    Weeping conduit ?
    ( greenhorn alert) HI I was on the last of 1" pvc . Burying them 18'' deep on the way to the shed. for a 80foot run. so i can add my 4 #12 thwn.wires, Now I heard someone mention about water condensation, and that all conduit has water in them,and that you need to add weeping holes ,to keep it drained, I guess that would be on the low end of you conduit run? It sounds like it makes sense?? BUT before I get the drill out ,I would like a pro"s or two opinion on this , and if you have done it and how many, and what size holes? And where? Part 2 while I have You! When you fasten conductors on your fishing tape , Like 12or 10 gauge thwn. How many do you pull at a time? Thank you !:confused: :confused:
    Handyman2007's Avatar
    Handyman2007 Posts: 988, Reputation: 73
    Senior Member
     
    #2

    May 1, 2008, 09:29 AM
    The weep holes and be as small as 1/8". I would use 1/4 " . I have pulled as many as 12 #12 THHN wires through 3/4" conduit. 4 of them should be no problem. Just spray a little silicon spray in the end of the conduit when starting the wires through.
    Mr Shove L's Avatar
    Mr Shove L Posts: 11, Reputation: 1
    New Member
     
    #3

    May 1, 2008, 09:48 AM
    Thank You Mr. HandyMan 2007. I'll put a 1/4 " hole, in the bottom of the 90 degree swipe just before it rises to the ub fitting. I'am going to lay it on pea gravel ,maybe keep it from clogging dirt or roots. And I'll try pulling the 4 wires all at once. Thank you for the Help!
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #4

    May 1, 2008, 02:29 PM
    Wait a minute, please.

    We just went through a similar discussion earlier. There are things you need to consider carefully.

    For example, there can be only one entry point for the electric power. Also, for a remote building, you need to put a sub-panel with its own equipment grounding rod system.

    If you put in a light, you have also put in at least one GFCI protected receptacle. You also need to put a light at the entry point for the building (Door).

    Running multiple #12 AWG into the structure is against code.
    Mr Shove L's Avatar
    Mr Shove L Posts: 11, Reputation: 1
    New Member
     
    #5

    May 1, 2008, 04:51 PM
    Thanks for advise Don! On the entrance light,and sub panel grounging info. But I'd like to ask you if I could run the shed at 120 volts ,but have a forth wire in the conduit not hooked up,so if I wanted to go with 240volts at a later date? I'll have the red wire there ,already to go ? For the future , a dead wire? While I'am pulling wires When I decide to go,or if I go with 240, I won't be to old to pull it ? Thanks for help!!
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #6

    May 1, 2008, 05:29 PM
    First off, DO NOT (!! ) drill ANY holes in a conduit run, especially underground. The inside of an underground conduit run IS a wet location. It WILL get water in it. This is normal and is expected.
    Weep holes are not needed nor wanted.



    Second, Don, you ARE allowed to run a multi-wire branch circuit to a remote structure. For this purpose, a MWBC is considered ONE circuit.
    Here is the code reference:

    225.30 Number of Supplies
    Where more than one building or other structure is on the same property and under single management, each additional building or other structure that is served by a branch circuit or feeder on the load side of the service disconnecting means shall be supplied by only one feeder or branch circuit unless permitted in 225.30(A) through (E). For the purpose of this section, a multiwire branch circuit shall be considered a single circuit.


    A sub-panel is NOT mandatory. A grounding electrode is not required unless a feeder is run to a remote building.

    The one thing that IS required is a disconnect switch. You DO need a disconnect switch at a remote building.
    With a MWBC a double-pole toggle switch is all that is needed.

    Here is the code reference for that:

    225.31 Disconnecting Means
    Means shall be provided for disconnecting all ungrounded conductors that supply or pass through the building or structure.

    225.32 Location
    The disconnecting means shall be installed either inside or outside of the building or structure served or where the conductors pass through the building or structure. The disconnecting means shall be at a readily accessible location nearest the point of entrance of the conductors. For the purposes of this section, the requirements in 230.6 shall be utilized.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #7

    May 2, 2008, 05:56 AM
    Stan,

    I'm having trouble understanding and converting the description of a MWBC into a physical connection.

    I'll go back through the code points you reference, but at this point, I'm at a loss to understand the benefit of a MWBC over a Feeder to Subpanel arrangement. To me it seems far safer to run one feeder cable to a subpanel and then fan out the circuits in the remote structure.
    Handyman2007's Avatar
    Handyman2007 Posts: 988, Reputation: 73
    Senior Member
     
    #8

    May 2, 2008, 06:19 AM
    Wow! Did I ever make a big mistake!! I guess my mind was wondering when I read this. I will revamp my answer. You have to run a sub panel in the shed. .
    I apologize to everyone for my very BAD advice. You must follow NEC for this. The above answers cover it all. FEEZ!! What was I thinking!! I just finished doing an underground feed for a sub panel in a garage!!
    Mr Shove L's Avatar
    Mr Shove L Posts: 11, Reputation: 1
    New Member
     
    #9

    May 2, 2008, 06:56 AM
    Thanks Handyman & Don! I will do a litte more resource,on the sub panel! I should have room to be able to some larger cable, to the sub panel Because , the way it stands ,I was going run 4#12 it in a nice new metal junction box? Inside the shed,then split from there ,I even got a shut off switich first thing So to make a long story short ! What size sub panel would you recomneded with what size cable? Thanks for advise ! Everyone! Cool site!
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #10

    May 2, 2008, 07:22 AM
    Stanforty and several others are much better at planning a site that I am.

    Stan advocated a MWBC as an acceptable feeder to your room. I have no experience with that particular configuration so I would ask you to wait to give other's a chance give better directions to you.

    However, I would first determine how many circuits are needed, Figure out the total amperage you need. For grins let's say that you need about 60 amps of 120/240.
    Do you have enough room in the main panel to put a 60 Amp breaker into the panel? From there you 2 #6 AWG as feed conductors, with a #8 as a ground wire. These go to the subpanel. Then you place the configuration of Circuit Breakers that you need to feed the room.
    Mr Shove L's Avatar
    Mr Shove L Posts: 11, Reputation: 1
    New Member
     
    #11

    May 2, 2008, 12:06 PM
    Thank you Mr.Donf. That sounds like a good plan, I need to do more studying , and reading before I tackle that one. What does MWBC stand for? Thank You!
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #12

    May 4, 2008, 06:37 AM
    Stan already spelled out MWBC as a Multi-Wire Branch Circuit.

    And he explained that a MWBC can feed a separate building, and that a panel is not necessary, as long as the MWBC can serve the circuits and load sufficiently, and that there is a switch, or up to six switches at the separate building to open, or disconnect the power to this building.

    Drilling holes in conduit is never allowed. Conduits must be arranged to drain, but holes in conduit is never the answer.

    If one were to drill a hole into a metal conduit, the remaining spurs and burrs on the interior of the conduit will damage the insulation of the wire.

    If water in an underground conduit is a concern because the conduit entry would allow water to enter an enclosure with live parts, then the conduit can be sealed to prevent water from entering the enclosure,

    Or,

    An open bottom junction box can be installed, with the handhole at grade level, and the conduit can be broken, and arranged to allow water to drain into the bottom of the junction box, and back into the earth.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Weeping Cherry Tree by Ran Su [ 5 Answers ]

I am trying to find out if this piece of artwork by Ran Su has any value. The label on the back of the piece states: House of Ran Su, Elmhurst, NY; it is titled "Weeping Cherry Tree" with the number 248 next to it. It also has the number 15168 at the top of the label. The front of the piece is...

How to size Conduit 6-3 [ 4 Answers ]

I have 2 6-3 for a 60ft run and 1 6-3 for another run. Question, what size conduit do I use. This circuit is for a tankless water heater. All will in my garage which is drywalled.

Weeping tile [ 2 Answers ]

First of all let me say that the info received from this web site has been excellent--too bad we do not have the experienced experts available on line up here ( Saskatchewan Canada) that one could log on to and ask. The House I am in, is what would be defined as an old timer. Half basement that...

Do I need conduit? [ 4 Answers ]

I have a panel in my garage for my garage based workshop. I want to run a 220 volt circuit (have have the capacity in the panel to do so). My question is whether I need to run the wire inside conduit or can I run romex without conduit. The wire will be behind drywall the entire way so it will...