Ask Experts Questions for FREE Help !
Ask
    HGilbert's Avatar
    HGilbert Posts: 3, Reputation: 1
    New Member
     
    #1

    Nov 17, 2007, 07:31 PM
    Valve does not turn on furnace in one zone
    I am having problems with one zone of a two-zone heating system. The thermostat does not function; previously this happened intermittently, and turning on the valve manually while the thermostat was set high enough started the furnace. Now, turning on the valve does not help either; the only way to get heat into this zone is to open the valve manually and turn up the thermostat in the other zone so that the furnace starts.

    Should the valve opening turn on the furnace independently of the thermostat - i.e. is this clearly a valve or valve wiring problem? Or could it be a thermostat problem?
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Nov 17, 2007, 07:39 PM
    What brand of valve and model number?
    Some valves have end switches etc so we need the model
    HGilbert's Avatar
    HGilbert Posts: 3, Reputation: 1
    New Member
     
    #3

    Nov 17, 2007, 07:48 PM
    The valve is by Honeywell: # 40004850-001 (only number I see on it)
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #4

    Nov 17, 2007, 10:19 PM
    V8043 or something like that is what you are looking for. The number you gave might be a number for a replacement power head which really does not answer the question but we are a little closer.

    The end switch that is in your valve might be defective. The end switch is what turns on the boiler circulator pump when the valve opens. Now if the valve is not opening to start with there are a few things to check.

    If the system is 24 volts or another voltage you need to test for that voltage at the valve when the system is set to turn on the valve. If voltage is missing it could be a transformer or other voltage source including the thermostat.

    If when the valve is set to open manually the boiler/pump does not kick on you need to check the end switch contacts.

    See this to check if this is the type of valve you have and the associated wiring.

    http://customer.honeywell.com/techli...0s/69-0404.pdf

    And here

    http://customer.honeywell.com/techli...0s/60-2133.pdf

    NOTE there are many configurations of voltage and switch as you will see in all the drawings and hook ups. Something should be there for your situation.
    HGilbert's Avatar
    HGilbert Posts: 3, Reputation: 1
    New Member
     
    #5

    Nov 18, 2007, 08:31 AM
    Well, I jiggled the valve box, took off the cover, tightened all the electrical connections and it works again. This happens periodically; I replaced the valve once already (a couple of years ago). Very mysterious... it certainly appears that it's not a problem with the thermostat, however.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Zone valve problem [ 5 Answers ]

Zone valve for upstairs will not open. Already replaced thermostat. The only time I have heat upstairs is when the valve in manually opened and the downstairs heat kicks on. Any help or advice would be great! Thank you.

Furnace only firing in one zone [ 1 Answers ]

Hello: I have a digital thermostat and gas heat (forced hot air). When I turn the heat on upstairs, the blower only blows cool air. When I turn it on downstairs, it works normally. I checked the fuse box to see if a fuse had been tripped, but it was normal. What other simple steps can I take...

NG Furnace will not turn on [ 2 Answers ]

Make: RHEEM Model: RGDO 06NC ER Installed: 1990 Problem: Observe glow in burner area from ignitor but the gas won't turn on. After a few seconds the glow will turn off. The Hot Surface Ignition Module was replaced in 1997. Please advise.

Furnace won't turn off [ 2 Answers ]

Our furnace won't turn off. I turned the heat off at the thermostat and no luck. I changed out the thermostat with a new one and it is doing the same thing. If the breaker is off, the fan and heat are off; is the breaker is on, the fan and heat are on even if the thermostat is set to off. We...


View more questions Search