    Replacing thermostat
    Hello all experts: I recenty bought a new Honeywell thermostat to replace my old GE thermostat. How do I connect the wires? My heating system is using heatpump with multistage. Thanks a bunch! Ben
    Attached Images
        
    acetc's Avatar
    acetc Posts: 1,004, Reputation: 79
    Ultra Member
     
    #2

    Aug 29, 2007, 07:14 PM
    The blue will go to "C", the red will go to "RC with jumper to "RH", the green will go to "G", the orange will go to "O/B", the white will go to "AUX.", the yellow will go to "Y", the brown will be taped off (it goes to a thermister in the outside unit) not used, the black will go to "E". Program thermostat for "O". Good luck. Mike
    Better life's Avatar
    Better life Posts: 16, Reputation: 1
    New Member
     
    #3

    Sep 5, 2007, 12:35 PM
    I eventually installed the thermostat as instructed. Tried it by raising the temp 2 degrees to 77 degrees, heat pump runs, heat air blows, but screen shows Aux heat on. This is not what I expected, I expect to blow heat from the heatpump.
    The screen show the inside temp still at 75 degrees without change, air blow stops but the heatpump keeps running.
    Next, I am going to try the cooling system.
    Better life's Avatar
    Better life Posts: 16, Reputation: 1
    New Member
     
    #4

    Sep 5, 2007, 01:16 PM
    I raised the temp to 80, the heat air blows and raised the inside temp to 76 with Aux Heat On. I stopped the heating system.
    Now I am trying the cooling system, I set the temp to 66 degrees, heatpump is on but there is no cool air blowing. I have been waiting for 10 minutes now.
    Please advise!
    acetc's Avatar
    acetc Posts: 1,004, Reputation: 79
    Ultra Member
     
    #5

    Sep 5, 2007, 06:20 PM
    You may have to tell your thermostat that you have a heat pump and that it uses the "O' terminal for the reversing valve. Check your installation manual for the advanced setup.
    acetc's Avatar
    acetc Posts: 1,004, Reputation: 79
    Ultra Member
     
    #6

    Sep 5, 2007, 06:20 PM
    You may have to tell your thermostat that you have a heat pump and that it uses the "O' terminal for the reversing valve. Check your installation manual for the advanced setup.
    Better life's Avatar
    Better life Posts: 16, Reputation: 1
    New Member
     
    #7

    Sep 5, 2007, 10:14 PM
    I did setup the function 0170 to number 7 as Multi-stage heat pump: Heat pump with backup or auxiliary heating.
    I also did setup the function 0190 to number 0 as Cooking changeover valve: Use this setting if you connected a wire labeled "O" to the O/B terminal.
    Is it normal that the heat is using Aux Heat at the whole time?
    Better life's Avatar
    Better life Posts: 16, Reputation: 1
    New Member
     
    #8

    Sep 5, 2007, 10:15 PM
    Should I jump from Aux to E?
    acetc's Avatar
    acetc Posts: 1,004, Reputation: 79
    Ultra Member
     
    #9

    Sep 6, 2007, 03:18 PM
    It may be possible that the aux. heat is running when you raise the temperature setting on the thermostat in the heating mode because you have exceeded the temperature differential between the first stage and second stage heating. You don't need a jumper.
    Better life's Avatar
    Better life Posts: 16, Reputation: 1
    New Member
     
    #10

    Sep 6, 2007, 03:26 PM
    My cooling system is not blowing cold air, is it suppose to blow like heating system? The heat pump runs on both systems.
    acetc's Avatar
    acetc Posts: 1,004, Reputation: 79
    Ultra Member
     
    #11

    Sep 6, 2007, 03:39 PM
    It is suppose to run in heat and cool mode, the reversing valve will have to energise to get cooling, if you have a volt meter you can check for 24 volts at the reversing valve or between the 'O" terminal and the "C" or common terminal, if no 24 volts here then it will be in heat constantly, make sure thermostat is in cooling mode and calling for cool, if you don't have a meter then with unit running put a jumper between the "O" and the "R" terminals in the outside unit, you should hear the valve change over, if it does not change over you may have a faulty solenoid coil on the reversing valve.
    Better life's Avatar
    Better life Posts: 16, Reputation: 1
    New Member
     
    #12

    Sep 6, 2007, 07:34 PM
    I have a volt meter. So I will put the red and black needles on both "O" and "C" without turning off the power, am I right?
    Or without volt meter, I will take off the outer panel on the heat pump then put a jumper between the "O" and "R" while the power is on?
    acetc's Avatar
    acetc Posts: 1,004, Reputation: 79
    Ultra Member
     
    #13

    Sep 6, 2007, 07:45 PM
    With the power on and the thermostat calling for cool, you should check the terminals "C" and "O" at the outdoor unit, or jumper "R" and "O" with the unit calling for cool.This is all low voltage controls and you should read 24volts.
    Better life's Avatar
    Better life Posts: 16, Reputation: 1
    New Member
     
    #14

    Sep 6, 2007, 08:54 PM
    Thanks and I let you know the result.
    Better life's Avatar
    Better life Posts: 16, Reputation: 1
    New Member
     
    #15

    Sep 14, 2007, 02:56 PM
    I don't see the terminals of "C" and "O" on the heatpump. I also found that the pipes going out from the unit to the wall are icy after I turned the cooling system on. The ice was melt after I turned the thermostat off.
    Any further picture you want me to take?
    Attached Images
        
    acetc's Avatar
    acetc Posts: 1,004, Reputation: 79
    Ultra Member
     
    #16

    Sep 14, 2007, 05:49 PM
    It appears that your indoor fan is not running, check at the air handler to insure the fan is running and if it is check the filter.
    Better life's Avatar
    Better life Posts: 16, Reputation: 1
    New Member
     
    #17

    Sep 14, 2007, 08:53 PM
    I tried to search the posts with pictures to check the air handler but I did not find.
    Please advise how to check the air handler.
    Attached Images
         
    Better life's Avatar
    Better life Posts: 16, Reputation: 1
    New Member
     
    #18

    Sep 17, 2007, 08:51 PM
    Do you give up helping me?
    acetc's Avatar
    acetc Posts: 1,004, Reputation: 79
    Ultra Member
     
    #19

    Sep 18, 2007, 03:37 PM
    Will give you all the help you need. The ice on the lines in one of your pictures indicates that the indoor fan was not running or there was something restricking the air flow.
    With the panel off, turn on the fan at the thermostat and see if the fan runs. If it does not run then take the red and green wires loose at the thermostat and twist them together, now see if the fan is running.
    The last pictures are of the air handler.
    Better life's Avatar
    Better life Posts: 16, Reputation: 1
    New Member
     
    #20

    Sep 24, 2007, 06:37 AM
    Finally, I got a chance to test it. I set the thermostat to fan on, there is no blowing while the heatpump runs. I then twisted the red and green wires together then turned the power on, the heatpump runs, the air handler has electric buzzing noise but the fan doesn't run.
    I took some pictures, the upper one is the relay in the air handler, the middle one is the recent thermostat and the lower one is the filter.
    I will test the volts if you could lead me. The temp in Seattle is getting cold, please help!
    Attached Images
       

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Replacing Janitrol Thermostat with Honeywell Thermostat [ 1 Answers ]

I am attempting to replace my manual Janitrol Model HPT 18-60 thermostat with a Honeywell Programmable Model CT3500 thermostat. My Heat Pump is a Trane TWR012-042C The 6 wires connected to the Janitrol thermostate are: Y, W2, G, R, O, C How do I connect these six wires to the Honeywell that...

Replacing thermostat. [ 6 Answers ]

I'm replacing a White-Rogers Type: 1F82-51 T-stat to Hunter Type: 44155C T-Stat. I don't know which wire goes to. Please help. It's very hot in Texas. Old White-Rogers Type: 1F82-51 wiring: C----blue wire L----black wire E----brown wire W2----white wire Y----Yellow wire O/B----orange...

Replacing thermostat [ 1 Answers ]

I'm replacing an old weathertron thermostat with a hunter 44110 one, having trouble with the wires. 8 from the old unit and 5 on the new one

Replacing thermostat [ 1 Answers ]

I am trying to change out my old thermostat which uses a mercury switch to a Honeywell ct2800 programmable thermostat. The old thermostat which is also a Honeywell has just 2 wires connected to it and none of the terminal posts got any letter markings. There is no instructions on the ct2800 on...

Replacing old thermostat [ 6 Answers ]

I bought a new thermostat (digital 7 day programable) for the main part of the house, and I was going to move the old digital to the "gas fire place heated room". My problem... there are only 2 wires coming out of the wall going to the gas fire place. The old one had 3 from the wall and the RC...


View more questions Search