    1Phase VS 3Phase
    1. What are the current ratings of 1phase 220v 2hp motor?
    2. What are the current ratings of 3phase 220v 2hp motor?

    Note: Please show calculations
    jcaron2's Avatar
    jcaron2 Posts: 986, Reputation: 204
    Senior Member
     
    #2

    Jun 11, 2009, 10:31 AM

    In reality, this question is pretty much impossible to answer as different motors draw different amounts of current at various loads.

    I think the crux of your question is, what's the difference in current draw between a 1-phase and a 3-phase motor, all else being equal.

    Since we're talking about AC here, voltages and currents are expressed in terms of their RMS values (root mean square). That's the equivalent DC (constant) voltage or current that would be required to produce the same amount of power as the AC signal. It is calculated as the square root of the average value of the square of the signal.

    For a single-phase sinusoidal signal, we have:

    V(t) = Vpeak*sin(wt), where w is the angular frequency (2pi*60 Hz in the US).

    V^2(t) = Vpeak^2*sin^2(wt) = Vpeak^2/2*(sin(2wt)+1)

    Since the average value of a sinusoid is 0, we have:

    V^2(t)_ave = Vpeak^2/2

    Finally, the RMS value is the square root of this:

    Vrms = sqrt(V^2(t)_ave) = sqrt(Vpeak^2/2) = Vpeak * sqrt(2)/2

    This is a very well-known formula that you've probably seen many times before.

    Now let's consider a 3-phase voltage. In this case, the RMS value of the voltage is the square root of the average value of the sum of the squares of the voltages, since each is contributing to the total delivered power.

    V1(t) = Vpeak*sin(wt)
    V2(t) = Vpeak*sin(wt-2pi/3)
    V3(t) = vpeak*sin(wt+2pi/3)

    The +/- 2pi/3 terms represent the 120 degree phase shift among the signals.

    V^2 = V1^2 + V2^2 + V3^2

    Substituting the formulas for V1, V2, and V3 from just above, and using the trig identity that sin(x+y)=sin(x)cox(y)+sin(y)cos(x), and knowing that cos(2pi/3)=cos(-2pi/3)=-1/2, we get:

    V^2 = Vpeak^2 * 3/2

    Since the result is actually a constant, not depending on t, finding the average is trivial; it IS the average.

    Thus RMS voltage for a 3-phase signal is:

    Vrms_3phase = Vpeak * sqrt(6) / 2

    Compared to the single-phase case we get:

    Vrms_3phase = sqrt(3) * Vrms_1phase

    With an RMS value sqrt(3) times larger than single-phase, a 3-phase source will therefore deliver sqrt(3) times as much power to a given load. A corrolary to this is that at a constant voltage, a single-phase source requires sqrt(3) times as much current to deliver the same amount of power as a three-phase source.

    In the case of a 2HP motor, therefore, the current drawn in the single-phase case should be about 1.732 times higher than for the 3-phase case. You can see that factor reflected in the motor current ratings shown here:

    The Panel Shop: PanelFacts - Motor Current Ratings

    In the case of a 100% efficient motor, 2HP of mechanical power would be generated by exactly 2HP of electrical power. Converting to watts, we get:

    2HP * 746 watts/HP = 1492 watts

    At 220V, this means the 1-phase motor would be drawing:

    I_1phase = 1492/220 = 6.8 amps,

    whereas

    I_3phase = 6.8/sqrt(3) = 3.9 amps.

    Finally, let me reiterate that just because that's what these fictitious 100% efficient motors would theoretically draw, that is NOT a realistic current rating for a real motor. Actual current draw varies greatly among motors, even at the same power rating, and will also vary greatly with rotational speed, torque, etc. For example, as you probably know, current draw at startup is MUCH higher than at full speed when the motor is generating significant back-EMF. Hence, on the link above you see a panel rating of 24 amps for a 2HP single-phase motor at 220V, nearly 4 times higher than the theoretical current draw!

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Convert 220 VAC 1Phase to 2-110VAC circuits [ 6 Answers ]

I have a 220VAC single phase 30 amp circuit that I would like to split into two 110VAC circuits. The 220VAC circuit has 3 wires and if I measure across the two main terminals I get the 220VAC and if I measure between a main terminal and what appears to be ground, I get the 110VAC. If I take one of...

3phase generator for 110v system? [ 2 Answers ]

I have the opportunity to buy a large 25KVA generator for a great deal. My dental office loses power a few times a year. Sometimes for an hour, sometimes a few. Never know whether to cancel the day's patients or wait for the power to come back on. My question: I have 3 separately metered...

3phase over 1phase [ 3 Answers ]

What is the difference between 3phase over 1 phase system?

Wire a 3phase welder with 1phase power ? [ 2 Answers ]

Have heard this can be done but wanted to get some help. Have a three phase welder and wondered if I can directly wire a single phase line to it? I realize I would loose 66% of the out put which is fine but just wanted to know if it can be done. If so were do I put the single phase lines to? There...

Trouble shooting a 3phase system [ 10 Answers ]

Hi All, I have a 480 VAC 3 phase ungrounded system. We monitor the system via a set of lights for each phase. If one phase goes to ground then that light should glow bright. In my case I have the B phase light out completely. While trouble shooting the problem I found which disconnect switch was...


View more questions Search