    Long refrigerant lines?
    What precautions should one take while installing long refrigerant lines- DX- R 410 A refrigerant.
    Case 1. Compressor above indoor coil -Horizontal 100 feet equivalent plus vertical 15 ft equivalent
    Case 2. Compressor above indoor coil- Horizontal 15 feet equiv plus vertical 100 ft equivalent.
    Case 3. Same as case 1 but compressor below.
    Case 4. Same as case 2 but compressor below.
    livefortoday61's Avatar
    livefortoday61 Posts: 28, Reputation: 1
    New Member
     
    #2

    Feb 18, 2012, 06:00 AM
    Personal safety is always of utmost importance
    When working on any HVAC system. Safety glasses and
    Gloves should be worn regardless of the refrigerant being
    Used. If it is necessary to heat a cylinder of R-410A—to
    Raise its pressure in cooler weather—heat the cylinder with
    Water that is 90°F or lower; never heat a cylinder with a
    Flame. Don't allow the cylinder to reach a temperature of
    More than 125°F during transport or storage. As a
    Reminder, a cylinder of R-410A at 125°F exerts a cylinder
    Pressure of 450 psig. Never exceed 80% of the capacity of a
    Recovery cylinder. Doing so may cause the cylinder to rupture,
    Causing possible physical injury or property damage.
    Recovery cylinders must be Department of Transportation
    Rated for R-410A use.
    Equipment selection:
    Always
    Replace linesets in retrofit applications to prevent intermixing
    Of the MO or AB oil with the POE oils. If replacing
    The linesets is not practical, the following precautions
    Should be taken:
    • Inspect the linesets for kinks, sharp bends or other
    Restrictions, and for corrosion;
    • Determine if there are any low spots thatmight serve
    As oil traps;
    • Flush the linesets with a flush kit (available commercially)
    To remove as much of the existing oil and contaminants
    As possible; and
    • Install a suction line filter-drier to trap any remaining
    Contaminants, and remove them after 50 hours of
    Operation.
    Because R-410A and POE oilmix so well together, oil-trap
    Installation is generally not required on R-410A systems.
    However, technicians should always be sure to seal refrigerant
    Lines by crimping them closed and brazing them if they
    Will be exposed to the atmosphere for any length of time.
    Never leave refrigeration lines open to the atmosphere to prevent
    Moisture and contaminants from entering the system.
    When connecting
    Lines, techs should not use soft solder. A brazing alloy with
    A minimum 5% silver content is recommended. A lowpressure
    Flow of dry nitrogen should be used when brazing
    Line connections in the field to prevent oxide formation on
    The interior walls of the copper tubing. POE lubricants
    Used in R-410A systems are a form of a mild organic acid,
    Which scrubs oxides and contaminants from the interior
    Of refrigerant tubing walls. The oxides, once removed, will
    Begin to circulate through the system and will likely end
    Up in the metering device and create performance issues.
    Once installed, the start-up procedures for an R-410A system
    Are identical to those of a traditional R-22 system.
    Because of the higher
    Pressure and POE oil found in an R-410A system, any tool
    Or test instrument that comes in contact with refrigerantlatest coil and condensing unit combination ratings,
    visit the Air-Conditioning and Refrigeration Institute
    (ARI) at www.aridirectory.org.

    Piping design guide>http://www.mcquay.com/mcquaybiz/literature/lit_systems/AppGuide/AG_31-011_120407.pdf

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Hot water lines take long time to heat up [ 1 Answers ]

Hello, Suspecting that I had a bad water heater, I replaced for a brand new electric GE 50 gallon tank. It helped with the problem a little bit, but I have a feeling that my pipes are not very well insulated as the hot water in the secondary bathroom (furthest away from the water heater)...

How long are the lines off your septic tank [ 2 Answers ]

Looking to install an above ground pool. Generly how long do the lines run off your septic tank? My home was built in 1993

How long to install new water lines [ 6 Answers ]

Can someone tell me how long it takes to install water lines on two bathroom sinks a kitchen sick and a toilet in new construction? And if this can be done with no water on yet.

Refrigerant Lines and Compressor Failure [ 2 Answers ]

I just discovered that my refrigerant lines are smaller than what the system calls for. My heat pump is not working. The compressor is burnt out. Will small refrigerant lines cause this to happen? My liquid line is 1/4 and my suction line is 5/8. Thanks


View more questions Search