    toddbailey's Avatar
    toddbailey Posts: 25, Reputation: 1
    New Member
     
    #1

    Dec 16, 2012, 02:18 PM
    Ungrounded Woodstove
    I have a ungrounded wood stove, should I make it a priority to ground the stove & flue?

    Is there any Nec chapters I want to review?

    Should I use a separate groung rod or can I use near by house wiring gnd or run a separate line to main panel ground

    Same question for a gas fired water heater flue.
    ballengerb1's Avatar
    ballengerb1 Posts: 27,378, Reputation: 2280
    Home Repair & Remodeling Expert
     
    #2

    Dec 16, 2012, 02:32 PM
    Are you concerned about a possible lightning strike? Your water heaters is most likely already grounded via the plumbing pipes.
    toddbailey's Avatar
    toddbailey Posts: 25, Reputation: 1
    New Member
     
    #3

    Dec 16, 2012, 03:06 PM
    Quote Originally Posted by ballengerb1 View Post
    Are you concerned about a possible lightning strike? Your water heaters is most likely already grounded via the plumbing pipes.
    Lightning is always a possibility, So I want to "play it safe" But I also want to make sure there is no code violations to deal with if a loss ever occurs.

    The water heater is currently ungrounded, plumbing is cpvc plastic.

    In researching the topic, the results are mixed with some suggesting leaving the applicances ungrounded as not to attract lightning.

    Having a new installed solar panel array and grounded frames, makes for a big lightning rod.

    So want to make sure all my ducks are lined up.
    ballengerb1's Avatar
    ballengerb1 Posts: 27,378, Reputation: 2280
    Home Repair & Remodeling Expert
     
    #4

    Dec 16, 2012, 04:50 PM
    I have never grounded a water heater flue or a stove flue, lightning rod would be the best thing on the house.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #5

    Dec 16, 2012, 07:37 PM
    Todd,

    Just because you have PVC piping inside your home does mot mean you have an ungrounded system. The cold water electrical ground refers to the water supply pipe. Even with that, the pipe must extend at least 10' from the home.

    But you should already know that. Have you checked the main service panelboasrd for an EGC? Have you checked for a connection to either one or two ground rods.

    Metal pipes make bonding easier.
    toddbailey's Avatar
    toddbailey Posts: 25, Reputation: 1
    New Member
     
    #6

    Dec 17, 2012, 12:45 AM
    The plumbing is all plastic from the water meter into the house, I should know a I had to replace all the qest brand crap with glue together cpvc.. Even the gas line is buried pvc.
    When I installed the new water heater I didn't think the flue might need to be grounded,
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #7

    Dec 17, 2012, 06:19 AM
    Todd,

    You do know that the NEC is not a "How To" manual. It provides the "Minimum" requirements for a "Safe" installation (Article 90)

    Thanks for the additional information. You are mixing two different terms. Grounding and Bonding. Basically, they serve the same purpose but in different ways. I'm paraphasing here so please don't shoot me if I'm not spot on. You can check the definitions for Grounding and Bonding in the NEC, Article 100. Also, Article 250 specifically addresses Grounding and bonding.

    Are you using a bare copper ground conductor in your cables? Ground carries the amperage away from a circuit and discharages it into the earth ground.

    Bonding means connecting all metal parts together so they would be at the same potential with reference to ground. This prevents things like getting a tingle when you touch the metal frameof the sink.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #8

    Dec 17, 2012, 07:19 AM
    Bonding means connecting all metal parts together so they would be at the same potential with reference to ground.
    Not exactly. It is more important that the reference to the source be noted.
    The dirt outside has nothing to do with clearing faults and tripping circuit breakers.
    I really think we need to clarify in the NEC the vast difference between the neutral/ground bond in the main service and a patch of dirt outside.
    toddbailey's Avatar
    toddbailey Posts: 25, Reputation: 1
    New Member
     
    #9

    Dec 17, 2012, 10:08 AM
    For some reason NEC treates a built-on-site home differently that a mfg home. In the end, either structure is basically the same, but according to Google searches NEC states the woodstove frame must be connected to a ground source, bolted to the floor (in case the home is ever relocated), and must use out side fresh air for combustion.
    In case I didn't make this distinction earlier, the structure is, at least in the eyes of the county, still a mfg home.

    The last requirement doesn't make much sense, to me at least.

    The difference between the neutral/ground is the neutral lead is a return path for an electral component, the ground is a path to earth ground.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #10

    Dec 17, 2012, 11:41 AM
    For some reason NEC treates a built-on-site home differently that a mfg home. In the end, either structure is basically the same, but according to Google searches NEC states the woodstove frame must be connected to a ground source, bolted to the floor (in case the home is ever relocated), and must use out side fresh air for combustion.
    In case I didn't make this distinction earlier, the structure is, at least in the eyes of the county, still a mfg home.
    I have never heard of such requirements in the NEC. Especially about combustion air, why would that be in the NEC?
    Also, the NEC only makes distinctions with regard to mobile homes. Modular homes are treated the same as stick built homes.


    The difference between the neutral/ground is the neutral lead is a return path for an electral component, the ground is a path to earth ground.
    This is what I mean about experience and knowledge. This is a fatally flawed incorrect assumption. One that can kill people and burn down houses.

    A neutral is a circuit conductor intended to carry circuit current.
    An equipment ground is intended to only carry fault current back to THE SOURCE, not to the earth.
    A grounding electrode is intended to dissipate extremely high voltage surges such as lightning.
    All three very different things.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #11

    Dec 17, 2012, 11:48 AM
    Stan,

    At the start of my post, I said I was taking literary license. I did that because I do not believe that the OP has ever read or studied the NEC.

    So I do apologize for the over simplication and I will make sure I do delute the statement again, but not my guess. I believe the OP is fishing for code compliance information while holding back on necessaryinformation. JMO!
    toddbailey's Avatar
    toddbailey Posts: 25, Reputation: 1
    New Member
     
    #12

    Dec 17, 2012, 12:17 PM
    This is basically what I said, only in a different way.

    "At the start of my post, I said I was taking literary license. I did that because I do not believe that the OP has ever read or studied the NEC."

    Not True, I have the 2011 edition

    "So I do apologize for the over simplication and I will make sure I do delute the statement again, but not my guess. I believe the OP is fishing for code compliance information while holding back on necessary information. "

    Not really fishing for code compliance here but rather the need (or not) to have a water heater and wood stove flue grounded.

    Additionally trying to make sense of the first and third item, "why a mfg house is required to have the w/s grounded and not in a 'tradition house'" and "using fresh air for combustion"
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #13

    Dec 17, 2012, 01:07 PM
    "why a mfg house is required to have the w/s grounded and not in a 'tradition house'" and "using fresh air for combustion"
    Can you provide the actual code references for these?
    toddbailey's Avatar
    toddbailey Posts: 25, Reputation: 1
    New Member
     
    #14

    Dec 17, 2012, 01:52 PM
    NFPA 9.3 for starters, Duct systems for all wood or solid fuel burning
    Appliances must, at a minimum, comply with the
    Requirements of NFPA 89-M (Table 2-3).

    Wa state L&I installation checklist extract reads...

    3280.809(d) Fireplace/wood or pellet stove is grounded with #8 copper grounding wire or
    Equivalent and terminated at each end with an NEC approved grounding device.
    A paint penetrating washer shall be installed where connected to frame.

    3280.709(g)(1) Combustion air inlet conducts outside air directly into fire chamber and prevents
    Hearth droppings onto area below mobile home. (Check that skirting is
    Adequately vented (no closable openings)).

    3280.709(g)(1) Fireplace/wood or pellet stove is secured to mobile home structure. (Check
    Manufacturers installation instructions to see if appliance must be secured to a
    Structural member.)
    hfcarson's Avatar
    hfcarson Posts: 1,003, Reputation: 49
    Ultra Member
     
    #15

    Dec 17, 2012, 02:06 PM
    NFPA 9.3? What is the title of this code?
    Where did you find this?
    toddbailey's Avatar
    toddbailey Posts: 25, Reputation: 1
    New Member
     
    #16

    Dec 17, 2012, 02:07 PM
    Quote Originally Posted by hfcarson View Post
    NFPA 9.3? What is the title of this code?
    Where did you find this?
    Google and Wa state Dept of L&I, their instalation check list answers my questions re: grounding etc.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Fireplace? Woodstove? Wood? Other? [ 12 Answers ]

Attn: Construction and/or ecology/engineering experts: Since there isn't any emergency preparedness forum on Ask-Me, I'm posting here, and hoping it's a practical place to post. I'm considering preparing a rear center bedroom for emergency preparedness. The room's dimensions are indicated...

Can I burn rusty wood in a woodstove? [ 7 Answers ]

Hi. I am new here so please be patient if I do something wrong. I have a woodstove that I use to help heat the house in winter. At work I can get some dunnage wood which is used to protect steel brought into our steel mill. The steel is not treated with anything and rusts before it gets to our...

Welding a woodstove to repair it [ 5 Answers ]

Can a cast iron woodstove lid be welded and expect to hold up under the temperatures normally associated with burning wood in the stove? We got a very nice, very decorative cast iron parlor stove (Art Deco? I don't really know) at a yard sale for $15 but it has a crack. The stove lid (I mean the...

Woodstove to wall clearances [ 1 Answers ]

I am planning to install a wood stove in the living room. Can the clearances from the stove to the wall be SAFELY reduced if I install cement board on the walls before having stone placed on the walls and hearth area?

Problems with woodstove [ 3 Answers ]

We have a woodstove in our house and tonight it backed up. The air was coming down the chimeney and forcing the smoke to come into the house. We could not get the smoke to turn around, we tried heating the chimeney pipe and pointing a fan in the door of the stove but nothing worked. Does anybody...


View more questions Search