped very little. It decreased the time from about 5 hours to 3.5 hours to heat the room up 10 degrees.
* We also tried slowing down the air to its maximum, thus making the air hotter. But that only made the air slightly hotter. It still took over 3 hours to heat the room up. That one cold supply never got above 70 degrees (meaning, we were losing over 60 degrees to travel from the furnace to the supply!)

So, our furnace is useless. Their warranty doesn't cover bad vents. And our slab can't be ripped up and fixed. We tried to salvage the counterflow furnace by lifting the furnace up, and then running the air back up into the ceiling. But there's no room anywhere for these extra vents. So our solution is:

* I'm going to tap into the upstairs furnace vents, so we have one furnace for the whole house.
* I'm going to spend my Christmas vacation time running supplies and cold air returns to every room in the basement. We'll have to sheetrock, mud, tape, and repaint everything when we're done.
* They're going to try and sell our counterflow furnace for us. We paid about $2900 for it. We'll probably have to sell it for $1200 to make it competitive with the 80%. But it may take months to sell it, as counterflows aren't common. They're looking to see if it can be turned on it's side, and if so, it should be an easier sell.

So if any of you want a brand new counterflow furnace, let me know :P

hvac1000
Dec 16, 2009, 04:06 PM
What a mess. You might be able to install some electric baseboard heaters easier.
Will your other furnace you are going to tap have the heat capacity and the blower capacity to run the entire show? Think before you act!!

bradpeterson
Dec 16, 2009, 04:47 PM
They did some calculations, two people said it would be OK.

I wouldn't mind a double check. The main furnace kicks into its second stage about 5 minutes in, and is rated to burn at 92,000 BTU (but from what I measured on the gas meter, it seemed to go up to 100,000 BTU). The entire sq ft will now be 2600 off that one furnace.

The main trunk line heading towards the east of the house will feed 10 supplies total (into the 4 bedrooms and 2 bathrooms). I hope a trunkline can handle that.

KISS
Dec 16, 2009, 05:09 PM
Brad:

Sorry your "professional installation" wet very bad. You seemed to tried to have it all together. As HVAC1000 has said in the past, the equipment is only as good as the installation.

Thank you for the feedback.

Manual D, Manual J

PS: I fixed a typo in post #25 for you: You had said increased the time. 5 to 3.5 is a decrease.

bradpeterson
Dec 19, 2009, 10:19 PM
Sorry to keep bothering you all, but this forum keeps coming back as the most helpful place I find :)

I want to force the company to give me all my money back. But I think I might need some good documentation.

I had another furnace company over to give me their opinion. He pointed out something I hadn't considered. The CFM on my supply ducts are terribly inadequate for what the furnace needs. If I'm running three 4 or 5 inch ducts for my supply ducts, then that's only rated for about roughly 150 CFM. But my furnace is now jumpered to run at 1000 CFM most of the time!

Therefore, the installation was bad. It's like they're trying to drive a semi under a 4 foot tall bridge. The installer should have instantly seen that supply lines are totally inadequate, and not installed the furnace it in the first place. I shouldn't have to pay for the labor, and I shouldn't have to pay for a furnace I can't use.

Now what I'm looking for is some kind of official manual that backs me up. Something that a small claims court would agree is authoritative. My furnace manual does say it burns 650 CFM on low fire an 1000 CFM on hire fire. But it doesn't mention a thing on how big the supply ducts should be.

So here's where I'm picking your brains. What's the best way for me to make the case that three small duct lines are so inadequate that the installer/company failed in their job? Are there city codes, or state regulations, or government websites that explain it? I'm in the dark here on this one...

hvac1000
Dec 19, 2009, 10:51 PM
I would first check with your local building department. I am sure the furnace company took out a permit.

Use your local rules/codes whenever possible since they are already approved by the powers to be.

On a furnace install the codes usually say to follow the manufactures install instructions for enforcement but on duct install it is usually a code like the CABO code or the states mechanical code.

A citys and states might use a different code or year of issue code book since the codes are on 3 year cycles and many jurisdictions do not adopt a code cycle right away.

KISS
Dec 19, 2009, 11:07 PM
Some stuff to munch on: Procedures For HVAC System Design and Installation (http://www.energy.ca.gov/efficiency/qualityhomes/procedures.html)

Energy Savers: Sizing Heating and Cooling Systems (http://www.energysavers.gov/your_home/space_heating_cooling/index.cfm/mytopic=12340)

WarmAir.net - Duct Design and Dynamics (http://www.warmair.net/html/duct_dynamics.htm)

So, actually what this all means is that there are two calculations needed to adequately do duct design.

One is called MANUAL J. This basically determines the heat loss for the space(s).

The other is called MANUAL D. This is the reference for doing the duct design. Manual J must be performed first.

The right company would have software to do the Manual D and Manual J calculations and it would not take long to do.

These guys: HVAC Software, HVAC-Calc for Heat Loss, Heat Load Calculations (http://www.hvaccomputer.com/) Have a homeowner version of manual J for about $50

Having the results done by a PE (Professional Engineer) and possibly paying him to be an expert witness, then you probably have the cat in the bag.

Here is an example of the software:

Wrightsoft: HVAC Software - Product Overview (http://www.wrightsoft.com/products/product_overview.aspx)

As an idea, call the software mfr and ask if there is anyone using their software near you and use it as a starting point.

I would agree, that it does seem a bit too small and I'll bet that the static pressure is too high too.