Log in

View Full Version : Generator Wiring


mark0139
Feb 13, 2008, 07:48 PM
I have a generator that puts out 5500watts & has (4) 120 volt 20 amp receptacles and 1 Nema L14-30 120/240volt receptacle. I am running a new wire to the panel so I can hook my travel trailer up. The RV requires a 30 amp 120volt receptacle. I have already purchased the wire and connectors but wanted some advice on where to hook the wires into the back of L14-30 receptacle . I need to have 1 ground, neutral,and hot lead but I need to be certain that I still have enough voltage and amperage to run the camper.

KISS
Feb 13, 2008, 08:01 PM
First, I want you to look here:

Look at the watertight connectors. The trailer should have pins.

The connector should have terminals X, Y, G (Green terminal) and a white terminal.

G is ground. White is neutral. Pick X or Y for the 120 V.

5500/240 is about 23 Amps and I'll bet the generator is fused for 20. Generally the ratings are at the higher voltage.

If it needs 30, you'll be a little short.

Washington1
Feb 13, 2008, 08:02 PM
Why would you supply power to your generators 30A receptacle to supply power to your RV?

Take the generator out of the picture.

You need to go buy yourself a nema 3R box with 30a 125v RV receptacle, and a 30A RV extension cord with RV plugs.
Run a #10 copper wire from panel to 30A NEMA 3r RV box, then plug your RV cord into the outlets.

If you have a different setup, then let us know.