I replaced a breaker box in my garage with a larger one. After reattaching all wiring to the new breakers everything worked perfect. The box holds 12 breakers but only six have the correct voltage and I want to add more breakers which is the reason for the larger box.

Looking at the box... There are 12 slots.. 2 side by side 6 down, every other set of 2 only has 60 amps. Where did I go wrong?

Thanks for any help

tkrussell
Dec 6, 2007, 03:27 AM
Need a picture of the interior of the panel to see how you wired it.

The possibilities are endless.

Stratmando
Dec 6, 2007, 07:42 AM
Verify the neutral is on neutral bar, and Each Hot is on the correct lug to supply power to each Buss. Wonder if you have a hot and neutral reversed.
Measure voltage between the ground and neutral. And all combinations between the 2 hots and neutral.