    Service entrance cable size for 100 amp and 200 amp service.
    I would like to know what size aluminum sec I would need for 100 or 200 amp service
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    Nov 1, 2008, 01:52 PM
    #2 for 100A
    4/0 for 200A
    brianbadbrian's Avatar
    brianbadbrian Posts: 1, Reputation: 0
    New Member
     
    #3

    Nov 2, 2011, 09:45 PM
    100 amp #4cu or #2al

    200 amp #2/0cu or #4/0al.. .

    Try looking at the NEC for service entrance conductor ampacity before you answer stan.. .

    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Nov 3, 2011, 02:41 AM
    And what exactly is incorrect about Stan's answer?
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #5

    Nov 3, 2011, 03:55 AM
    Quote Originally Posted by brianbadbrian View Post
    try looking at the the NEC for service entrance conductor ampacity before you answer stan . ..
    Hmmm... I actually find this pretty funny. :D
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #6

    Nov 3, 2011, 05:24 AM
    Brian,

    Try reading the question before running off with the mouth.

    The OP only asked for the sizes for Aluminum conductors. Stan gave the correct answer.
    cre8tive31's Avatar
    cre8tive31 Posts: 6, Reputation: 1
    New Member
     
    #7

    Apr 4, 2012, 07:48 PM
    What seize wires do I need from the meter can to a transfer switch for a standby generator. And also what seize do I need from the transfer switch to the service panel going into conduits. How many singles
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #8

    Apr 5, 2012, 04:28 AM
    Quote Originally Posted by cre8tive31 View Post
    What seize wires do I need from the meter can to a transfer switch for a standby generator. And also what seize do I need from the transfer switch to the service panel going into conduits. How many singles
    All we know is you want to install a transfer switch.

    What size service?
    What size transfer switch?
    What size generator?
    What size conduits?
    What are "singles"?

    What is your location?
    cre8tive31's Avatar
    cre8tive31 Posts: 6, Reputation: 1
    New Member
     
    #9

    Apr 6, 2012, 02:40 AM
    200A service.
    200A automatic transfer switch with service disconnect.
    20,000KW GE whole house generator.
    1 1/2" or 2" PVC conduit depending on wire seize.
    Single wires from meter can to transfer switch and from transfer switch to 200A service panel using PVC conduit.

    Location.
    Bloomfield CT.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #10

    Apr 6, 2012, 12:14 PM
    Very good. Thank you.

    You'll need typical 4/0AL or 2/0CU, three conductors, from the meter to the transfer switch. You can downsize the neutral if you like. 2" is typical.

    From the transfer switch to the panel you'll need four wires, using a dedicated equipment ground, this can be #4cu. 2" will work as well.
    Remember, the main panel will now become a sub-panel, so all the grounds will need to be separated from the neutral bar and a dedicated ground bar installed, and the neutral bond removed.

    From the generator to the transfer switch you'll need #4cu minimum, also running four wires. I'd do a separate 1" for the power and a 3/4" for the controls.
    cre8tive31's Avatar
    cre8tive31 Posts: 6, Reputation: 1
    New Member
     
    #11

    Apr 6, 2012, 03:53 PM
    From the transfer switch to the generator.
    I was thinking of running as follows:
    3 single THHN #3
    1 #6
    2 #12
    2 #18 or 1 twisted pair #18 (in a separate conduit)

    Could I use 3 single THHN 3/O for meter can
    And ( 4 single THHN 3/O going back to the panel or 3 THHN 3/O and a #6)

    In a 2" conduit PVC
    cre8tive31's Avatar
    cre8tive31 Posts: 6, Reputation: 1
    New Member
     
    #12

    Apr 6, 2012, 04:14 PM
    From the transfer switch to the generator.
    I was thinking of running as follows:
    3 single THHN #3
    1 #6
    2 #12
    2 #18 or 1 twisted pair #18 (in a separate conduit)

    Could I use 3 single THHN 3/O for meter can
    And ( 4 single THHN 3/O going back to the panel or 3 THHN 3/O and a #6)

    In a 2" conduit PVC
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #13

    Apr 7, 2012, 04:45 PM
    Quote Originally Posted by cre8tive31 View Post
    From the transfer switch to the generator.
    I was thinking of running as follows:
    3 single THHN #3
    1 #6
    2 #12
    2 #18 or 1 twisted pair #18 (in a separate conduit)

    Could I use 3 single THHN 3/O for meter can
    and ( 4 single THHN 3/O going back to the panel or 3 THHN 3/O and a #6)

    in a 2" conduit PVC
    The #3 and 3/0cu are overkill for residential, but you can if you like.
    The four 3/0cu is WAY overkill IMO.
    cre8tive31's Avatar
    cre8tive31 Posts: 6, Reputation: 1
    New Member
     
    #14

    Apr 7, 2012, 08:09 PM
    Thank you so kindly for all of your useful info.
    Once again I thank you,stanfortyman.
    cre8tive31's Avatar
    cre8tive31 Posts: 6, Reputation: 1
    New Member
     
    #15

    Apr 7, 2012, 08:13 PM
    Oh by the way the generator is about 100ft. Away from the transfer switch and the service panel and that's the reason for that seize wire.
    shottsk2002's Avatar
    shottsk2002 Posts: 1, Reputation: 1
    New Member
     
    #16

    Dec 17, 2013, 08:04 PM
    Wouldn't the transfer switch be the sub panel since first point of entrance is still main panel?
    hfcarson's Avatar
    hfcarson Posts: 1,003, Reputation: 49
    Ultra Member
     
    #17

    Dec 18, 2013, 05:05 AM
    Shottsk - would you call a transfer switch a panel?
    And if it was?
    Please, elaborate...

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Service entrance cable [ 23 Answers ]

I am re-wiring an old house. It is a small 2 bedroom, 1 bath house. We put in a 200 amp service and need to run a service entrance cable about 20 -25 ft to the inside breaker panel. My question is how big of a gauge wire should we run for the service entance cable. #? 3 conductor with ground in...

Service entrance cable [ 2 Answers ]

Having new 100amp meter installed professionally,but I am burying wire to the building which is 125' from where meter is mounted. Will I have to upsize the size of wire because of the distance? I also intend to enclose in conduit, so I'm not worried about using "U" coded wire

Size of main breaker and service entrance cable [ 1 Answers ]

Hi, I am new on this site. I just want to know what is the minimum size of service entrance conductor and main breaker for 17 lighting outlets and 15 conveniece outlets plus one 1.5Hp aircon and 2000 heater. Your reply would be highly appreciated. Thank you.

Cable TV and Telephone New Service Entrance [ 7 Answers ]

I'm in the process of changing the location where the telephone and cable service come into my house to a new location. I was wondering if there is a proper way to correctly attach the two lines (one coax for cable and one multi conductor for telephone) coming from the overhead pole in my back...

Service entrance cable [ 1 Answers ]

Is there a code restriction on the footage of service entrance cable from the triplex to the meter socket ?


View more questions Search