    Furnace blower can not auto start
    I have a problem with my furnace blower not starting automatically. It works good when I swiched the fan option to "ON", the furnace was burning and fan was running. However if I pick "AUTO", only the furnace burns periodicaly, and the fan totall gets stuck. I am wondering if it is a wiring problem, but not so sure. I will appreciate any help from anyone.
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #2

    Oct 30, 2005, 04:54 PM
    You have 2 temperature limit switches in the furnace. One turns on the blower once it is hot enough when the furnace comes on. The second one turns off the gas if the blower fails to come on, or it gets too hot for some other reason. If the blower fails to start, the gas will keep coming on until the upper limit switch shuts it off.

    Some furnaces use a different relay and coil for a higher speed for fan only and A/C is you have it. This means the problem could be the relay too. Most of the controls on newer furnaces except the limit switches, are on a board making diagnose and repair difficult. If the limit switch seems to be working, you may be best off buying and installing a new board, hoping that fixes the problem. You could call a repairman, and pay another $100 in labor for him to replace the board. $$$$$$$
    hwuaiyuc's Avatar
    hwuaiyuc Posts: 9, Reputation: 1
    New Member
     
    #3

    Oct 30, 2005, 06:31 PM
    The fan worked very well in summer time when use A/C.
    [QUOTE=labman]You have 2 temperature limit switches in the furnace. One turns on the blower once it is hot enough when the furnace comes on. The second one turns off the gas if the blower fails to come on, or it gets too hot for some other reason. If the blower fails to start, the gas will keep coming on until the upper limit switch shuts it off.

    Some furnaces use a different relay and coil for a higher speed for fan only and A/C is you have it. This means the problem could be the relay too. Most of the controls on newer furnaces except the limit switches, are on a board making diagnose and repair difficult. If the limit switch seems to be working, you may be best off buying and installing a new board, hoping that fixes the problem. You could call a repairman, and pay another $100 in labor for him to replace the board. $$$$$$$[ Thank you very much. The interesting thing is fan worked perfectly in the summer time when I uesed A/C. At your point, there are 2 control systems to the fan for heater and cooler separately? ]
    hwuaiyuc's Avatar
    hwuaiyuc Posts: 9, Reputation: 1
    New Member
     
    #4

    Oct 30, 2005, 06:47 PM
    But how about that fan worked well in the summer time?
    Thank you very much, Labman. The interesting thing is fan worked perfectly in the summer time when I uesed A/C. At your point, there are 2 control systems to the fan for heater and cooler separately? By the way, where is the board, I checked manu and there is not a "board".
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #5

    Oct 30, 2005, 07:04 PM
    The older furnaces were much simpler and cheaper to fix. Start at the blower motor. Follow its wires back to the relay or relays. The relay should have 4 wires, one connecting to the power supply from the house, one to the motor, one to a transformer, and one to the limit switch. If you have 24 volts at the wires from the limit switch and transformer, power from the house, and the blower isn't running, the relay is bad. You may be able to confirm it is the problem by giving it a knock. If the blower starts, the relay is definitely bad.
    hwuaiyuc's Avatar
    hwuaiyuc Posts: 9, Reputation: 1
    New Member
     
    #6

    Oct 30, 2005, 07:19 PM
    Thank you
    Thank you, I know where it is, and will work on it.
    hwuaiyuc's Avatar
    hwuaiyuc Posts: 9, Reputation: 1
    New Member
     
    #7

    Oct 30, 2005, 08:15 PM
    Yes, you are right. My furnace was older, around year 1985. But I found 5 wires connecting to the relay instead of 4, of which 2 were connected to the limit switch. Do you know the 5 wires are right? :)
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #8

    Oct 30, 2005, 08:28 PM
    The fifth wire could be from the A/C. That makes it look like the limit switch could be bad. On the other hand, if it set for a while between the cooling season and when you needed heat, the relay could have stuck.
    hwuaiyuc's Avatar
    hwuaiyuc Posts: 9, Reputation: 1
    New Member
     
    #9

    Oct 30, 2005, 08:49 PM
    Do you think it might be a problem of wiring on the limit switch? Someone repaired wires to A/C before summer came this year.
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #10

    Oct 31, 2005, 08:53 AM
    Yes. The switches close when the air in the furnace heats up. If somebody
    Disturbed the wires to the limit switch. It would look like it was open, the air
    Not hot enough to start the blower. If you have a multimeter or a test light,
    Check the wires to the limit switch. With the power off, it should show
    Conductivity through the switch. Sometimes just bending a wire a little can leave it broken off inside the insulation.
    hwuaiyuc's Avatar
    hwuaiyuc Posts: 9, Reputation: 1
    New Member
     
    #11

    Oct 31, 2005, 08:53 PM
    I tested relay by using multi-meter, and it sounds good. Now I am concerning about the wiring. Right out of the blower motor, there is a small box that contains a transfromer and a relay. On the box is a switch board, all wires connecting to the thermostat are fixed on this small board. How to check if those wires are rightly connected? By the way, how I re-ignit the little light in the furnace, it disappeared when I checked the limit switch? :confused:
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #12

    Oct 31, 2005, 09:30 PM
    The guy could have messed up the heating wires. The basics:

    Usually there is a 24 volt AC transformer in the furnace with the secondary winding connected to a red wire running to the thermostat and a blue wire, common, to the gas valve, A/C relay, and fan relay. From the thermostat there will be white wire to the gas valve, yellow to the A/C, and green to the fan. The thermostat is wired to switch the power from the red to the white, yellow, and green as needed with the blue completing the circuit. Most thermostats and furnaces have the contacts labeled R, B or C, W, Y, and G for the corresponding wire colors. It may be wired to have the A/C control wires return to the furnace and its controls and then a second wire goes to the A/C unit. Internal wiring may replace the green wire if the thermostat does not give you the option of fan only or continuous fan. Digital or programmable thermostats may need the blue wire connected to them.

    As for the little flame, it is the pilot light. If there aren't instructions on lighting it posted on the furnace, look for a knob with off, pilot, and on positions on the gas valve. Turn it to pilot, hold it in, and light the pilot light. Hold it on a minute or 2 to heat up the thermocouple. Then release it and turn the knob to on.
    hwuaiyuc's Avatar
    hwuaiyuc Posts: 9, Reputation: 1
    New Member
     
    #13

    Oct 31, 2005, 10:27 PM
    Thanks Labman, I figured out the flame, and I am working on the wiring.
    ravithas's Avatar
    ravithas Posts: 14, Reputation: 2
    New Member
     
    #14

    Nov 21, 2005, 12:01 PM
    I have same problem as you had with your furnace
    Hi "hwuaijuc",

    I have similar problem as you had last month with your furnace. It runs perfect on "Fan On" mode through thermostat. When it's on "Auto" mode, the blower doesn't kick on.

    Did you resolve your problem. I hope you did. Would you please share with me your findings and provide me with some tips?

    I am thanking you in advancing for your assistance.

    Thanks, Ravi :confused:
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #15

    Nov 21, 2005, 12:40 PM
    The blower operates completely differently in heating mode than On or A/C. Usually there is a lower speed coil in the blower motor controlled by a different relay which in turn is control by a limit switch. Check the limit switch first. It should have power either from the white wire from thermostat or directly from the red wire on the transformer. Power should flow to it and back once the furnace is up to temperature. It then activates the blower relay, powering the low speed coil. Often as not, the problem is the relay. Unfortunately, the newer ones are on a circuit board, challenging to diagnose and replace. The board is expensive to replace. You want to be very sure the low speed blower coil and the limit switch are working before replacing the board. If the board is bad, you can save $50-100 by not having a technician to come out and check it and replace it.

    OK, I still had this on my clipboard from my last answer.
    ravithas's Avatar
    ravithas Posts: 14, Reputation: 2
    New Member
     
    #16

    Nov 21, 2005, 06:52 PM
    Please response
    Hi "hwuaijuc",

    Were you able to fix your furnace? As I mentioned earlier, I have the similar problem as you had.

    Labman is helping me out with his comments. I am trying to follow him. In the mean time, I would like to know whether you were able to identify and fix the problem.

    Please let me know.

    Thanks, Ravi :confused:
    mitchella's Avatar
    mitchella Posts: 3, Reputation: 2
    New Member
     
    #17

    Nov 22, 2005, 06:01 PM
    Maybe this will help
    Hello boys, my first post and I learn a lot reading this forum, especially from Labman, a true Rennasance man. I never could spell.
    I think probably the fan is running on high speed when you put the thermostat on "ON", here the thermo is sending out a G signal, and is probably going to high speed by powering the cooling relay. When the thermo calls for heat on "AUTO", it sends out a "W" signal and should work the low speed, or heat fan relay. I sounds like your high speed circuit is working but not your low speed. To check your low speed circuit, do what Labman has suggested by following the voltage from the thermostat, limit switches, etc. To be safe, you can check the continuity of the components without the power on using the ohm meter. You can remove the limit switche, for example, and bench check them with a hair drier or flame. You should have a schematic, maybe you can find it and maybe post a picture or scan of it. This would help immensly. :D
    ravithas's Avatar
    ravithas Posts: 14, Reputation: 2
    New Member
     
    #18

    Nov 23, 2005, 05:28 AM
    Hi Michella, :confused:

    Thanks for the response.

    How do I find out whether the limit switch is a part of the control board or outside of the board?

    Please help me out.

    Thanks, Ravi
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #19

    Nov 23, 2005, 08:01 AM
    Quote Originally Posted by ravithas
    Hi Michella, :confused:

    Thanks for the response.

    How do I find out whether the limit switch is a part of the control board or outside of the board?

    Please help me out.

    Thanks, Ravi
    My omission. The limit switch must be inside the furnace around the heat exchanger. I also failed to mention the upper limit switch. It is set higher. And shuts the gas off if the blower fails to start. The limit switches may be connected directly to the blower relay and gas valve, or to logic on the board. If the limit switches connect to the logic, it is harder to sort them out. You may need a schematic. Might be easier to yank them both out and hit them with the hairdryer as suggested. I think the lower one should close when warm, and the upper one open.
    ravithas's Avatar
    ravithas Posts: 14, Reputation: 2
    New Member
     
    #20

    Nov 25, 2005, 12:30 PM
    I believe I see only one limit switch, which is located inside the furnace and above the heat exchanger. There are two thermocouples attached with a one cent size round tab connected and placed inside the furnace above the heat exchangers. Is this the limit switch. How do I make sure the limit switch is working?

    Please advise me. As I mentioned earlier, I am running the furnace with "Fan On" mode on the thermostat. The blower doesn't come on with "Auto" mode.

    Your help is highly appreciated.

    Thanks, Ravi :confused:

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Fan Blower will not come on in auto [ 8 Answers ]

Blower will only come on when in "ON" position. "Auto" position will not cause it to go on. One can hear the thermostat click (basically saying its time to kick in) but the blower will not commence until I manually set it to "ON". At first, I thought it was thermostat so I replaced it with a...

Furnace Manual Fan OK - Not Auto Though [ 1 Answers ]

I have a York Stellar Plus (15yrs old) with an Auto and Manual Fan Switch on the T-stat. The Fan will work when turned to ON (at the T-Stat) but it will not come on when you turn the heat on with the Fan switch turned to Auto. I have replaced the Limit Switch. No difference Thanks!

The blower doesn't start on "Auto" [ 10 Answers ]

Please someone help me. My furnace Lennox G20Q3/4E-100-5 behaves as follows: 1) Fan is on "Auto" 2) Thermostat calls for heat 3) Green light comes "On" on IPI module and then burner comes "On" 4) Flame occurs 5) Blower doesn't come "On". After a while, the burner stops due to safety. It...

Furnace won't heat in Auto [ 2 Answers ]

I have read the different posting and replys, but they don't seem to address my problem. Friend has an older Kenmore Power Miser 70 that has an old electronic ign. (no flame senser). The furnace will heat when the fan switch is set to "on" position, and it will cycle the heat. When the fan is...

FAN doesn't work when it's 'Auto', but works fine at 'On' in my central air/furnace [ 1 Answers ]

undefinedFAN 'On' or 'Auto'FAN 'On' or 'Auto' Hi, I have programmable thermostat connecting air condition / furnace system. Now if I turn system to 'Cool' and Fan at 'Auto', no cool air come out (compressor works, you can hear the noise). If I set FAN to 'On', life is getting better. But the FAN...


View more questions Search