    NO AC, compress on but no fan
    Hello, I turn my AC on for the first time this year. The compressor outside came on but the fan does not come on, in the furnace. I hear nothing going on in the furnace.
    The heat works fine. The controller board was change over the winter.
    Any ideas??
    hvacservicetech_07's Avatar
    hvacservicetech_07 Posts: 1,083, Reputation: 75
    Ultra Member
     
    #2

    May 9, 2007, 05:25 PM
    The outdoor fan is not coming on? What model is the furnace? Will the indoor fan come on if you switch the t-stat to the ON position?
    JackT's Avatar
    JackT Posts: 260, Reputation: 19
    Full Member
     
    #3

    May 9, 2007, 05:28 PM
    Call the contractor back to wire up the new board the correct way. They probably didn't connect the G terminals and the furnace blower is cycling with the fan temperature switch.
    browndj1642's Avatar
    browndj1642 Posts: 6, Reputation: 1
    New Member
     
    #4

    May 9, 2007, 08:21 PM
    Quote Originally Posted by browndj1642
    Hello, I turn my AC on for the first time this year. The compressor outside came on but the fan does not come on, in the furnace. I hear nothing going on in the furnace.
    The heat works fine. The controller board was change over the winter.
    Any ideas????
    I should read my statements before I submit them. I was trying to say that I turned on my AC for the first time and the only thing that comes on is the compressor outside fan and all. The blower on the furnace does nothing. The blower works fine with the heat. There was no contractor, I replaced the controller board. I was troubleshooting over the phone with a HVAC person. I am an electrical engineer, but without a schematic I'm a little lost.
    Rheem 90 Plus imperial about 15 years old.

    Thanks for the fast response.
    JackT's Avatar
    JackT Posts: 260, Reputation: 19
    Full Member
     
    #5

    May 10, 2007, 02:50 AM
    You need to see if you have 24 volts at your control board between the "G" & "C" ( transformer common ) terminal. 24 volts is needed to pull in your blower relay. If you don't have 24 volts, check your thermostat wiring and program. If you do have 24 volts, the blower relay may be bad. See if the blower will come on when you move the fan switch to the "ON" position. If it does, you may need to program the thermostat to bring on the blower in the cooling mode.
    browndj1642's Avatar
    browndj1642 Posts: 6, Reputation: 1
    New Member
     
    #6

    May 10, 2007, 05:55 PM
    Jack, I found part of the problem. Back during winter one of my limit switches went bad, of course I am not a contractor so I could not get the part. So I just bypassed it and it worked fine. So what I did was take the bypass off,(open) and the blower fan came on. But the compressor went off. Does this limit switch have to be in play for some odd reason, it is the high heat switch I believe.
    hvacservicetech_07's Avatar
    hvacservicetech_07 Posts: 1,083, Reputation: 75
    Ultra Member
     
    #7

    May 10, 2007, 08:45 PM
    The limit switch will not effect the blower operation for cooling. Make sure that all of the fan wires are in the right position.
    browndj1642's Avatar
    browndj1642 Posts: 6, Reputation: 1
    New Member
     
    #8

    May 10, 2007, 09:09 PM
    Havacservicetech, the only problem with verifying the wiring is that I don't have a schematic. I don't suppose if I took a hi-res picture of my controller board, posted it on a website for all to see. Would someone be able to tell if I missed wired something?
    hvacservicetech_07's Avatar
    hvacservicetech_07 Posts: 1,083, Reputation: 75
    Ultra Member
     
    #9

    May 10, 2007, 09:19 PM
    Actually that would help. What is the model of the furnace? Try to get a close up so that I can see the labeling on the control board.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Hampton Bay Remote Ceiling Fan - light works - no fan [ 2 Answers ]

After about 4 months of use, this began to happen. I would try to turn on the fan (either Low Med or High) and the fan would barely turn. Sometimes it would work - this lasted for about 5 days. Since then, if you try to turn on the fan, you get no response. Now, the light will still turn on...

Hampton Bay Ceiling fan: fan speed pull chain [ 2 Answers ]

The pull chain controlling the fan speed snapped off inside the unit. How much disassembly is required to replace it?

Garage door spring, compress or expand? [ 2 Answers ]

I weighed my door then bought a second hand spring for a 7 x 9 door. I was told turn it approx. 8 rotations. I know to be careful , use visegrips as a backup and keep my face away. The question is do I expand or compress the spring? Thanks!

Compress Screen [ 1 Answers ]

Often when I start up my computer I get a compressed screen in the center of my screen. I have no idea what causes this, so I don't know how to fix it. I recently had a new mother board and processor put in, and had my hard drive reformated. So I was not expecting any problems. This problem has...

Trouble with ceiling fan on a dual fan/light dimmer switch [ 1 Answers ]

I just installed a new Harbor Breeze ceiling fan and dual fan/light dimmer, also from Harbor Breeze. Unfortunately, now I'm scratching my head... Do I have a bad dimmer switch? Here's the problem: 1. The light will turn on only when the fan speed on the wall switch is set to high. 2. When...


View more questions Search