    Conduit sizing?
    Hi all!
    I am relocating my breaker box approx 30 feet from its original location. Installing splice box in the old location for connections. My question is : I have 14 12-2 and 3 12-3 to pull from new box to splice box what size conduit do I need so not to worry about heat build up or de-rating breakers?

    Thanks
    :)
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #2

    Aug 19, 2005, 06:54 AM
    Usually you do not put NM such as 14-2 in a conduit. It may not meet code. Usually you use singles such a T or TW. My old handbook gives a maximum of 9 #14 singles in 1/2'', 15 in 3/4'', and 25 in 1''. For #12, 7 in 1/2'', 12 in 3/4'', and 19 in 1''. Be thinking this over and checking prices while waiting for newer info from Tkrussel.

    I recently did a small adding outlets project, and my local Ace Hardware had better prices on THNN than Lowe's and Home Depot.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #3

    Aug 19, 2005, 01:53 PM
    Once you have 4 or more current carrying conductors in a conduit, you must begin derating. Sleeving NM cable is not prohibited by code specifically, but only practical if you want to sleeve a cable or two a short distance. I would not try pulling 17 cables through 30 feet of conduit. Not only do you need to size the conduit for the actual wires, you would also need to allow for the sheathing of each cable, and not fill the conduit more than 40 % with the cable. Without going through all the calcs, you would probably need a 4-5 inch conduit.

    Do exactly what Labman suggested, run single conductors through the conduit. The most common used today is THHN insulation. The insulation is rated to carry much higher current, and helps a great deal with derating.

    With the cables you mention, you have 37 current carrying conductors, which must be derated 40 %. Installing all in one conduit requires some calculations. I know I will get some comments on this, but #12 THHN is rated to carry 30 amps, derating by 40% will only allow 12 amps. So running 37 #12 in one conduit cannot be done if all,I assume , are connected to a 20 amp breaker.

    There are two methods to "derate", one is to lower the size of the breaker, the other is to use larger wire. If all are #12 they as I said, probably all 20 amp circuits with 20 amp breakers.

    One simple way of doing this is to use one 1-1/2 in EMT conduit and install 38 #10 wires. This size conduit can hold exactly 38 #10 THHN wires, and 37 #10 current carriying wires need to be derated 40 % of 40 amps that #10 THHN can carry. The 38th wire is the equipment ground that will take the place of each of the bare grounds in each cable, you do not need to run each ground in each cable.

    To make it simple I would run the following:

    1-1/2 in EMT conduit with 38 #10 THHN wires consisting of: 20-hots(colors) Labeled #1 through 20
    17-neutrals(white)
    1-green

    If you want to use any other type of conduit, you better check back because all the other types, such as flexible, or PVC, etc. has lesser amounts of #10 allowed.

    There is a minimum size junction box allowed, the box must have at least 217 cu inch of volume, allowing for 2.5 CI for each #10 and 2.25 CI for each #12. A 6" x 6 " x 6" only has 216 cu in, so thats too small, the next size available is probably a 8" x 8" x6", has 384 CI of volume. A larger box can be used if you have the space, and would make splicing all the easier.

    There is a lot of info here, review it and let me know if there are any other questions.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Aug 21, 2005, 05:01 AM
    I made a typo, size conduit should be 1-1/2 inch not 1-1/4 as I originally wrote. Apologize for the mistake
    ultrajoker's Avatar
    ultrajoker Posts: 18, Reputation: 2
    New Member
     
    #5

    Aug 23, 2005, 03:40 AM
    Thank you for the advice labman & tkrussell. Pulling THHN is probably my easiest and best bet , I get paranoid :o about the heat dissipation because none of us wants an electrical issue like that. I am going to use my old 100 amp breaker box as a pull/splice box that's 12 x 18 x 4 so that gives plenty of space for the connections to "breathe" . Using 2" conduit and pulling the 240 lines directly to the new box, I should be good without heat issues. :)
    Thanks Again!

    Keith

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Bow Sizing [ 2 Answers ]

How does one determine what size bow to buy? I have noticed many lengths and draw distances. I don't want to spend a lot of money on a bow to find out it is not comfortable to use.

Conduit requirements for basement wiring [ 1 Answers ]

I am finishing a basement with stud wall and dry wall. Is there any need for conduit to carry the wires behind the dry wall? I know for an unfinished basement wiring below grade must be in conduit but must it if the walls are finished? Thanks Dschaar

Do I need conduit? [ 4 Answers ]

I have a panel in my garage for my garage based workshop. I want to run a 220 volt circuit (have have the capacity in the panel to do so). My question is whether I need to run the wire inside conduit or can I run romex without conduit. The wire will be behind drywall the entire way so it will...

Flexible conduit limitations [ 5 Answers ]

I am rerouting wires in a condo. The original construction has every wire running through rigid conduit. It would be much easier for me to use flexible conduit for the reroutes. Are there any limitations to the length of a flex run? Can sections of rigid conduit be interspersed when it is...

Electrical conduit [ 1 Answers ]

I am running a new exterior line to a carport to install two fluorescent lights in the ceiling of a "V" shaped aluminum 2 car carport. The underside of the carport reaches very hot temperatures during the summer months, metal parts are burning hot to the touch. I undersatnd I need to use exterior...


View more questions Search