    Newly Finished Basement Not Heating Properly
    Last fall, we had our basement finished by a small, local general contractor who came recommended by a friend. The job added about 700 sq ft of finished space to our previously 2000 sq ft home, which is heated by an electric heat pump, and has no separate heating zones.

    The contractor added 4 additional registers to heat the basement, but the result was terrible. All throughout the winter the basement remained uncomfortably cold. So much so, that our children were unable to play there. The themostat is on the first floor, and when we turned up the heat, it became uncomfortably hot (!) on the upper two floors of the house, and still made the basement only just bearable.

    To experiment, I spent a month closing the registers on the upper two floors (to keep them cooler and force more of the heat into the basement) -- this worked a bit, but still did not create a comfortable balance between the basement and the rest of the house -- and our electric bill absolutely sky-rocketed when I attempted this solution! (Was this an unwise way to attempt to fix the problem?)

    I talked to the contractor about it this week, and he was quite friendly, but I feel as if he avoided addressing the issue directly or taking responsibility for the problem. Before I speak to him again, I'm hoping to be a bit more informed.

    My question is this: Do you have guesses about what the problem might be -- or where someone would start investigating? What might be going wrong? If I push a bit, I want to be confident that he's considering the right things, and not avoiding issues that might have been poor decisions on his part.

    (Our house is only 4 years old and therefore has windows and doors that are energy efficient. The basement is exposed on the back wall and has two large bays of windows and a set of french doors. The contractor used R-19 insulation on the exposed wall and I believe no insulation on the three poured walls. If I understand him correctly, he claims that poured concrete walls are very thick, and also have a layer of insulation buried on the outside, and therefore do not require interior insulation.)

    Thank you so much for any ideas you can generate!
    Your time is much appreciated!
    csavage1's Avatar
    csavage1 Posts: 86, Reputation: 5
    Junior Member
     
    #2

    May 5, 2009, 04:18 AM

    Is this forced air registers?
    If so are the registers in the ceiling or walls?
    If so is there any coldair returns?

    Trying to help let us know.
    erclark's Avatar
    erclark Posts: 11, Reputation: 1
    New Member
     
    #3

    May 5, 2009, 04:38 AM
    Quote Originally Posted by csavage1 View Post
    Is this forced air registers?
    If so are the registers in the ceiling or walls?
    If so is there any coldair returns?

    Trying to help let us know.

    Yes, they are forced air registers.

    The registers are on the walls, about a foot up off the floor.

    To be honest I'm not sure about the cold air returns. There is only one vent that might be a cold air return. I'll look into it. If it is a cold air return, there is just that one.

    Thanks for your further questions! Let me know what you think.
    csavage1's Avatar
    csavage1 Posts: 86, Reputation: 5
    Junior Member
     
    #4

    May 5, 2009, 02:30 PM

    The way to check for cold air returns would be a sheet of paper over the register grill.When the blower is on and heat is blowing go the grills and check with a sheet of paper.

    If it's a return that paper will be sucked up to the grill and if it's a supply hot air it will be blown away from the grill.

    Normal setup is a proper sized supply and proper sized return. This has to be balanced or the system will not move the air as needed and you will have problems heating that area.

    Is the duct work above a drop ceiling?
    Have you changed the air filter at the blower area?

    So many questions can be asked to help you understand how this should be.

    What size are the runs to the wall grills in the basement?

    Did the contractor install dampers in the ducts to the 4 runs to the walls?

    Maybe Mygirlsdad and or others will see this and help with there expertise on this.
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #5

    May 5, 2009, 02:44 PM

    It is just a basement, it will not be the same temp as the upstairs. Concrete stays cold 56 degrees. Did they put in square registars or round?
    erclark's Avatar
    erclark Posts: 11, Reputation: 1
    New Member
     
    #6

    May 5, 2009, 03:51 PM

    Thanks for all the questions and input. I'll try to answer some, and I appreciate any and all ideas. I know that a full diagnosis can't be made online, I'm just looking to generate a list of possible problems, so that I know what types of issues might be responsible.

    The ducts are above a drywall ceiling and then come down the walls. The registers are rectangular. The filter in the furnace was recently replaced.

    Could these things be sources of possible problems?

    So if I understand correctly, the one possible problem that's been generated so far is a lack (or inadequate number of) cold air returns. Is there a way to assess this, or would we just need to go to the expense of adding cold air returns to find out if it helps?

    Joshdta, I anticipated that the basement would never get quite as warm as the upper floors, especially given that the thermostat is upstairs. However, shouldn't it be possible to heat the basement to at least a useable temperature?

    Thanks for any other suggestions about what might be causing the problem!
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #7

    May 5, 2009, 03:58 PM

    Do you have carpet down there now??
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #8

    May 5, 2009, 03:59 PM

    Also you can let the fan run on the on mode and this will help to even the temp out between the 2 floors
    plumberchris911's Avatar
    plumberchris911 Posts: 6, Reputation: 1
    New Member
     
    #9

    May 5, 2009, 04:08 PM

    Just a quick answer but sounds like there is no proper heating there
    If it's a basement it will need a lot
    Turning up the stat on the higher floors will just make them warmer as heat rises
    I suggest you think about the wall structures around the basement and add radiators or some form of under floor heating
    Radiators are good
    Underfloor heating might be more expensive
    Get a plumber in - electric heating wong cut it as it is colder down there
    erclark's Avatar
    erclark Posts: 11, Reputation: 1
    New Member
     
    #10

    May 5, 2009, 04:08 PM
    Yes, wall to wall carpet in most of the 700 sq ft, with linoleum in the laundry room and bathroom.

    Quote Originally Posted by Joshdta View Post
    also you can let the fan run on the on mode and this will help to even the temp out between the 2 floors
    I'm not sure what this means.. :rolleyes:
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #11

    May 5, 2009, 04:09 PM

    On the t-stat you have a auto and a fan on mode, by letting the fan run will help circulate the air
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #12

    May 5, 2009, 04:12 PM
    To heat a basement you need twice the amout of heat runs as you have upstairs, then it the summer you will have to close them all down to keep the ac from freezing out the basement. Do you have the block walls painted? Or drywall on all the sides? How much insulation was it the walls?
    erclark's Avatar
    erclark Posts: 11, Reputation: 1
    New Member
     
    #13

    May 5, 2009, 04:17 PM
    Quote Originally Posted by Joshdta View Post
    to heat a basement you need twice the amout of heat runs as you have upstairs, then it the summer you will have to close them all down to keep the ac from freezing out the basement. Do you have the block walls painted? or drywall on all the sides? how much insulation was it the walls?
    All of the walls in the basement, poured concrete and block, are now drywalled. The block wall has R-19 insulation.

    I was concerned from the beginning that the contractor simply skimped and put too few registers down there in order to save money. Essentially, there are four new registers in the basement, but upstairs, the comparable area is heated with eight.

    Would you guess that this is really the major problem? Would adding more registers take care of the problem? (Thanks again so much for your time, Joshdta!)
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #14

    May 5, 2009, 04:22 PM

    Yes, is your furnace close to the carpted area? How many supllys do you have in that room?
    wmproop's Avatar
    wmproop Posts: 3,749, Reputation: 91
    Ultra Member
     
    #15

    May 5, 2009, 04:23 PM
    Chances are the heat system was designed and sized for the 2000 sq. ft home.adding another 700 sq. ft to it ,could mean the heat system is now to small to do the job,,
    erclark's Avatar
    erclark Posts: 11, Reputation: 1
    New Member
     
    #16

    May 5, 2009, 04:26 PM
    Quote Originally Posted by Joshdta View Post
    yes, is your furnace close to the carpted area? How many supllys do you have in that room?
    Furnace is now in a small closet, which does not have carpet, but the room around it (bedroom) does.

    There is just one register in that bedroom.
    erclark's Avatar
    erclark Posts: 11, Reputation: 1
    New Member
     
    #17

    May 5, 2009, 04:28 PM
    Quote Originally Posted by wmproop View Post
    chances are the heat system was designed and sized for the 2000 sq. ft home.adding another 700 sq. ft to it ,could mean the heat system is now to small to do the job,,,,
    I was also afraid that this could be the problem. :eek:

    I'll feel so disappointed if this is what it comes down to, because I feel as if the contractor should probably have considered this and included it in our discussion, but also because we won't be able to afford to put in an entirely new system for quite some time. So our dream basement won't be usable for the three-four months a year when we need it the most. :(
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #18

    May 5, 2009, 04:29 PM

    How many btu's is the furnace you have now?
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #19

    Dec 29, 2009, 09:57 AM

    There MAY be a way out of your problem: High velocity HVAC

    Ten Steps To Installing A High-Velocity HVAC System - How To - Air Conditioning, Heating & Refrigeration NEWS

    It uses small tubes about 1.5" in diameter. I have been in structure that had one, a residence on top of a barn.

    How is it going?
    wmproop's Avatar
    wmproop Posts: 3,749, Reputation: 91
    Ultra Member
     
    #20

    Dec 29, 2009, 02:31 PM
    This thread was first posted 8 months ago,, I hope the problem was solved

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

What's the order of construction in my finished basement? [ 6 Answers ]

I've got drywall up and am in process of painting now. I still have to install doors, cabinets/vanity, toilets, flooring and trim. Do I install the flooring before the doors, cabinets, toilet, etc? Any particular reason to do one beforenthe other?

How do I add vents in my finished basement? [ 7 Answers ]

I have finished the framing and I need to run some lines from the trunk lines into the newly added rooms in my basement. I built soffits around the main/trunk lines and I'm wondering if I should have done the HVAC ducts first. I thought I'd run a rectangular duct through the soffit and just put the...

Heating a finished basement [ 2 Answers ]

I have a finished basement, furnished and live in the Midwest. I do not use the are very rarely in the winter. I would like to know how much it would decrease my heating bill. I could close it off with a temporary closure. I have all the heat ducts closed. Is it worth the effort to close it...

Plumbing in a finished basement [ 1 Answers ]

I am currently finishing the basement in my home built about 2 years ago. The people that did the plumbing and heating didn’t want to spend the time to keep all of the plumbing and ductwork up in the joists so I’m having to move a bunch of it. I actually have 2 questions: 1. I have an A/C...


View more questions Search