    What size wire to use for new service?
    We are currently building a greenhouse, and I need to run about 240 foot of wire from the pole to the greenhouse breaker box. The greenhouse will have 2- 115/230V fans drawing 6.0 amps each, 3- 1/3hp sump pumps not sure of the amperage yet but will be 115v, LP gas instant hot water heater, 10 heater coils. Heater coils are 115v but the motors do not say how many amps they draw, just that they draw less than two amps each. So my question is, what size wire do I need to buy for this project? Mainly just the service wire from the main box and meter to the new box in the greenhouse. Also I would like to run this service underground. Thanks for the help,
    Randy
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Oct 20, 2006, 02:02 PM
    As a close minimum,#1 aluminum XLPE cable just exceeds the max of 3% voltage drop for a feeder , 240 feet, and assuming 80 amps of load. If your load would not exceed 50 amps, then #1 is fine.

    However sounds like you may want to expand later, so I would like to suggest you use #4/0 URD cable, it is very popular and a good investment, and eliminate Vd till the load gets to 150 amps

    If money is no object, then go the next size down, but bury the copper immediately as it is very popular with thieves.

    For such a long run, through farm or rural setting,
    Use 4" PVC DB conduit,
    use handholes every 75-100 feet as pull points, and at direction changes,
    use Sch40 PVC for exposed conduit,
    use Sch40 in urban areas, and Sch80 in drive or truck roadways.

    If it may be needed, lay a separate spare conduit, the largest you can afford, no less then 2".

    Rural, bury 24 " deep , use a bed of sand 6" top and bottom in rocky soils
    Heavy urban, go 36".
    Lay warning tape over the entire length 12 " below grade.

    Hope this helps.
    cumminstex's Avatar
    cumminstex Posts: 2, Reputation: 1
    New Member
     
    #3

    Oct 20, 2006, 06:34 PM
    Thanks for the help!

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Bathroom wire size [ 2 Answers ]

I know that a 20 amp breaker and a GFCI plug are required in a bathroom. Does this mean the wire size has to be 12 gauge or can it be 14? If I wire the bathroom lights on the same circuit, can I splice in and use 14 gauge for the lights on a 12 gauge feed?

Ground Wire for new Service Drop [ 2 Answers ]

I am upgrading my house to a 200 AMP. This requires a new service drop and panel. The technician that came out and gave requirements says I need to run a ground wire that connects my natural gas line, to my water line, to a 8' ground spike and to the new panel. He instructed me to have few as...

Wire Size For 200 Amp Service [ 2 Answers ]

Recently purchased new mobile home with a 200 amp breaker inside.the distance between the outside pole and inside breaker is about 70 feet.what size,or type,or gauge wire do i need to run. Lost in paradis... :) :confused:

4 wire home service entrance wire size [ 1 Answers ]

Mobile home requires 4 wire electrical service entrance wire. Distance is 160 foot from meter to breaker panel. 220V service. What size wire do I use? Can I use diff. size for neutral and ground?

How do I figure out what size wire to use on a 200 amp service. [ 2 Answers ]

My question is... how do I figure out what size wire to use when I know the Amperage of the electrical device. Is there some form of electrical calculation? For example I want to upgrade to a 200 amp panel from a 70 amp panel.


View more questions Search