    What size wire do I need to run 45amp service from a 50 amp sub panel 230 feet
    I need to get 45 amp service to my RV which is 230 feet from a 50 amp well pump sub panel. What is the least expensive awg copper wire I should use?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Jan 22, 2013, 06:00 AM
    To deliver 240 volts with a 45 amp load 230 feet and keep voltage drop at 3% or less would require #4 copper wire.

    To keep costs down, compare price of #4 copper to # 2 aluminum.
    mark4lab's Avatar
    mark4lab Posts: 3, Reputation: 1
    New Member
     
    #3

    Jan 22, 2013, 06:16 AM
    Thanks so much... just what I needed.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #4

    Jan 22, 2013, 06:31 AM
    TK,

    Please educate me. Why did you use 3% as opposed to the 5% end to end for your calc?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #5

    Jan 22, 2013, 06:45 AM
    I use 3% for feeders and 2% for branch circuits.

    I will consider this a feeder.

    Recommended maximum vD is 5% total, in designing, you can use either 3% or 2% for either feeder or branch circuit.

    My design, my choice.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #6

    Jan 22, 2013, 06:55 AM
    TK,

    I'm not disputing you. I agree that the cable would be a feeder. I also like your logic.

    You do not have a problem with me. For example, I just learned that using the 5% figure for the feeder does not leave any room for the branch circuit side.

    Thanks
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #7

    Jan 22, 2013, 11:55 AM
    What worries me is that he is pulling power from a (most likely) 240V circuit to feed an (almost certainly) 120/240V circuit.

    Is there a neutral at the well house?
    mark4lab's Avatar
    mark4lab Posts: 3, Reputation: 1
    New Member
     
    #8

    Jan 23, 2013, 02:53 PM
    Quote Originally Posted by stanfortyman View Post
    What worries me is that he is pulling power from a (most likely) 240V circuit to feed an (almost certainly) 120/240V circuit.

    Is there a neutral at the well house?
    I can go from the well house sub panel or directly from the main 200 amp panel at the meter (which has only the well house on it) they're about the same distance and thy both have neutral. My RV was plugged in at the well house but I had to move it. It needs the 45 amps because it has 2 air conditioners. Would you still recommend #4 copper or #2 aluminum going to the 200 amp panel as well (still 200-225 ft)?

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

How to find wire size for 60 amp panel 350 feet away [ 2 Answers ]

I'm building a shed and its 350 feet away from 200 amp service and I want to put in aluminum wire and I need to no what size to use

What size wire would you need to run a 60 amp circuit 150 feet [ 3 Answers ]

Feed to a barn for some lights, receptacles and an air compressor

Wire size for a 100 amp sub panel 200 feet away [ 8 Answers ]

I have a 200 amp main panel in my house and I just built a garage and am planning on putting a 100 amp sub panel in the garage. The garage is about 200 feet from my house and it has a 2 inch pvc stubbed out underground. I am wondering what size aluminum I would need to feed it, and if I can use a...

Wire Size for 150 amp service 300 feet [ 1 Answers ]

I need to take electrical service 300 feet to my barn. I want to take a 150 amp service. What wiresize to I use for this effort.


View more questions Search