    Electrical load calculation formula?
    I have 600 v supply about 700 feet away from my motor that is 40 amps full load I need to find out the size of the wire needed
    sathe1963's Avatar
    sathe1963 Posts: 97, Reputation: 4
    Junior Member
     
    #2

    Feb 17, 2011, 07:16 AM
    Dear sir, refer to cable catalogue to find out resistance per kilometer length of the cable. Same can be converted to feet. Now you have resistance of cable, current you are knowing... find out size of cable which gives you voltage drop not less than 2 to 3%.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #3

    Feb 17, 2011, 12:39 PM
    Try:

    Southwire - Delivers Power

    By entering your data, I get a #4 copper wire.
    astor's Avatar
    astor Posts: 1, Reputation: 1
    New Member
     
    #4

    Mar 1, 2011, 11:18 AM
    I have 600 volts at 20 amps 3 phase my load is 50 amp what size stepdown transformer do I need
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #5

    Mar 1, 2011, 01:33 PM
    A 20 amp load at 600 Volts 3 phase is 20,760 VA. Typically transformers need to be rated 25% higher than the load, so you would need at least a transformer rated 29,950 VA.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Electrical load computation formula [ 12 Answers ]

How can I conpute the electrical load (ampere) of a building

Wind load calculation formula on wire rope of ropeway [ 1 Answers ]

12 mm dia wire ropeway fixed at a distance of 1000 meter at both the end and it is fixed at a 45 degreeand around 150 kg weight is moving on it. How can calculate the wind load?

Calculation or formula [ 2 Answers ]

How to calculate the average cost per share of common stock?