    Furnace Wiring - Adding a common "C" wire
    My new thermostat has uses a W,R,Y,G and now a "C". My wiring has only W,R,Y, and G and these are needed.
    How do I, or can I add the needed "C" wire? Is it just adding a wire from the transformer? :confused:
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #2

    Sep 19, 2008, 05:06 PM
    (C) depends on the stat. Battery powered ones make (C) an optional connection.

    (C) goes to the other terminal of the secondary that (R) does not go to. You should find a few low voltage wires on that terminal (gas valve, fan, and outside AC unit all tied together)
    letmetellu's Avatar
    letmetellu Posts: 3,151, Reputation: 317
    Ultra Member
     
    #3

    Sep 19, 2008, 06:17 PM
    Quote Originally Posted by Bocaheat
    My new thermostat has uses a W,R,Y,G and now a "C". My wiring has only W,R,Y, and G and these are needed.
    How do I, or can I add the needed "C" wire? Is it just adding a wire from the transformer? :confused:
    Are you saying that you need a fifth wire that runs from the furnace to the thermostat? If so all you have to do is to just add one 18 gage wire to the four that you already have or you can buy a different wire that has six or more wires and replace the four wire cable that you have now.
    Bocaheat's Avatar
    Bocaheat Posts: 9, Reputation: 1
    New Member
     
    #4

    Sep 20, 2008, 10:05 AM
    Ok. Added the wire but now the Fan will not turn off. I used the "B" terminal for the common. Any ideas what is wrong?
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #5

    Sep 20, 2008, 01:33 PM
    Common may not be marked. There are two wires that go to the outside unit. One is connected to "Y". The other wire will be common.
    letmetellu's Avatar
    letmetellu Posts: 3,151, Reputation: 317
    Ultra Member
     
    #6

    Sep 20, 2008, 06:05 PM
    Quote Originally Posted by Bocaheat View Post
    Ok. Added the wire but now the Fan will not turn off. I used the "B" terminal for the common. Any ideas what is wrong?
    Which fan will not turn off? The indoor fan or the outside fan. Let me know and I can tell you what to do.
    Bocaheat's Avatar
    Bocaheat Posts: 9, Reputation: 1
    New Member
     
    #7

    Sep 30, 2008, 06:59 AM
    Quote Originally Posted by letmetellu View Post
    Which fan will not turn off? the indoor fan or the outside fan. Let me know and I can tell you what to do.
    Inside fan keeps running. Note, the other side of the Blue wire goes to the same common terminal inside the furnace.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #8

    Sep 30, 2008, 08:18 AM

    Remove the "G" wire from the thermostat. Does the fan turn off?
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #9

    Sep 30, 2008, 08:26 AM
    Let's make this simple. G,R,Y,G and C

    Let's leave C out of this temporarily.

    When R connects to G, the fan comes ON.

    When R connects to W, the furnace turns on: The furnace controls the fan (On and Off)

    When R connects to Y, the outside AC unit comes on.

    Thermostat oddities:

    In heat, the fan is controlled by the furnace, but Turning the fan to the ON rather than the auto position sometimes doesn't work in heat mode. OFF will not turn off the fan - the furnace must do it.

    In cool the thermostat controls both the W and G terminals. In order to get cool, both Y and G are connected to R.

    When a common is used, there will be 24 VAC between R and C at all times.

    Bold items were corrected thanks to EPM.
    Bocaheat's Avatar
    Bocaheat Posts: 9, Reputation: 1
    New Member
     
    #10

    Sep 30, 2008, 01:12 PM
    Quote Originally Posted by KeepItSimpleStupid View Post
    Let's make this simple. G,R,Y,G and C

    Let's leave C out of this temporarily.

    When R connects to G, the fan comes ON.

    When R connects to Y, the furnace turns on: The furnace controls the fan (On and Off)

    When R connects to W, the outside AC unit comes on.

    Thermosat oddities:

    In heat, the fan is controlled by the furnace, but Turning the fan to the ON rather than the auto position sometimes doesn't work in heat mode. OFF will not turn off the fan - the furnace must do it.

    In cool the thermostat controlls both the W and G terminals. In order to get cool, both Y and G are connected to R.

    When a common is used, there will be 24 VAC between R and C at all times.
    I will try this weekend... I'm on the road. Will let you know how I make out. Appreciate the help. If I can not get it figuredd out, I will include some pictures. Thanks
    EPMiller's Avatar
    EPMiller Posts: 624, Reputation: 37
    Senior Member
     
    #11

    Sep 30, 2008, 04:53 PM
    Quote Originally Posted by KeepItSimpleStupid View Post
    Let's make this simple. G,R,Y,G and C

    <snip>
    When R connects to Y, the furnace turns on: The furnace controls the fan (On and Off)

    When R connects to W, the outside AC unit comes on.
    <snip>
    Uhh... KISS, I think you got it backwards. Unless they do it differently in your part of the world.

    R to Y calls the compressor, which usually is cooling. If it is a heat pump then the O or B terminal (the type of reversing valve determines which must be used) decides whether it will heat or cool.

    R to W calls heat. If it is a heat pump W often is the second stage (W2) or backup heat.

    Some systems control the fan from the control board and some from the thermostat. You program your tstat accordingly if it allows you to. Otherwise R to G will call the fan (you had that correct), and the temp limiters will overide the fan call and keep it running until the system is below the limit switch threshold.
    Bocaheat's Avatar
    Bocaheat Posts: 9, Reputation: 1
    New Member
     
    #12

    Oct 3, 2008, 02:19 PM
    Ok, here is what I have found. Please see attachment. When I connect the Yellow wire to "C" the fan inside turns on and stays on. (Thermostat - Furnace) RH-R, G-G, W-W1, Y-Blue wire, and finally C-B.
    Attached Images
     
    Bocaheat's Avatar
    Bocaheat Posts: 9, Reputation: 1
    New Member
     
    #13

    Oct 3, 2008, 02:24 PM
    Sorry, not correct! The "O" and "B" terminal on the Furance are reversed.Name:  Furnace.GIF
Views: 7618
Size:  12.9 KB
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #14

    Oct 3, 2008, 02:33 PM

    Since the new tstat has Rh, there musct also be an Rc. Rc and Rh MUST be jumpered together.
    Bocaheat's Avatar
    Bocaheat Posts: 9, Reputation: 1
    New Member
     
    #15

    Oct 4, 2008, 03:41 AM

    The instrucion had me insert a jumper for my configuration. I assume that was what it was for.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #16

    Oct 4, 2008, 03:59 AM
    Unless it was missed can you post the brand and model of your new thermostat?
    Bocaheat's Avatar
    Bocaheat Posts: 9, Reputation: 1
    New Member
     
    #17

    Oct 4, 2008, 10:51 AM

    Ritetemp 6080
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #18

    Oct 4, 2008, 10:56 AM
    If you follow this all should work. Now if the wiring color has not been followed by the original installer then you might have to track down the wiring and start over.

    The RiteTemp Support Site - 6080 Technical Support Page
    Bocaheat's Avatar
    Bocaheat Posts: 9, Reputation: 1
    New Member
     
    #19

    Oct 4, 2008, 11:00 AM
    I rechecked the wiring and it seem to be working now. Thanks.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #20

    Oct 4, 2008, 11:07 AM
    Glad you got it going. Keep the web site for future use if necessary.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Intertherm Electric Furnace Blower works in "on" not in "auto" [ 6 Answers ]

I have an Intertherm Electric Furnace E2EB-015AH. I came home from work last night, turned the heat on and it didn't work as advertised. I could hear the relays clicking occasionally so I investigated a little and found the elements are heating up and cycling, the relay inside the thermostat cycles...

Trane 80XL "Common" connection [ 3 Answers ]

Hey Folks... I have a special thermostat in which I need to connect the common line, "C" in order to power this thing. Where can I get a connection to "Common" in this older furnace? See attached Many many thanks! Brian

Changing wiring to use "second line" rather than "first" line on specific jack [ 9 Answers ]

Hi, and thanks! I have two phone lines (telephone numbers) coming into the house. I want to change a particular jack from one line to the other (exclusively for a fax). The current jack has a pair of tan wires going to "black (heavier wire and screw)", a pair of blue wires going to "red", a pair...

"common wire" [ 1 Answers ]

I have a Carrier gas/ ac system installed in 1998. I just bought honeywell digital thermastat that requires a "common wire". I have blue, tan, black and orange not being used. How can I test to determine which is "common" ?


View more questions Search