    Joining black steel to stainless: which dielectric union?
    I am trying to connect black steel pipe to stainless steel pipe and I am wondering what type of dielectric union is appropriate. I have not seen any iron/stainless unions out there and it seems galvanized will lead to corrosion once the coating is removed during threading the parts together. Is an iron/brass dielectric union best for this with a brass to stainless connection directly? Any help is much appreciated
    Kevin
    Sand Daddy's Avatar
    Sand Daddy Posts: 95, Reputation: 14
    Junior Member
     
    #2

    Feb 11, 2008, 02:32 PM
    What is the application?
    ballengerb1's Avatar
    ballengerb1 Posts: 27,378, Reputation: 2280
    Home Repair & Remodeling Expert
     
    #3

    Feb 11, 2008, 02:38 PM
    Black steel pipe and dielectric unions are two words that seldom come together. Black pipe is for gas and a dielectric union is a plumbing fitting to join to dissimilar metal pipes. What are you putting together.
    kbrotherman's Avatar
    kbrotherman Posts: 4, Reputation: 1
    New Member
     
    #4

    Feb 11, 2008, 10:14 PM
    Thanks for the replies. I'm in the midst of building a micro-brewery. The black pipe will run steam from a low pressure boiler to the stainless steel jacketed tanks. This steam will be uused to boil. The inlets to the tanks are stainless, as are the outlets. I need to connect the black steel pipe to these inlets.

    A parallel note: I recently used a copper/galvanized steel dielectric union to bring the city water to my brew piping (stainless). Now I'm not sure if the fact that it is leaking (about a drop every hour or less) is partly to blame, but the galvanized to stainless connection (threaded) is showing signs of rust (red and smells of iron). This is why I don't think galvanized steel is right.

    So, are there stainless/malleable iron dielectric unions out there? Galvanized/iron is the closest I've seen.
    Thanks for the help!
    Kevin
    iamgrowler's Avatar
    iamgrowler Posts: 1,421, Reputation: 110
    Ultra Member
     
    #5

    Feb 12, 2008, 06:40 AM
    Quote Originally Posted by kbrotherman
    thanks for the replies. I'm in the midst of building a micro-brewery. The black pipe will run steam from a low pressure boiler to the stainless steel jacketed tanks. This steam will be uused to boil. The inlets to the tanks are stainless, as are the outlets. I need to connect the black steel pipe to these inlets.

    A parallel note: I recently used a copper/galvanized steel dielectric union to bring the city water to my brew piping (stainless). Now I'm not sure if the fact that it is leaking (about a drop every hour or less) is partly to blame, but the galvanized to stainless connection (threaded) is showing signs of rust (red and smells of iron). This is why I don't think galvanized steel is right.

    So, are there stainless/malleable iron dielectric unions out there? galvanized/iron is the closest I've seen.
    thanks for the help!
    Kevin
    If both threads are male, then use a brass ground joint union.
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #6

    Feb 12, 2008, 07:06 AM
    I agree with Geowler. A dielectric union isn't needed here. Install a regular ground joint union. However, if one thread's female use a brass nipple to pick up the union. Regards, Tom

    Sure you did!
    I don't have to bother with a plumber who is only interested in scams.
    Hey! You said it on another thread. Not a very high opinion of plumbers.
    ballengerb1's Avatar
    ballengerb1 Posts: 27,378, Reputation: 2280
    Home Repair & Remodeling Expert
     
    #7

    Feb 12, 2008, 08:47 AM
    "The black pipe will run steam " is it really a piece of black pipe which is normally used for gas?
    kbrotherman's Avatar
    kbrotherman Posts: 4, Reputation: 1
    New Member
     
    #8

    Feb 12, 2008, 09:35 PM
    The black pipe is schedule 40, normall used for low pressure gas...

    So, I'm still a little confused. I though the idea of a dielectric union was to keep metals like copper (brass) and steel away from each. The advice given says to connect brass to the black steel and the stainless, which seems to be creating more of a potential problem. Does the brass union do something I'm missing? Is it like a sacrificial electrode? What is meant by grounded joint? Is is a standard brass union?

    As If I haven't asked enough questions already: Can I buy a stainless union and a black steel union, disassemble them and make my own dielectric union by adding a rubber washer?

    Thanks VERY much for everyone's help!
    Kevin
    ballengerb1's Avatar
    ballengerb1 Posts: 27,378, Reputation: 2280
    Home Repair & Remodeling Expert
     
    #9

    Feb 13, 2008, 08:20 AM
    Maybe its me who is confused but I have never heard of using black iron pipe for anything other than gas. I would think that the steam will just get the black pipe rusting.
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #10

    Feb 13, 2008, 04:20 PM
    Bob, Back in the 40's my Dad had a Plumbing and Heating shop. For our main steam supplies they used 4 and 6 inch threaded black iron, but I can't ever remember using smaller sized black iron on anything but gas lines. Regards, Tom
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #11

    Feb 13, 2008, 04:55 PM
    I'm still a little confused. I though the idea of a dielectric union was to keep metals like copper (brass) and steel away from each. The advice given says to connect brass to the black steel and the stainless, which seems to be creating more of a potential problem.
    Understandable! I'm pretty sure what Growler meant was a galvanized ground joint union. (see image) and as In remember,( it's been a long time), I seam to remember that the boss of the union had some brass that made contact for a better joint. So the two IRON pipes would be joiined by a galvanized IRON union. Regards, Tom
    ballengerb1's Avatar
    ballengerb1 Posts: 27,378, Reputation: 2280
    Home Repair & Remodeling Expert
     
    #12

    Feb 13, 2008, 04:57 PM
    Guess I'm just getting brain dead , see no good reason to run stream into a pipe that will rust when you could use other materials. I think you once told me that it wasn't that long ago when there were no toilet flanges, things keep changing, sometimes even for the better. Its getting more rare to even use black pipe for gas. Must be an age thing.
    kbrotherman's Avatar
    kbrotherman Posts: 4, Reputation: 1
    New Member
     
    #13

    Feb 13, 2008, 09:15 PM
    This is common in the brewing idustry. The low pressure steam boiler output pipe is black steel. Also, here's a description of uses from McMaster Carr (McMaster-Carr) page 57:
    Standard-Wall (Schedule 40) Black Steel Unthreaded Butt-Weld Pipe Fittings

    Use with air, water, oil, natural gas, steam
    Pipe: Use standard-wall (Schedule 40) black steel unthreaded (see page 58)
    Flanges: Use low-pressure black steel unthreaded (see page 58)

    So, hopefully it won't just rust the pipe. Any idea why there's a suggestion to add a brass ground joint, when the dielectric union was designed to separate brass from steel? I'm considering proceeding with connecting the black pipe to galvanized components and then the galvanized components to my stainless steel... thanks for the responses
    Kevin
    massplumber2008's Avatar
    massplumber2008 Posts: 12,832, Reputation: 1212
    Senior Plumbing Expert
     
    #14

    Feb 14, 2008, 04:51 AM
    YUP kb and speedball... black pipe and steam work fine... no rust... or at least rare. We pipe steam boilers in black pipe all the time... still do to this day. No comment on union fittings.. you guys seem to have that covered. ;)
    iamgrowler's Avatar
    iamgrowler Posts: 1,421, Reputation: 110
    Ultra Member
     
    #15

    Feb 14, 2008, 06:54 AM
    Quote Originally Posted by kbrotherman
    Any idea why there's a suggestion to add a brass ground joint, when the dielectric union was designed to separate brass from steel?
    A dielectric union is designed to separate steel from copper, not from brass.

    While brass does contain copper as an amalgam, it is not subject to the same level of electrolysis as pure copper.

    Look at it this way -- Red Brass is the principal material used in ball valves, check valves and gate valves for both copper and galvanized steel piping systems.

    As for your low pressure steam system, if it isn't piped yet and you're still concerned about electrolysis, then plumb it with type L copper and make the connection at the boiler and brewing equipment with a dielectric union.

    Also -- You can buy dielectric unions that are FIP on both sides, if you go this route, connect the galvanized steel side of the union to the Stainless Steel inlet of the equipment and the brass side of the union to the Iron Pipe side.

    An aluminum companion flange is yet another option.
    ballengerb1's Avatar
    ballengerb1 Posts: 27,378, Reputation: 2280
    Home Repair & Remodeling Expert
     
    #16

    Feb 14, 2008, 07:55 AM
    Well guys you taught me something today. Most or my work is repair and installation, never been around a brewery much but know of its products too well. Thanks,
    Bob
    JOSH BROWN's Avatar
    JOSH BROWN Posts: 1, Reputation: 1
    New Member
     
    #17

    Oct 13, 2008, 12:02 PM

    I assume you realize that a union is not the proper item you need by now.

    I suggest you use carbon steel 150 RF threaded flange on one side.

    A stainless steel rf threaded flange on the other side.

    And a flange insulation kit to go in between to stop electrolosis.

    This is you're best solution.

    Trust me

    Call me for a quote 530-222-0423

    Thank you,

    Josh Brown.
    Northern Industrial Sales / JW Wood Co.
    nevellens's Avatar
    nevellens Posts: 1, Reputation: 1
    New Member
     
    #18

    Feb 6, 2011, 02:45 AM
    Doesn't really matter... use any die-elctric union.It is basically the insulation in the union that keeps the dis-similar metals apart.The Black steel can be threaded and the Stainless Steel can be soldered to brass easily.No sweat!
    massplumber2008's Avatar
    massplumber2008 Posts: 12,832, Reputation: 1212
    Senior Plumbing Expert
     
    #19

    Feb 6, 2011, 07:01 AM

    Hi Nevellens...

    Thanks for posting but please note the dates of the threads you post to as in this case the thread goes back to 2008... ;)

    Mark
    cableup's Avatar
    cableup Posts: 1, Reputation: 1
    New Member
     
    #20

    Mar 1, 2013, 01:06 PM
    And this post is from 2013 from an industrial pipe sup.
    All preceding answers except the Josh Brown answer are wrong and do not meet standards established for both process piping (brewing) and pressure piping (steam).

    A dielectric flange set is the accepted method of mating SS to Cu. Electrolysis is present in a threaded or brazed connection of SS to Cu directly and it is present in a bronze valve. The amount of degeneration in minimal but the point is not to minimize it. The point is to eliminate it.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Dielectric Union Leak [ 10 Answers ]

Hello - I've just installed a new hot water tank, and have two leaks. Each leak is at the dielectric unions. The leaks are very slow. I even took the union apart, cleaned the thread, re-applied the teflon tape and put them back together. I have the same slow drip, on both the hot and the cold...

How to clean stainless steel [ 1 Answers ]

How can I clean stainless steel?

STAINless? Steel cleaning [ 3 Answers ]

Hello. I just had my kitchen completely redone and I think it looks nice. I am now trying to keep it clean but, I got to tell you, I purchased a couple of stainless steel appliances, the microwave and the refrigerator and I am finding it nearly impossible to keep the surfaces clean. No sooner do...

Laminate stainless steel countertops [ 1 Answers ]

Anybody ever seen laminate stainless steel countertops? Do they look good? Or can you tell it's fake?


View more questions Search