Log in

View Full Version : Water heater leak


Quantum62
Nov 5, 2008, 03:58 PM
Water heater problem. The T&P valve is leaking. It might go 2 weeks and then BAM... water on the floor. I have a thermal expansion tank installed. I replaced the T&P valve, but it still randomly leaks. The water pressure is 80 PSI. The temperature is set at 120 degrees. I checked both thermostats and they appear to be working correctly (electric water heater). I have NO idea what could be causing the problem. I was looking for information about the thermal expansion tanks (TET). They say that it comes pre-charged to 40 psi. When I have the water turned on, the TET is 76psi. If I turn off the cold water intake, and open the hot water faucets until they stop running (so the system is "open") the TET reads 8.5 psi. Is this normal? Any idea what could be wrong?

ballengerb1
Nov 5, 2008, 05:21 PM
I think you could install a pressure reducing valve (PRV) right after your meter to get the house pressure down to about 45 psi. Your tank pressure gauge is likely just off by about 8 psi, it should read zero with the inlet closed and the hot taps open

letmetellu
Nov 5, 2008, 07:41 PM
One idea---If you tank should have a pressure of 40# with the water off and the pressure relieved then I think your bladder in the tank has a hole in it and needs to be replaced.

If this is not the case then try to add pressure to your tank with and bicycle pump or somethiing similar.

ballengerb1
Nov 5, 2008, 08:23 PM
I'm confused by post #3, we are talking about a water heater, not a well pressure tank. There is no bladder in a water heater. With the supply closed and a hot faucet open the pressure should be zero.

KISS
Nov 5, 2008, 08:37 PM
Zero, no. Pressure is zero at the outlet of water of a pipe, but somewhere along that pipe there is a pressure drop.

Your not measuring the pressure at the outlet. Your measuring it somewhere up stream, thus frictional losses from pipe, elbows etc. show up. 8.5 psi would not be unusual.

ballengerb1
Nov 5, 2008, 08:40 PM
Not sure what you meant. There is no supply to the tank and the tank is open at the other end via a faucet. That lets the tank pressure drain from 76 psi until the water stops completely, that should be zero. Are we looking at the same picture in our minds eye?

hkstroud
Nov 5, 2008, 09:52 PM
I think Quantum62 meant that expansion tank has only 8 lbs of pressure when water pressure is relieved. Indicating ruptured bladder in expansion tank. First thing to do however, is install pressure regulating valve regardless.

KISS
Nov 6, 2008, 01:26 AM
Yep, you really need to install a PRV.

Milo Dolezal
Nov 6, 2008, 02:52 AM
KISS said it: Install Pressure Reducing Valve.

Quantum62
Nov 6, 2008, 01:45 PM
Yup. I was referring to the expansion tank only having 8 PSI when everything is open. I would "assume" that it should read 40PSI. So you guys think the expansion tank has a ruptured bladder? Is there a way to check this w/o taking it off?

Is 80 PSI water pressure really that high that I need a PRV? What is a standard pressure?

Thanks for the help guys!



I think Quantum62 meant that expansion tank has only 8 lbs of pressure when water pressure is relieved. Indicating ruptured bladder in expansion tank. First thing to do however, is install pressure regulating valve regardless.

letmetellu
Nov 6, 2008, 02:23 PM
I'm confused by post #3, we are talking about a water heater, not a well pressure tank. there is no bladder in a water heater. With the supply closed and a hot faucet open the pressure should be zero.

I am sorry about the wrong answer that I entered but I thought he already had a thermal expansion tank. That is why I thought that he had a ruptured tank.

Quantum62
Nov 6, 2008, 02:32 PM
No, your answer was correct. I was talking about an expansion tank.


I am sorry about the wrong answer that I entered but I thought he already had a thermal expansion tank. That is why I thought that he had a ruptured tank.

letmetellu
Nov 6, 2008, 02:59 PM
No, your answer was correct. i was talking about an expansion tank.

Then it is still possible that it is the bladder in the expansion tank. Water can not be compressed and so without a bladder pressure the pressure could build up past the rating on the T&P valve and when it opens it only drains a small amount of water because the pressure would drop very fast.

Quantum62
Nov 6, 2008, 03:02 PM
I posted this above:

Yup. I was referring to the expansion tank only having 8 PSI when everything is open. I would "assume" that it should read 40PSI. So you guys think the expansion tank has a ruptured bladder? Is there a way to check this w/o taking it off?

Is 80 PSI water pressure really that high that I need a PRV? What is a standard pressure?



Then it is still possible that it is the bladder in the expansion tank. Water can not be compressed and so without a bladder pressure the pressure could build up past the rating on the T&P valve and when it opens it only drains a small amount of water because the pressure would drop very fast.

KISS
Nov 6, 2008, 03:11 PM
Standard pressure is around 45-55 PSI. Your WAY above that. You need a PRV ASAP.

I figure 8 PSI is not unreasonable for reasons I said before. The closer the gage is to an open tap the lower the pressure is going to be. In the limit, i.e. when the pipe is at atmospheric pressure, the pressure is 0 PSIG.

Quantum62
Nov 6, 2008, 03:24 PM
Yes, but the 8PSI is on the expansion tank. Wouldn't I be measuring the pressure between the bottom of the tank and the diaphram? To me that SHOULD read 40 PSI, because isn't that what the tank is pre-charged to? Perhaps I'm missing something.






Standard pressure is around 45-55 PSI. Your WAY above that. You need a PRV ASAP.

I figure 8 PSI is not unreasonable for reasons I said before. The closer the gage is to an open tap the lower the pressure is going to be. In the limit, i.e. when the pipe is at atmospheric pressure, the pressure is 0 PSIG.

mygirlsdad77
Nov 6, 2008, 03:28 PM
Are you on city water or private well?

Quantum62
Nov 6, 2008, 03:32 PM
City water




on you on city water or private well?

mygirlsdad77
Nov 6, 2008, 03:38 PM
If tank says its precharged to 40psi, and you are only reading 8psi, then yes, you may need to replace tank. However, if you instal a prv. Lower your pressure, you may not even need the expansion tank.

KISS
Nov 6, 2008, 03:42 PM
Let me think about it too. Air is compressible. Water is not.

This gage is measuring water or air pressure? If it's measuring air pressure I could see it being 80 PSI. If it's measuring water pressure then I don't see it.

But, on the same note if you have a PRV, you should not be able to get to 80 PSI at all. As say 50 PSI air is compressed by 40 PSI water, you'll end up with a 10 PSI difference.

The expansion tank works because it has a variable air volume and that volume is pressurized just below the normal water pressure. It cannot read higher than the water pressure.

Think about this: Can you inflate a tire to 90 PSI from a 40 PSI stream. No.

Water is a weird fluid. It expands when cooled and it expands when heated, but we are concerned about the heating. Heating water below the boiling point will not raise the pressure 40 PSI.

Go buy a pressure gage that fits on a hose fitting and measure the house pressure at an outside tap. It won't be between 45-55 PSI.

mygirlsdad77
Nov 6, 2008, 04:04 PM
I may be lost. If you have a normal residential electric water heater, you really shouldn't need a thermal expansion tank, unless your water pressure is to high, or your water temp is to high. You say your water heater is set at 120 degrees. Does it feel scalding hot at times? Maybe try checking the temp of your water with a thermometer. This problem of the leaky temp/pressure relief valve may be as simple as a fualty themostat on the electric water heater.

EPMiller
Nov 6, 2008, 04:28 PM
If you have a normal residential electric water heater, you really shouldnt need a thermal expansion tank, unless your water pressure is to high, or your water temp is to high. You say your water heater is set at 120 degrees. Does it feel scalding hot at times? Maybe try checking the temp of your water with a thermometer. This problem of the leaky temp/pressure relief valve may be as simple as a fualty themostat on the electric water heater.

Mgd77,

You are incorrect on not needing an expansion tank. On city water, there is a back-flow prevention valve at the meter that prevents contamination of the water distribution piping network in case of a loss of pressure. When you turn on a water heater full of cold water, the expansion as it heats could drive the pressure on the house above safe limits because of that back check valve. Usually the T&P valve blows off in that case. Around here it is a code requirement to have an expansion tank on any house that has city water and a water heater, which most do! :p

EPMiller
Nov 6, 2008, 04:38 PM
Yup. i was referring to the expansion tank only having 8 PSI when everything is open. I would "assume" that it should read 40PSI. So you guys think the expansion tank has a ruptured bladder? Is there a way to check this w/o taking it off?

Is 80 PSI water pressure really that high that I need a PRV? What is a standard pressure?

Q62,

To test your expansion tank, shut the water off at the meter, shut off the water heater, open a valve in a sink on the lowest floor and let the pressure go down to nothing. Measure the pressure in your xpn tank and if it is 8 psi, pump in some air until you get it back to it's 40psi precharge number. If the pressure just keeps leaking away (thru the open faucet), then the bladder is shot. Otherwise PUT THAT PRV ON and then precharge the xpn tank to the same pressure as the PRV setting. NO MORE and not much less. You don't want much water in there at all under normal working conditions. It should only have to take water to absorb the expansion of heating water. If you actually read the installation instructions on those things they will tell you to do what I just said.

EPM

ballengerb1
Nov 6, 2008, 04:41 PM
I think I recommended a PRV in post #2. It's the logical thing at this point. I did however misunderstand KISS and Letme for a moment, I'm on board now guys.

mygirlsdad77
Nov 6, 2008, 04:44 PM
Varies from state to state I guess. We are not required to install expansion tanks on potable water systems. Just boilers and the like. I guess I'm just saying that the expansion tank is most likely not the problem for pressure, temperature relief valve leaking from time to time. We have no idea where asker is from, or what codes they follow.

I may be incorrect, for the area you live, but please do not say that I am (in general) incorrect. Kind of hurts my feelings. Lol

KISS
Nov 6, 2008, 06:08 PM
If Check valve (Backflow preventer) on Main then install Expansion Tank

If Boiler Then install Expansion Tank

If incoming water pressure is too high (>~60 PSI) [Expansion Tank Irrelevant] then install Pressure Regulator (PRV).

OK?

Quantum62
Nov 7, 2008, 02:01 PM
The water pressure at the tap is 80 PSI. It almost sounds to me like the expansion tank has ruptured AND I have to hig of a pressure entering the house.





Let me think about it too. Air is compressible. Water is not.

This gage is measuring water or air pressure? If it's measuring air pressure I could see it being 80 PSI. If it's measuring water pressure then I don't see it.

But, on the same note if you have a PRV, you should not be able to get to 80 PSI at all. As say 50 PSI air is compressed by 40 PSI water, you'll end up with a 10 PSI difference.

The expansion tank works because it has a variable air volume and that volume is pressurized just below the normal water pressure. It cannot read higher than the water pressure.

Think about this: Can you inflate a tire to 90 PSI from a 40 PSI stream. No.

Water is a wierd fluid. It expands when cooled and it expands when heated, but we are concerned about the heating. Heating water below the boiling point will not raise the pressure 40 PSI.

Go buy a pressure gage that fits on a hose fitting and measure the house pressure at an outside tap. It won't be between 45-55 PSI.

KISS
Nov 7, 2008, 02:17 PM
Get the pressure reducing valve installed first. There is no point troubleshooting the expansion tank now.

You do stand a chance of having a bad tank, but there is nothing pointing to that yet.

For lots of bedtime reading material about expansion tanks, see:

Learn About - What is thermal expansion, selecting an expansion tank, Potable vs. Non-Potable systems. (http://www.watts.com/pro/divisions/watersafety_flowcontrol/learnabout/learnabout_thermexpansion.asp)

mygirlsdad77
Nov 7, 2008, 04:44 PM
Sounds like kiss nailed it. Good luck and let us know what you decide.

EPMiller
Nov 8, 2008, 06:21 PM
Varies from state to state i guess. We are not required to install expansion tanks on potable water systems. Just boilers and the like. I guess im just saying that the expansion tank is most likely not the problem for pressure, temerature relief valve leaking from time to time. We have no idea where asker is from, or what codes they follow.

I may be incorrect, for the area you live, but please do not say that i am (in general) incorrect. Kind of hurts my feelings. lol

Sorry, I didn't mean to hurt your feelings, but I thought that was current code all over. You can see that I don't travel much! :p I will agree, an expansion tank is not needed on a city water system without any back flow prevention valves. However, I've seen leaking T&P valves that were "fixed" by nothing other than the addition of an expansion tank. But then I've also seen systems that worked fine with a back check and no expansion tank. A lot of piping helps. Around here one municipality I know of is going around and reinspecting homes and requiring back flow prevention and expansion tanks to be retrofitted. Other obvious violations are cited too, but they are bringing their systems up to date with the back flow prevention valves.

mygirlsdad77
Nov 9, 2008, 03:56 PM
I don't travel much either, so I learn new things everyday on this site. We are not required here to have back flow preventers. No hard feelings. Thanks for the update.