    Replace main breaker in a ge 125 amp outdoor panel
    Can the main breaker in a 125amp ge outdoor panel be replaced with a regular 60 amp double pole breaker?
    smoothy's Avatar
    smoothy Posts: 25,492, Reputation: 2853
    Uber Member
     
    #2

    Jul 19, 2013, 07:56 AM
    Why do you want to reduce its capaicty to less than half its original.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #3

    Jul 19, 2013, 08:52 AM
    I agree. Why would you need to?

    Maybe you are using it as a sub-panel and want the main intact? If so the main can be larger than the feeder breaker.

    Either way, explain a bit what you are doing so we can give an accurate answer.
    paulloftis00's Avatar
    paulloftis00 Posts: 3, Reputation: 1
    New Member
     
    #4

    Jul 19, 2013, 09:42 AM
    Ok I have to have a subpanel with a main breaker outside. The lowest amp outdoor panel I could find is a 125 amp ge panel. I only need 2 - twenty amp circuits of power so I don't want to buy bigger wire for 125 amps I would like to know if I can change that 125 amp breaker to a 60 amp and run 6/3 from main panel to subpanel. Basically will the main come out to be replaced with a regular 60 amp double pole breaker
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #5

    Jul 19, 2013, 09:46 AM
    The 125A breaker is only serving as a disconnect. The breaker in the main panel is your feeder breaker and you wire needs to be sized to that.
    Basically, the sub-panel can be larger than the feeder breaker and wire.
    paulloftis00's Avatar
    paulloftis00 Posts: 3, Reputation: 1
    New Member
     
    #6

    Jul 19, 2013, 03:06 PM
    Ok thanks. And just to confirm the inspector won't have a problem with that.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

CAN I putting a lugs SUB -PANEL box 125 amp breaker in a 200 amp main house to feed [ 1 Answers ]

CAN I putting a lugs SUB -PANEL 125 amp breaker in a 200 amp main house to feed the sub-box

Why do I have to replace the main breaker in sub panel [ 4 Answers ]

Home insp for the buyer of our house said we need to do it

I have a 125 amp. Main panel.no space can I run small sub panel [ 2 Answers ]

I have a 125 amp. Bryant main panel that is maxed out with piggy back breakers. Can I feed a small amp. Panel off the main if I remove some breakers and put them into the sub panel , I need to run a 2 pole 30 amp. On the sub panel.

Replace a two pole breaker in main panel box [ 1 Answers ]

I need two replace a bad two pole breaker in main panel boxwhat tools do I need

125 amp subpanel - can a 60amp main breaker be used? [ 6 Answers ]

My question is in the title. Here are the details, I bought a 125 amp sub-panel but I only need 60 amps. The main service panel is 200 amps. I ran a 6/3 awg wire to the sub-panel. Can I install a double pole 60 amp breaker in the main panel to power the sub-panel or do I have to use a double pole...


View more questions Search