    20 AMP Outlet on a 30 AMP Circuit
    I have a question regarding putting a 20 amp outlet on a 30 amp circuit. I'm replacing appliances in my kitchen, and there's currently a 30 amp, 240V, 3-wire + ground feed to the location where the oven is located, on a 30 amp, double pole breaker. I'm planning to install an electric oven (240V) and a microwave oven (120V). Can I split off a single 20 amp, 120V receptacle for the microwave oven from one of the hot feeds while maintaining 240V for the oven? Would using a GFCI outlet instead of a standard one increase the safety of this installation? Or am I going to be forced to run another line to the breaker box specifically for the microwave?
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #2

    May 3, 2007, 10:43 AM
    You should run new wiring for Microwave.
    Most Electric ovens use at least 40 Amps,(#8)for the hots and # 10 for the Ground and #10 for the Neutral.
    I always pull #6 for hots, #8 for neutral and 10 for ground to be able to handle about any home oven.Adjust breaker accordingly(see Nameplate)
    ballengerb1's Avatar
    ballengerb1 Posts: 27,378, Reputation: 2280
    Home Repair & Remodeling Expert
     
    #3

    May 3, 2007, 10:48 AM
    Stratmando has it pinned. Leave the 240 as a dedicated line and pull new wire and circuit for the microwave. Just to clarify, "20 amp outlet on a 30 amp circuit" your outlet isn't amp rated, the wire and the breaker consistute the max amperage of the circuit.
    gcaxp's Avatar
    gcaxp Posts: 2, Reputation: 1
    New Member
     
    #4

    May 3, 2007, 10:55 AM
    Quote Originally Posted by ballengerb1
    Stratmando has it pinned. Leave the 240 as a dedicated line and pull new wire and circuit for the microwave. Just to clarify, "20 amp outlet on a 30 amp circuit" your outlet isn't amp rated, the wire and the breaker consistute the max amperage of the circuit.
    Then what's the difference between a 15 amp and 20 amp outlet?
    ballengerb1's Avatar
    ballengerb1 Posts: 27,378, Reputation: 2280
    Home Repair & Remodeling Expert
     
    #5

    May 3, 2007, 11:04 AM
    The outlet fixture is the same but the wiring inside the outlet leading to the breaker box is heavier for a 20 amp than a 15 amp. The wiring was hopefully matched to your circuit breakers when it was installed. If there have been home owner improvements over the years this matching may be in doubt.
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #6

    May 3, 2007, 12:18 PM
    Most 120 volt outlets are rated for 15 amps. Some devices drawing more than the 12 amps a 15 amp circuit is derated to, use a different style plug rated for 20 amps and require a matching 20 amp outlet. So there are outlets rated for 20 amps. Not that microwaves come with plugs fitting them.

    If you did run 120 volt service from a 30 amp, 240 circuit, you would have to run #10 wire. Not everything that will work, meets code. Our electrical expert, tkrussel, has posted a link to the NEC in a sticky at the top of the forum. It is often better to wait for him to explain what it means. Whatever he says, you can trust. I think any outlet within 6' of a sink must be GFCI.
    jboughto70's Avatar
    jboughto70 Posts: 1, Reputation: 1
    New Member
     
    #7

    Jul 27, 2010, 10:29 AM
    Actually, there is a difference between a 15 amp and 20 amp outlet and it has nothing to do with the wiring, it is what the internal parts of the receptacle can handle. If you were to run a 20 amp receptacle off a 30 amp circuit, the breaker would allow 30 amps before tripping, which is more than the receptacle is made for, and can cause short circuits and fires, so this is not to be done! You definitely need new wires for the microwave.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #8

    Jul 27, 2010, 01:52 PM
    Quote Originally Posted by jboughto70 View Post
    actually, there is a difference between a 15 amp and 20 amp outlet and it has nothing to do with the wiring, it is what the internal parts of the receptacle can handle.
    Not entirely true. The only difference between a 15 and 20A receptacle is the orientation of the slots. The internals are basically the same.


    Quote Originally Posted by jboughto70 View Post
    If you were to run a 20 amp receptacle off a 30 amp circuit, the breaker would allow 30 amps before tripping, which is more than the receptacle is made for, and can cause short circuits and fires, so this is not to be done!
    Again, not exactly. The breaker protects the wiring, NOT what is plugged in. Besides, a duplex 20A receptacle is TWO 20A receptacles.
    Running more than 20A through it will NOT cause a short circuit. In fact, I am curious as to how you think this is possible.
    It can however cause the internal parts to get too hot since it is rated for only 20A feed-through. Even a 15A duplex receptacle is rated for 20A feed-through.
    The codes on what devices, receptacles and loads are allowed on what size circuits can be confusing, but they are pretty straight forward.


    Quote Originally Posted by jboughto70 View Post
    You definitely need new wires for the microwave.
    You are aware that this thread is over three years old, right? I think the OP is done by now.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

20 AMP Circuit with 15 AMP Receptical, is this OK, and in code? [ 5 Answers ]

This is sort of similar to the other thread, but my problem is the house I bought is wired with 12, all the breakers are 20AMP except for the 30AMP for the AC and Dryer. When me and my dad were changing the power recepticals, which were 15 amp, someone told us that we should have 20 recepticals, or...

10/2 wiring on 15 & 20 amp circuit [ 6 Answers ]

I was wondering if it would be okay to use 10/2 wire on branch circuits in my house? Any help would be greatly appreciated. Thanks!

Can you use a 15 amp outlet on a 20 AMP breaker with 12-2? [ 13 Answers ]

I have a few questions that I need help on. I recently moved into my home and discovered a few things. 1. 12-2 wire has been ran throughout the house. Can you use a 15 amp outlet on a 20 AMP breaker with 12-2?? 2. How many lights would you say you can run on 12-2 and/or 14-2 wire? 3. How...

Compatibilities between awg wiring, breaker amp size, outlet amp size [ 4 Answers ]

Hi. Is there a resource out there, prefereably on the web, that outlines the compatibilities between awg wiring, the breaker amp size, outlet amp size, how many recepticles/outlets can be on x amp outlet, etc? For example, it would be nice to see something that shows: you can use a 20 amp...

40 amp range in 30 amp circuit [ 1 Answers ]

I have a 30 in drop in range that is hard wired. The circuit breaker is 30 amps, house built in 1987. The new range is a slide in and requires 40 amps. I was told I would also need a junction box installed and circuit upgrades. How many hours are expected for an experienced electrician to do...


View more questions Search