    Proper wire sizing?
    We are re-routing the supply line to our pump house, where there is an extension panel with 30A 220V (pump controller) and 15A & 20A 110V breakers. It's about a 60' run from the 200A main service in the house, being placed in conduit 2' underground. The wire in place is newer 10 gauge solid copper. Is this sufficient, or what should we use?
    Thanks.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Jun 21, 2006, 01:48 PM
    Assuming the max allowed load of 24 amps for a 30 Amp circuit with #10 wire , 60 feet, there will be a 3.5 volts dropped from 240 volts, leaving 236.5 volts at the end of the circuit.

    Recommended max voltage drop is 5% at the end of a branch circuit, or no more than 12 Vd, or 228 volts minimum volts supplied.

    There is an issue with the starting current of the motor on long runs. A motor draws 6 to ten times the running current when starting, inversely proportional to time, which means as the motor starts and current rises to peak quickly, the current then
    Drops down to normal as time passes.

    As the motor starts and current rises, this will increase the voltage drop, which may exceed the 5% allowed. Unless this is a very small motor, I believe you can have problems with Vd, which , over time, will affect the life of the motor.

    I would recommend using #8 or maybe #6 wire to eliminate the any possibility of voltage drop effects to the motor. This does not even consider the load on the 120 volt circuits, which I assume are for minor general purpose loads, such as drill, drop light, etc.
    Walt3241's Avatar
    Walt3241 Posts: 1, Reputation: 1
    New Member
     
    #3

    Feb 2, 2012, 04:02 PM
    You should be good to use the 10 Gauge, as you are in within and under the 100ft to have to start worrying about voltage drop on the circuit, being that it is a 240V motor, I would assume that it would be no more than 1.5-4HP moter, if that, and the max inrush you could handle would be about 8-9 amps, and then it would quickly reduce to running current. You should supply the nameplate data of the Motor and Pump together, and make sure that the motor is/or is not a capacitant start induction running motor, if it is, the initial starting current could drastically increase because of the capacitor, but if it is a gen purpose motor you should be fine with the wiring supplied. Hope I helped.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #4

    Feb 2, 2012, 06:40 PM
    Quote Originally Posted by Walt3241 View Post
    Hope I helped.
    Please keep in mind, you are saying this to an almost six year old post.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Neutral wire is hot(has voltage potential like the black wire) [ 5 Answers ]

Hi, The problem started at midnight last week. One of my line in the basement is starting to have issue whenever I connect a water pump or appliances to the outlets. Before I plug the appliance in, the neutral is neutral(zero voltage), but when I plug the appliance in, the neutral is now...

3-wire home, 3-wire fan, 2-wire remote [ 9 Answers ]

Greetings, My home is 3-wire. I bought a Hunter ceiling fan (model 23811). The fan came with a remote assy. That I do NOT want to use... The fan has standard 3-wire connections (black, white, blk&white strip, ground). The remote receiver home-side wiring looks to be for 2-wire (blk and white)....

4 wire home service entrance wire size [ 1 Answers ]

Mobile home requires 4 wire electrical service entrance wire. Distance is 160 foot from meter to breaker panel. 220V service. What size wire do I use? Can I use diff. size for neutral and ground?

2 Wire White-Rogers with no wallplate wire question [ 2 Answers ]

Hi there. I want to replace my current White-Rogers 1E56W309 thermostat with a new Honeywell RTH7500D. The problem is that the tools that installed my high efficiency furnace didn't install the wall plate with my thermostat (it was a new house and the builder contracted these guys). Instead,...

Wiring a 2 wire thermostat to a 4 wire system [ 1 Answers ]

I have a gas furnace equipped with central air.The compressor is shot in the AC unit,and I needed to replace the thermostat so I bought a heating only thermostat.I have the blower and the w wires together on the w terminal designation and the rh on the r terminal designation, and I have the y wire...


View more questions Search