    Dec 31, 2006, 04:14 PM
    Bryant furnace blower restarts momentarily
    Hello

    I own a vintage Bryant #394GAD036100 furnace that is working just fine accept for one little problem. The unit cycles and maintains the desired temp setpoint (heating mode) but after the main recirc blower shuts off it restarts momentarily one time approx 2 sec later,
    And again approx 2 sec later.
    I currently have an electrostatic furnace filter and a humidifier(media wheel type external) hooked up to the auxiliary pilot contacts. Originally convinced that I was dealing with a coasting blower wheel back EMF issue,I applied 130v metal oxide varistors at various places about the control circuit board(across relay contacts,txfmr etc.),still no relief.I then disconnected the aux circuit loads (humidifier and EP filter) same problem.
    I am about ready to drag out my oscilloscope and monitor the PCB for any stray spike activity. I believe that the onboard operational amplifier is simply being used as post gas valve shutoff time delay.
    Does any of this make any sense,and has anyone else ever experienced this problem previously?
    Thank you and I look forward to any suggestions or help. If I had a schematic on the PCB I could fix it in a snap.

    Mark
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #2

    Jan 3, 2007, 02:43 PM
    Could be a dirty or bad upper limit switch.
    mebaskin's Avatar
    mebaskin Posts: 2, Reputation: 1
    New Member
     
    #3

    Mar 7, 2007, 09:15 AM
    A defective n.c. motor relay was the culprit.The contacts had eroded so badly that arcing noise was being close coupled back into the diff comparator delay circuit.
    I removed the 13vdc coil relay and replaced it with a PC mount spdt 12vdc hi sensitive coil relay.The new relay is simply used as a buffer logic inverter that then feeds an external 20A 3-32vdc input solid state relay.Works great!
    Nice thing about the SSR is that it is zero voltage turnon and zero current turnoff.No more nasty mid sine wave arcing.
    Please let me know if anyone is interested in this solid state conversion.No more arcing or burnt out contacts.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Bryant furnace problem [ 20 Answers ]

Hi All, I have a 5 y/o 80% eff bryant furnace. The problem I have is that my furnace Doesn't always kick on even when thew thermostat shows the temp under the Temp set. I will sometimes have to go down and turn of the blower switch on the furnace wait a couple seconds and then turn it on again....

Bryant furnace won't lite [ 3 Answers ]

Hello, I have a Bryant furnace. It Keeps flashing code 13 on the circuit board. I read the code and it says that the switch will reset after 3 hours. It also refers me to # 33 which gives more possibilities as to what the problem may be. However it does say to reset the limit or flame roll out...

Bryant Gas Furnace Problem [ 4 Answers ]

Hi, I have a Bryant 373LAV Gas furnace that has stopped working. There are a couple of issues with the furnace and I'll try to explain what is going on. For now, the heat does not turn on. The thermostat (White-Rodgers Comfort Set II) shows 60 and the heat is set at 70. So I opened up...

Bryant ceiling mount furnace [ 1 Answers ]

:confused: thank you for your quick response, upon receiving your reply I was a bit more bewildered. I went to run it through a cycle and watched entirety.I am under the impression the fan is working properly(may be kicking on a bit early)the new problem I noticed is the burners run initially for...

Bryant upflow furnace model394g lp [ 1 Answers ]

How do you adjust pilot light?


View more questions Search