Have a new Goodman furnace that has a peculiar issue. The furnace will heat just fine and burners will shut off normally when set point is reached. After the burners have shut down, the blower will run for a minute or so then it seems as though it is given a signal to stop then immediately restart. The blower never stops turning and it wold be best described as someone turning off a light switch and turning it right back on again. After another minute or so the system shuts down as it should. What could be causing this electrical "bump" with the blower motor?
Thanks,
Mike Waters
Lynnwood, WA
hvac1000
Dec 23, 2008, 02:25 PM
A out of range fan and limit control allowing the residual heat left in the heat exchanger to reactivate the blower for a short time.
KC13
Dec 23, 2008, 02:28 PM
How new is it? Installer warranty may still be in effect, and poking around may compromise coverage. A call to your installer may be your best next move.
mwatersjr
Dec 23, 2008, 02:35 PM
Father-in-law and his ex-heating contractor friend were installers. Got furnace cheap (but new), so no warranty.
KC13
Dec 23, 2008, 02:36 PM
Okay then... check the status LED for fault code display while this is occurring.
mwatersjr
Dec 23, 2008, 02:45 PM
I just timed the event and it occurs exactly 30 seconds after main burner shutdown. The blower continues to run for another 2 minutes then shuts down until next heating cycle.
I see an LED light that is currently illuminated while the furnace is off. I will count the blinks of this LED the next time the furnace kicks on. Shouldn't be long since it is 30 degrees outside.
mwatersjr
Dec 23, 2008, 03:17 PM
In looking at the Emerson control board, while waiting for the system to come on naturally, I saw a button labeled "Fault Recall". Pushing it gave me two sets of 4 blinks. The fault code legend on the furnace panel for 4 blinks indicates that this is an "Open High Limit" condition. Now what?
mwatersjr
Dec 23, 2008, 04:00 PM
The system had come on now and run through its cycle. As expected, after 30 seconds a series of fast clicks was heard at the control board and the blower power seemed to be shut off then turned back on within a fraction of a second. NO fault codes were shown by the LED on the control board during this heating cycle. I have made sure there are no restrictions in either the intake or room air side of the furnace.
hvac1000
Dec 23, 2008, 04:30 PM
Loose or improper ground. Loose connection. Bad or defective control board. Bad sensor feeding control board. Those are my guesses since nothing has shown elsewhere.
mwatersjr
Dec 23, 2008, 04:59 PM
Any change in diagnosis if I said this was on a 3-month old furnace?
mwatersjr
Dec 23, 2008, 05:01 PM
What sensor could be feeding the control board a bad signal?
hvac1000
Dec 23, 2008, 05:07 PM
NO since all those items would have to be tested or replaced to find the problem.
MarkwithaK
Dec 23, 2008, 06:49 PM
Was the furnace size correctly for your duct work?
mwatersjr
Dec 23, 2008, 07:21 PM
I assume it was. The unit didn't start doing this. It took several weeks. I have a tech scheduled to come look at it next Friday.
Missouri Bound
Dec 23, 2008, 08:23 PM
Has this happened from day 1? Get the "installers" back and have them do it right. Relatives or not, cheap or not, it needs to be made right. And are you sure that Goodman won't warranty this item? Goodman sells through distributors to the public and a warranty is there for a reason. Check around online, do some research before you give up.
MarkwithaK
Dec 23, 2008, 08:26 PM
I assume it was. The unit didn't start out doing this. It took several weeks.
Assume? What makes you assume that the proper calculations were done? Judging by this comment:
Father-in-law and his ex-heating contractor friend were installers. Got furnace cheap (but new), so no warranty.
I would make sure of it. I understand the lure of saving money on labor costs but by doing it the shade tree method you are asking for potentially expensive issues down the road that will more than negate the money you saved on labor and losing that warranty doesn't help either.
Missouri Bound
Dec 23, 2008, 08:29 PM
Back to the warranty issue. Goodman will warranty all equipment if you install it yourself IF... you have the equipment checked out by a licensed professional. Your "tech" may be the one to validate the warranty.
MarkwithaK
Dec 23, 2008, 08:38 PM
Back to the warranty issue. Goodman will warranty all equipment if you install it yourself IF....you have the equipment checked out by a licensed professional. Your "tech" may be the one to validate the warranty.
While I do believe that the warranty will stand if checked out by a qualified tech, If it is improperly sized you're SOL, likewise with the duct work.
mwatersjr
Dec 23, 2008, 08:47 PM
Like I said in a previous post, It took several weeks of use before this showed up. The furnace was replacing an older gas furnace of similar size, CFM output. The tech may be able to check a warranty for it.
mwatersjr
Jan 3, 2009, 02:42 PM
Tech came out and scratched his head.. Said he hasn't ever seen a furnace do this in 20 years... Have opened the filter compartment, pulled the filter and let it runs once or twice unencumbered by any possible return air restrictions... same result. I found that I do have the warranty - even registered it with Goodman - Lifetime heat exchanger and 10 yrs parts. I am going to see about getting the control board checked/replaced.
greghvacguy
Jan 3, 2009, 03:07 PM
Make sure you have good ground.
mwatersjr
Jan 3, 2009, 05:55 PM
Just ran a separate ground to the unit and it still does it.
wmproop
Jan 3, 2009, 09:07 PM
Its 10 days later,, I hope its fixed by now, if not someone had a cold Christmas
KC13
Jan 3, 2009, 09:14 PM
Try this: disconnect and insulate the wire connected to "G" on the circuit board (probably green). If problem stops, look to thermostat.
mwatersjr
Jan 3, 2009, 09:22 PM
KC13 - I will try that next.
WMproop - Furnace works fine except for this weird electrical anomaly. Christmas was toasty warm in the house.
mwatersjr
Jan 3, 2009, 10:48 PM
With "G" wire disconnected, issue still persists. The "G" wire is for the manual blower "on" signal from thermostat.
KC13
Jan 3, 2009, 11:18 PM
You are correct, and you have eliminated one more possibility.
wmproop
Jan 3, 2009, 11:30 PM
Have a new Goodman furnace that has a peculiar issue. The furnace will heat just fine and burners will shut off normally when set point is reached. After the burners have shut down, the blower will run for a minute or so then it seems as though it is given a signal to stop then immediately restart. The blower never stops turning and it wold be best described as someone turning off a light switch and turning it right back on again. After another minute or so the system shuts down as it should. What could be causing this electrical "bump" with the blower motor?
Thanks,
Mike Waters
Lynnwood, WA
If its new, can`t the installer help you to make things right?
mwatersjr
Jan 4, 2009, 09:56 AM
if its new,,can`t the installer help you to make things right?
He is helping, but he is retired from the heating business and got me the furnace from the person who bought his business. He installed it for free and it cost me next to nothing. He is checking on Monday with his former business to see if they have seen anything like this with a Goodman. The tech I had come out to diagnose it said he had never seen this in 20 years.
hvac1000
Jan 4, 2009, 10:27 AM
Exact model number of furnace?
Exact brand and model of thermostat?
mwatersjr
Jan 4, 2009, 01:50 PM
Model: Goodman GDH80904BXAC
Thermostat: LUX 1500
hvac1000
Jan 4, 2009, 02:28 PM
Now try this. Disconnect all the thermostat wires in the furnace. Label them or mark down exactly where they go. Now use a jumper (piece of wire) and jump the W and R terminals only. This should bring on the heat. Let it run till the blower comes on then disconnect the R and W wires while it is running. The blower should shut off and stay off after the residual heat is blown out if my theory is correct if not nothing was lost or gained. If it does work I will tell you where to place a resistor.
mwatersjr
Jan 4, 2009, 03:16 PM
Jumpered the R&W terminals like you said. Burners lit, then blower motor started. Removed jumper midstream and burners shut down. Exactly 30 seconds later, the "oddity" was once again heard. Blower continued to run for additional 2 minutes then shut down and stayed off. This has been the experience all along. Now, through this experiment, we have removed the thermostat all together from the equation as a possible bad component.
MarkwithaK
Jan 4, 2009, 03:50 PM
If it does work I will tell you where to place a resistor.
Voltage fluctuation in control circuit?
hvac1000
Jan 4, 2009, 07:15 PM
Is that a LUX CAG1500 series thermostat OR a TX1500E Or a Smart Temp TX1500? There is no LUX 1500! Accuracy counts! If so it is one stage but your furnace is two stage but factory setup to use a one stage thermostat. Not that it makes a difference since all the wires were disconnected but two stage is good.
For your future parts needs
http://igate.northernplumbing.com/partsbreakdowns/GoodmanMfg/GDH8.pdf
Notes:
CFM in chart is without fi lter(s). Filters do not ship with this furnace, but must be provided by the installer.
All furnaces ship as high-speed cooling and medium-speed heating. Installer must adjust blower cooling and heating speed as needed.
For most applications, about 400 CFM per ton when cooling is desirable.
INSTALLATION IS TO BE ADJUSTED TO OBTAIN TEMPERATURE RISE WITHIN THE RANGE SPECIFIED ON THE RATING PLATE.
The chart is for information only. For satisfactory operation, external static pressure should not exceed value shown on the rating plate.
The shaded area indicates ranges in excess of recommended maximum heating static pressure.
The dashed (----) areas indicate a temperature rise not recommended for this model.
The above chart is for furnaces installed at 0-2000 feet. At higher altitudes, a properly de-rated unit will have approximately the same temperature
Rise at a particular CFM, while ESP at the CFM will be lower.
Complete specs.
http://www.heatandcool.com/v/GOODMAN%20PRODUCTS/GMH80/GMHspecs.pdf
Warranty
http://www.heatandcool.com/v/GOODMAN%20PRODUCTS/GMH80/GMHwarr.pdf
This info provided so you can download to your computer for reference.
At this point I have to say that Goodman might have a problem with there new style circuit board that is causing the motor situation.
Contact by phone
Goodman Manufacturing Co.
2550 N.Loop W Ste. 400
Houston TX 77092
713-861-2500
Talk to Russ Charles or Kim Zachary just do not mention me since they are private contacts within the company and I want no part of this discussion if you know what I mean. LOL You do not know exactly who I am anyway so you could not tell them I said to call. LOL
Circuit board # 0130F00006S (javascript:showUrl("/GetPartPictureAction.do?partnumber=0130F00006S&modelid=28084&document=P-425", "part_19"))BOARD, IGNITION, HSI INTEGRATED, 2-STAGE
Or PCBBF109S
As in new numbers see link
http://www.waroosevelt.com/dealers/service_bulletins/SERVICE_BULLETINS/SF-020.pdf
Goodman needs to send me checks instead of free equipment to test. LOL
mwatersjr
Jan 4, 2009, 08:32 PM
The closest LUX I could find to what I have is the TX1500E. Mine looks an awful lot like it only the TX1500E looks newer, updated, but mine has the same buttons/switches on it. Mine literally only has printed on it the words - "Lux 1500".
Are we sure my furnace is a two-stage and is it functioning as a two-stage? Now for the really ignorant question... what's a two-stage furnace as opposed to a single-stage one? The documentation on the TX1500E says it is not for use on a two-stage device.
hvac1000
Jan 4, 2009, 09:01 PM
Your furnace is one of the newer type designs that is a two stage that is actually controlled by a one stage thermostat. When the furnace kicks on it operates on one stage then after a period of time/possible temperature pass it automatically switches to the second and final stage.
A singel stage unit burns at one rate all the time but a two stage does not and by using the first stage most of the time it helps to save energy by having less stack/flue loss based upon the first stage lower gas consumption rate. This was developed so heating contractors would not have to pull a new thermostat wire containing a extra wire for the second stage and also the original or a cheaper one stage thermostat could be used. A pretty nifty idea if I say so myself.
When you talk to Russ or Kim just tell them you have had a goodman service person check it out and it is still doing the motor thing. Then ask for there recommendations or advice so you can repete it to the service person. Unless they have some special posting on the factory site I could not find then I am going to guess it is circuit board time. OR if the retired HVAC guy or whoever calls them they can ask the same question but hopefully will sound more professional. They do not like to talk to homeowners that much.
Do not worry about the thermostat at this point since we know by the disconnection of wires it is not causing this problem.
mwatersjr
Jan 7, 2009, 09:08 PM
New furnace control board went in today and the problem did not go away. Will be calling Goodman soon to find out if this is really a design "feature". Ughh...
hvac1000
Jan 8, 2009, 12:32 AM
Your going to love the answer if they tell you it is normal. Good luck.
mwatersjr
Jan 19, 2009, 06:50 PM
Ok, the jury has come back with a verdict. After finally getting around to consulting Goodman directly the answer is... drum roll please...
It's normal! Tada!
The kind gentleman explained that the sound is from the relay switching the blower motor from high speed to a lower speed during the cool down period. I even created a video of it and posted it to Youtube. Here (http://www.youtube.com/watch?v=UnrZKHxR2aI) is the link if you are interested in hearing the sound.
Another weird thing which must be simply a matter of coincidence is that no matter when the furnace is started, and I mean no matter when, either automatically or manually by me, the main burners will always shut off when the second hand of my watch is at the quarter past the hour mark. It is most uncanny and I can't explain it even after dozens, yes dozens, of experiments trying the furnace at different times. You can see this happen in the video. Rod Serling must be involved somehow I'm convinced.
hvac1000
Jan 19, 2009, 07:45 PM
Link does not go to video. LOL
At least you now know its normal? LOL
mwatersjr
Jan 19, 2009, 07:56 PM
Try this link. http://www.youtube.com/watch?v=UnrZKHxR2aI
hvac1000
Jan 19, 2009, 07:59 PM
Hum. It says hope for a greener future. LOL something is not working.
hvac1000
Jan 19, 2009, 08:01 PM
Did you name the video could be I could look it up
mwatersjr
Jan 19, 2009, 08:05 PM
I think I had it set to Private. I just changed it to Public. Let me know if it works now.
wmproop
Jan 19, 2009, 08:07 PM
I think the watch is pulling all the power away from the furnace,, solution,get rid of the watch, :):):):)
hvac1000
Jan 19, 2009, 08:22 PM
Yep video works. Looks like the timing section of the chip works great. At least now you know but truthfully most folks would never notice this situation. Glad it is figured out.
mwatersjr
Jan 19, 2009, 08:28 PM
Thanks again for the help!
hvac1000
Jan 19, 2009, 08:43 PM